Discuss No filling loop and red expansion vessel installed. How to represurrize heating? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Status
Not open for further replies.
The boiler you have is made as a heat only boiler, as its probably open vented, it can be fitted to an sealed system if appropriate safety features are added, the f22 fault is probably because you drained it and never bled the boiler or pump etc, have a look in the attic for a small plastic tank that will supply water to the boiler and rads, the f22 fault may also be a temp rise difference within boiler , ( circ problem due to air or lack of bleeding ), hope this helps mate

Looks like you are closing down on the issue... thanks mate. I only bleeded radiators.. don't know where to bleed boiler or pump from? There is definitely a plastic tank in the attic (as pictures posted above). Can you please suggest where to bleed boilder / pump from and is it as straight forward as bleeding radiators or I would be risking something big here.. like leak, permanent failure or massive issue?
 
Is there water in that tank?

Haven't check the water as such. Should it be there or not?

I can get up to attic again and check.. it is a difficult place to get to and tank is closed with plastic strings..
 
Haven't check the water as such. Should it be there or not?

I can get up to attic again and check.. it is a difficult place to get to and tank is closed with plastic strings..

Try bleeding the pump first, if no it's off to the attic you go. :D
 
Looks like system is piped up in a way that will be hard to fill and be prone to air locks. No way to bled air from boiler return except on the compression joint. Feed and vent positions look wrong before pump but hard to see. I would repipe it or turn into a sealed system. I think you will keep getting problems as it is
 
I'm going to say it's your pump.
You said you've got f.22 error on a glowworm that's not low water pressure (that's f9) f.22 I believe without checking is low flow rate through boiler/boiler flow return temp differential wrong
I would start with the pump.

Edit just checked, f22 is described as low water pressure but that doesnt really apply to this boiler with your setup
 
Last edited by a moderator:
image.jpg
 
Looks like system is piped up in a way that will be hard to fill and be prone to air locks. No way to bled air from boiler return except on the compression joint. Feed and vent positions look wrong before pump but hard to see. I would repipe it or turn into a sealed system. I think you will keep getting problems as it is

There's a drain valve on the bypass circuit (with red valve set on 0,4 bar). Is that where it should be and to be used to remove air lock? Else there are two radiators on ground floor where similar drain valve is present. I used one of them to drain the system and not other.
 
I'm going to say it's your pump.
You said you've got f.22 error on a glowworm that's not low water pressure (that's f9) f.22 I believe without checking is low flow rate through boiler/boiler flow return temp differential wrong
I would start with the pump.

Edit just checked, f22 is described as low water pressure but that doesnt really apply to this boiler with your setup

Yep.. and that's the reason for this whole conversation that there was no filling loop to increase pressure. But now I know as this is open vented system, no need for pressure loop and pump is on the highest point already. F22 disappeared after resetting boiler twice, but many radiators were not getting hot.
Plumber advised to close TRV on radiators which are getting hot so water is pushed to other rads, which did a trick but still there are two rads (one on ground floor and other is towel rail where inhibitor was poured in) which are not getting hot at all and upon bleeding, cold water is coming out.

Not sure if there is air lock in the pipe as such which need to be vented out and how?
 
What do you mean pump is on the highest point?
I've had plenty of pumps that run okay but are sludged up so they are not pushing water round as much as they should, only way of telling is by removing the pump head.

You can try shutting all the rads off apart from the two that don't work that should force any air out, I find flicking the pump between speeds quite often clears airlocks too, also check that the lockshield side of the radiator is open on the two that don't work
 
Status
Not open for further replies.

Reply to No filling loop and red expansion vessel installed. How to represurrize heating? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

On my Valliant eco tec boiler the pressure guage is on red when cold . I drain a radiator to correct to pressure and it works fine and stays in...
Replies
5
Views
543
Oliver1234
O
Hi I have a baxi duotec combi boiler that every day or other day needs topping up as pressure drops below 0.5bar. When fired up it can reach...
Replies
2
Views
419
hello we have an unvented system. we have an issue where the hot water is hot for 10 seconds and then luke warm, turn off taps / wait and turn...
Replies
5
Views
728
Hello, I live in a two floor semi with a gravity fed conventional gas fired boiler (Potterton Kingfisher MF). The boiler is fed cold water from...
Replies
0
Views
517
Good afternoon, I am experiencing a pressure issue with my heating system and was hoping to receive additional insight as to what the problem...
Replies
9
Views
401