I have a baxi duotec combi boiler that every day or other day needs topping up as pressure drops below 0.5bar.

When fired up it can reach OVER 2.5bar also whilst running CH.

Is this more than likely a flat Expansion Vessel that needs inflating or could there be other possible causes if this turns out to be holding 1bar once tested?

Would i need to drain the water from the boiler by using the Pressure release Valve or is there another area where water is drained from after closing both inflow and outflow valves and do i do all this woth the boiler completely switched off from the mains?

Thankyou
 
Expansion Vessel that needs inflating
drop the front panel on the rhs there is a drain tap white knob
put bucket under for all the water, top presure to 1bar .
leave open for 2mins see if its drops
 
Expansion Vessel that needs inflating
drop the front panel on the rhs there is a drain tap white knob
put bucket under for all the water, top presure to 1bar .
leave open for 2mins see if its drops
Thanks for the info. Went over today and it seems to have held for the past week or so without over or under pressure so a bit strange but left it for now and if it occurs again I will do what you suggest. Thankyou
 

Reply to Expansion vessel issue possibly? in the UK Plumbing Forum | Plumbing Advice area at PlumbersForums.net

Similar plumbing topics

Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
223
Hello all, I'm would like to extend an existing outside tap to another point in the garden. I'm about to pour a concrete patio and was hoping to run the water line underneath. There are existing drain (and who knows what) pipes running along the same wall so I'm nervous about digging too far...
Replies
6
Views
227
I want to reconnect some outbuildings to an existing water supply. The supply pipe is old 22mm MDPE and buried for a fair distance so not going to dig it up and replace it šŸ˜¬. Question is can I use normal 22mm plumbing push-fit connectors to make the connection as finding 22mm MDPE fittings...
Replies
1
Views
262
I was stupid enough not to check the position of the pipes under the tiles when installing a toilet and drilled right through the center of a 16 mm copper water pipe. I exposed the pipe by removing a ~30cm section of the plastic sleeve and a ~10 cm section of the pipe around the hole. Several...
Replies
0
Views
186
Hello all, Iā€™m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. Iā€™m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
231
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock