After work has been carried out on a gas leak ( new copper section inserted to line under concrete floor ) by a qualified gas engineer, when looking at paper work what safety checks should have been carried out?
 
normally a purge and relight with a visual risk assessment unless the pipework route was altered greatly, No paperwork required unless requested.
 
normally a purge and relight with a visual risk assessment unless the pipework route was altered greatly, No paperwork required unless requested.

+1, plus a tightness test
 
I don't think there is an actual obligation to do but a tightness test would be a no brainer followed by a purge and test of all appliances
 
Don't get me wrong I do every time without fail but I was taught that it's not a must have
 
Don't get me wrong I do every time without fail but I was taught that it's not a must have

When/where were you taught that?
You don't HAVE to TT a LL inspection or, eg , a service. If you turn off the gas at the meter, then a TT is required.
 
Take your word for it mate, it's irrelevant as I always do it. But as said I find it staggering the amount that don't in any situation
 
Take your word for it mate, it's irrelevant as I always do it. But as said I find it staggering the amount that don't in any situation

You may think it is irrelevant, but I find it staggering that you have apparently been mis taught a fundamental. No offence intended.
 
These things happen mate. To be honest the fella I learned with knew his stuff but was very bad at explaining himself. One of those that was better to watch than listen to. As I said he taught me to always test so never any fear of a missed leak. Can't really understand why someone wouldn't
 
If you've just repaired a gas leak, TT is the first thing you'd do
Then the usual visual of all exposed pipe work, bonding, labels etc
Personally, I leave a gas safety cert explaining exactly what I'd done and why I,d done it
 
By law you would be required to test the insulation after working on the gas supply, you would also be required to visually inspect(5 point check) any appliance connected to the supply of gas. Would be common sense to also test(tt) before work. Paperwork is a grey area,we are not required to issue minor works certs like electricians but this could be up for debate.
 
I'm doing the Gas part of my level 3 at the moment and its been drummed into us literally that after every bit of work you do a tightness test. But what do i know, i still a puppy lol
 
I'm doing the Gas part of my level 3 at the moment and its been drummed into us literally that after every bit of work you do a tightness test. But what do i know, i still a puppy lol
That may be the common sense approach, but it isn't accurate. You should be being taught the rules and regs. Otherwise we end up with pointless debates like this. Or you may end up critisising amother guy without realising you are wrong. if you see what I mean
 
By law you would be required to test the insulation after working on the gas supply, you would also be required to visually inspect(5 point check) any appliance connected to the supply of gas. Would be common sense to also test(tt) before work. Paperwork is a grey area,we are not required to issue minor works certs like electricians but this could be up for debate.

Installation and 6 point! It appears we all have our own interpretations of gsuir 1998, gae 1954, Ige/up/1(I.e,1, 1a 1b,1c)
 
I'm doing the Gas part of my level 3 at the moment and its been drummed into us literally that after every bit of work you do a tightness test. But what do i know, i still a puppy lol

I was always taught TT first thing before touching anything else or doing any work.
 
thats a common sense approach to minimising your grief down the line,

Which is why we were all taught that way mate, I've broke my own rule before and then found a drop on the TT, heads in tatters then wondering if it was already there ?? Teaching my apprentice now, soon as we get to a job...he has the U gauge out.
 
Which is why we were all taught that way mate, I've broke my own rule before and then found a drop on the TT, heads in tatters then wondering if it was already there ?? Teaching my apprentice now, soon as we get to a job...he has the U gauge out.

colleges dont seem to teach this as it isnt required in the regs, hence my comment on the common sense approach :)
 
Understanding the mandatory requirements is a starting point, unfortunately too many people use their opinion rather than the regs,
It is a mandatory requirement to know your gas work is gas tight, so if you are altering a gas pipe on existing carcass and existing appliances, if you only test after and find a 1mb drop how do you know if it was there before you started or caused by you, however there are plenty of situations where a TT isn't mandatory
 
Last edited by a moderator:
I was told by one of my college tutors that if you turn the ecv off and do work on the gas you have to TT but if you where to isolate and then work from that point on you could just LDF

Although I always TT first and after any work.
 
Some would say if you were to change a gas valve on a domestic boiler, fsd on cooker, that ldf is enough. But, the more cautious interpretation of the regs would require: Tt all aappliances and carcass then 6point check/purge and relight of all appliances.
 
If your working on an appliance then you need to perform more than a visual risk assessment. Changing a safety device requires a test on said device which sometimes is best done with your gauge on the meter. Ie cooker fsd shuts gas supply, tt at meter to confirm no gas is passing.
 
Personally I test work before and after like I've done for god knows how many years it's like riding a bike once learnt never forget
 
If i am going to a property that has reported a gas escape, before i even touch anything, i whizz over the meter /ecv/service and immediate outlet pipe with a detector. I then TT,repair as necessary then TT again. If i am going to exchange a gas carrying component on an appliance i TT the whole thing first,do job, TT again and survey the appliance i have worked on with a sniffer.
 
Well as a gas escape is ID you need to rectify that before anything in the usual way.
Detect-rectify-test.

If you change a gas fitting then you have interuppted the supply so its test again and relight
 
Well as a gas escape is ID you need to rectify that before anything in the usual way.
Detect-rectify-test.

If you change a gas fitting then you have interuppted the supply so its test again and relight

rectify/make safe
 
Status
Not open for further replies.

Reply to Gas checks after repair? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
482
I was stupid enough not to check the position of the pipes under the tiles when installing a toilet and drilled right through the center of a 16 mm copper water pipe. I exposed the pipe by removing a ~30cm section of the plastic sleeve and a ~10 cm section of the pipe around the hole. Several...
Replies
0
Views
192
We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the man-door to the boiler room. It's intent is to 'halt' the operation of the boilers in the room should there be an emergency. He is demanding that I do...
Replies
5
Views
266
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
249
Hello all, I'm would like to extend an existing outside tap to another point in the garden. I'm about to pour a concrete patio and was hoping to run the water line underneath. There are existing drain (and who knows what) pipes running along the same wall so I'm nervous about digging too far...
Replies
6
Views
237
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock