I'm hoping a few people on here can help me as I took the plunge and had a wood pellet boiler installed last year and it's been nothing but trouble since.

In May 2013 I had a company install an MCZ RED365 Compact 18 wood pellet boiler and it has been a nightmare with LOADS of issues. since installation I have had the installers back out about 20 times to fix all manner of issues.

The main issue is that it keeps tripping the electrics (MCB) in the boiler room but am guessing that is caused as a knock on effect from some of the other issues.

- 3 x faulty igniters
- 1 x faulty turbulator
- 3 x faulty motherboards
- leaks due to the boiler not having the right UK connections
- many blown fuses
- overheating issues
- constantly tripping the electrics

In January, after being without heating and hot water for over 2 months I had them rip it out and replace it for a new one (the same model) and 4 weeks later, that has just tripped the electrics, blown fuses and caused other issues and I am now without heating and hot water AGAIN !!!

has anyone else had similar experiences? I just have no idea what to do now other than to instruct the installers to take it out and refund me in full.

has anyone else got a RED 365 Compact 18 or Compact 24 boiler with issues?

i'd love to hear from you to share your experience :)

thanks

Rob
 
Sounds like a nightmare... I would request either a engineer from the manufacturer attends to the boiler, or the company sort it out or have it replaced by a different system.

Grant make a wood pellet boiler, uk based and probably a better overall product if you are looking to replace.


Sounds like the firm who installed are trying to sort the issues, but I would request a replacement at there cost.
 
You aren't the first person I have heard of having issues with the MCZ range of boilers, especially the earlier ones - Although your issues seem to be alot more serious than most I have heard of!

Gassafe is right in suggesting that you get a senior engineer from MCZ out to look at what is going on with your unit.
The Grant Spira boilers are fairly robust, if a bit agricultural in their design and maintenance routine. There are a lot of options out there now in terms of Pellet boilers from the cheaper end like MCZ up to the top end units from manufacturers like Eta and Windhager.

Is your boiler bag fed or supplied by a bulk store, and does the boiler heat an accumulator tank or the heating system directly?
 
Rob what area are you in
I might be doing a course on them boilers in next month or so
I could ask the rep for a manufacture engineer direct number for advice if you can't get sorted
 
Grant are very good but I believe they are now off the MCS register due to a condensate issue
 
My last firm fitted the grant pellet boilers... First ever models caught fire at the burner & auger feeds pipe :0 I'm guessing they sorted these issues out tho....
 
If I remember correctly Specflue are one of the 'official' UK distributors, and the other big distributor of then is PipingHotStoves so you could try speaking direct to them.

At least it sounds as if you installer is doing what he can to get you sorted, however the product is clearly not 'fit for purpose' at the moment...

(Kind one of the reason the pellet boilers we fit cost a lot more..)

There are a lot better boilers available for the price though.. so they could swap it for for another make.
 
Last edited:
Grant are very good but I believe they are now off the MCS register due to a condensate issue

DECC overturned the decision on condensing Biomass boilers recently, so the Grants are now back on the RHI lists thankfully!! (As we'd fitted a few ready for the RHI... Was nearly embarrassing!)
 
Rob what area are you in
I might be doing a course on them boilers in next month or so
I could ask the rep for a manufacture engineer direct number for advice if you can't get sorted

Hi, i'm near to Warwick - I won't name the installer but the distributer was one of the ones mentioned in this thread, they've already been out a number of times as well as the installer and have now booked a date to do a full inspection of the boiler next week. it still doesn't help the fact that I have been without heating for another week again !!

the boiler is currently fed by bags with the sotre of bags situated the other side of a block wall... so there is no reason I couldn't put a hopper there and have an auger going up through the wall..

can anyone suggest a better boiler to go for if I can get them to replace it? It's situated in a utility room so we have limited space - I would say the available area would be 0.8 x 1.8M but that would include the space needed around the boiler too.

or maybe suggest a better more reliable source for heating (preferably on the mCS register) - we are in a remote village so no mains gas obviously..

thanks
 
@Robsmith88, Unless you do a major heating and insulation upgrade, then biomass is your option.

Automated delivery systems and not complicated though they do take time to install and get working correctly unless the boiler has integrated controls for them (few do), so they ave to effectively operate standalone from the boiler, i.e sensing levels in the boiler's 'day hopper'

Before I could make any recommendations I'd need to know what your heat load is - it should be on your hand over documents - what are your total building heat losses calculated to be (i.e max kW needed) ?

(We are just near Evesham and are carrying out a site survey in Ettington tomorrow)

Please note my comments before, the MCZ is down at the how can I be polite ... 'value' end of the scale of products, traditionally we supply and install at the other end... however we do have a range of 'affordable' products for those that don't want the sophistication of being emailed when the ash box needs emptying :)

We educate our customers that the RHI is just that, an INCENTIVE, not an investment opportunity, so they can afford something of quality.
 
Last edited:
i actually had a compact 35 outside my back door for a while.
it was rather....charred

pile of Italian pap
 
Assuming the system was correctly sized (18kW) then our choice of circa 18kW auto fed pellet boilers would be (in no particular order):

CTC Ecoflex: [DLMURL="http://www.ctc-uk.com/biomass/wood-pellet/ecoflex"]EcoFlex[/DLMURL]
ETA PU15 ETA Heiztechnik GmbH - ETA PU PelletsUnit 7 to 15 kW or ETA PC20 ETA Heiztechnik GmbH - ETA PC 20, 25 and 32 kW
HDG K15 HDG K15 / HDG K21 HDG K21

You get what you pay for.. quality, reliability, post installation support ..

Bearing in mind when you go auto fed, you'll pay a premium in price for deliveries of less than 4t (6 ***) and then you'll need auguers / vacuum feeds etc.

Yes there are cheaper alternatives -as a single example of why they are cheaper - just check the burn back protection on them though, - some have virtually none, others rely on a plastic tube melting, the above all have full protection so that the fire cannot reach the pellets.
 
Last edited by a moderator:
Italians are good at making simple things like pizza and ice cream not complicated things like boilers.

I would be tempted to fit an LPG boiler and a tank or bottles outside. Either as a back up or to take over if this thing turns out to be a lost cause. I'd get an immersion heater if possible too to back up the hot water.

At least then the pressure is off and you have decent heating till the problem is resolved or rip it out and stay on the LPG boiler. At least it's pretty guaranteed to work.

You can't realistically live with something so unreliable. It's not fit for purpose. I agree with gassafe it's sounds like a fire hazard too.
 
I'm probably old enough to be most of your dads and am suprised at the lack of appreciation by most plumbing / heating installers of the benefits of renewables.

Done properly (and maintained properly) these are just as reliable (and more than some of the c**p gas boilers we've taken out) as anything that is available on the gas / oil / lpg market place. You seem to forget that northern and western europe have been building and using these for well over 20 years - it isn't new, just new to the UK.

Stop nay saying and get up to date with tommorrows technologies, given time all your lpg and oil customers will convert to more efficient, more cost effective, solutions.

If you buy cheap, you'll get what you pay for. If you don't research the market, you get what your sold...
 
Italians are good at making simple things like pizza and ice cream not complicated things like boilers.

I would be tempted to fit an LPG boiler and a tank or bottles outside. Either as a back up or to take over if this thing turns out to be a lost cause. I'd get an immersion heater if possible too to back up the hot water.

At least then the pressure is off and you have decent heating till the problem is resolved or rip it out and stay on the LPG boiler. At least it's pretty guaranteed to work.

You can't realistically live with something so unreliable. It's not fit for purpose. I agree with gassafe it's sounds like a fire hazard too.

I ripped out LPG to have this installed, as well as having a preference towards a more sustainable way of living LPG and oil prices are just rising way too fast. when we moved in to the property 6 years ago I was paying about ÂŁ800 a year for LPG for heating and hot water - when I ripped it out a year ago I was paying ÂŁ1,500 a year ! now with wood pellet I should go back to paying around ÂŁ800 - ÂŁ900 a year - and yes this will obviously rise and track fossil fuel prices but looking at the rest of europe and scandanavia it should track it at about 2/3 of the price.

it looks (at the moment) like my main issue with the RED 365 Compact 18 was down to the installers wiring it incorrectly - I assume this is due to the huge marketplace for 'green' energy at the moment and installers not being as experienced - no doubt this will change with time and products in the UK will become more reliable. Even with my issues I still think this is the way forward and I personally will not look at LPG or oil as an option in the future even if i don't stick with pellets.
 
It looks (at the moment) like my main issue with the RED 365 Compact 18 was down to the installers wiring it incorrectly - I assume this is due to the huge marketplace for 'green' energy at the moment and installers not being as experienced - no doubt this will change with time and products in the UK will become more reliable. Even with my issues I still think this is the way forward and I personally will not look at LPG or oil as an option in the future even if i don't stick with pellets.

I agree for some people pellet boilers are a great choice. (We install loads of them)

However I would actually put your faults down to being very typical of the type of installer that would offer / install this range of boilers. For the ranges that we install the installer training and accreditation by the boiler manufaturers is far far more stringent before they will even supply you with one. - Anyone can purchase an MCZ boiler with no manufacturer training. - So inherently those installers aren't investing as much themselves in the products.

Back to my original quotation I'm afraid - you get what you pay for - caveat emptor .

We see this more and more across the whole renewables sector - people spend hours reseacrhing the technology and then don't research the installer.. Yet if you have an extension built you don't research the bicks and concrete - you research the builder ...
 
Last edited:
the boiler is still currently running so all good there (time will tell of course)..

Does anyone have any info on the best way to set the MCZ RED365 Compact 18 up so that it runs at optimum efficiency? is it solely down to the pellet recipe?

Our house was specced at 14KWh heating + hot water usage for 3 people - we have cavity and loft insulation etc so the house is fairly efficient apart from the lounge, hall and dining room on the ground floor which have no insulation under the loor (beneath the floor boards it is just earth). the heating is set to come on at 5:30am and goes off at midday - it then comes on again at 3:00pm and runs until 9:00pm. we have the house thermostat set between 18 and 22 degrees depending if we are in or not.. I've tried having the heating running on lower all day and having it coming on and off throughout the day but that doesn't seem to change consumption.

we're currently using 3 bags of pellets a day (EN+ good quality ones - Verdo) but that seems excessive as is costing ÂŁ8.40 a day - at that rate i'll be using nearly a ton a month.

any ideas what I can try or if there are any companies that will come and set these up to best efficiency?
 
Is it going direct in to heating or you using a buffer or thermal store
 
In fact could you post a couple of pictures up of boiler installation
 
Is it going direct in to heating or you using a buffer or thermal store

Hi, will try and get a few pics up.

It is running to a twin coil thermal store in our airing cupboard. Both could currently connected to the boiler, got it just in case we go solar thermal (but that's another story).
 
Hi, will try and get a few pics up.

It is running to a twin coil thermal store in our airing cupboard. Both could currently connected to the boiler, got it just in case we go solar thermal (but that's another story).

How big is the thermal store? What Make? What controls the heat input to the store?

If it is properly configured then the boiler should only be heating the store, and the store then heating the rads / water.
 
Hi, will try and get a few pics up.

It is running to a twin coil thermal store in our airing cupboard. Both could currently connected to the boiler, got it just in case we go solar thermal (but that's another story).

What litre is the thermal store
You should have had it piped up to solar coil to get best performance till you get solar fitted at least
Is there a load valve at boiler?
 
What litre is the thermal store
You should have had it piped up to solar coil to get best performance till you get solar fitted at least
Is there a load valve at boiler?

It says it's a 277 litre tank. I'll try and upload some photos now...

Its ta controlled by an 'iflo' thermostat and a programmer in the house that has 2 controls, one for hot water timing and the other for heating...

image.jpgimage.jpgimage.jpg
 
These boilers work best in to a buffer or at least into a thermal store
From what I can see I think it's direct in to heating won't be efficient at all the load valve isa standard tmv not designed for this use

This obviously is not the problem with the electrical problems but I'd also say it's not set up correctly
 
Agree with the above...
The way this is set up could be causing some of the problems with igniters as well as dropping efficiency through the floor, as the boiler will be cycling on / off more often than it should be.
I would personally go with a minimum of 35 litres of accumulator tank per kw (as a rule of thumb) on a modulating pellet boiler, to allow you to run high efficiencies and low cycle frequency - 50l/kw on non modulating boilers
I would change that TMV acting as the load unit pretty sharpish too, that will not be doing your boiler or system any good at all
 
Last edited by a moderator:
Agree with above. Can't quite see all the pipework (bottom of photo cut off)
That tmv need changing - though they should have used an esbe for the back end protection.
As for the rest - looks like no buffer tank - you need one as recommended by everyone here for efficiency purposes.
At least they've plumbed in both coils to the DHW tank (even if the "strap a stat to me" is half way up the tank) - what make is that cylinder?
 
Agree with above. Can't quite see all the pipework (bottom of photo cut off)
That tmv need changing - though they should have used an esbe for the back end protection.
As for the rest - looks like no buffer tank - you need one as recommended by everyone here for efficiency purposes.
At least they've plumbed in both coils to the DHW tank (even if the "strap a stat to me" is half way up the tank) - what make is that cylinder?

OK i'm getting more and more confused by the day. i have a few questions that hopefully you can help with:

  1. Is a 'buffer tank' different to the thermal store? or should it be the thermal store that is used as the buffer tank?
  2. is there a reason they would have taken out my small hot water cylinder and replaced it with the thermal store if it is not being used for anything other than hot water?
  3. What is the problem with the TMV and what issues is this likely to cause if it is not changed?

If you can give me any answers, hopefully I can go back and have a constructive discussion with the installer.

Thanks
 
What thermal store?

1)Buffer tanks and thermal stores are similar . The difference really is how they are used and the number and type of heating sources that are connected to them.

Thermal stores are normally directly connected to the (biomass) boiler and indirectly connected to the solar (coil) looks like your big green tank has two coils one for the boiler and one for solar. Additional the hot water would normall be heated via a coil or plate heat exchanger from the thermal store, so you with a thermal store it is not usual to have a store of Domestic Hot water - it is heated on demand.

from the pictures you've posted it doesn't look as if your big green tank is a thermal store, it looks like a large Domestic Hpt Water (DHW) Cylinder.

Buffer tanks are directly connected to the heating source (biomass boiler in your case) and then the heat for the Heating and DHW are drawn from the buffer tank.

2) DHW cylinders with Solar thermal input would normally have a volume dedicated to the Solar - i.e the volume associated with the bottom coild hence they will always be larger than a DHW cylinder heated only by a boiler.

Heres a thermal store configuration: :: AKVA SOLAR

3) Down to quality, and what they're designed for. Flow rate, nominal pressure, differential pressure, leak rate etc.

Much more information and we're going to have to start charging you :) :)

Ask for a copy of the hydraulic design from your installer (we always do one so that the plumbers put everything in correctly )
 
Last edited:
FYI - latest update - my last contact with the installer 'New World Solar Installations' was back in April when they still denied they had wired up the boiler original boiler correctly... even though it was proven adn the same faults on the second boiler, they said they would need to arbitrate this to find who was liable for the cost of the new boiler !! disgraceful behavour !!

New World Solar went into Liquidation about 4 weeks ago so i'm left high and dry.. I'm trying to contact MCS who said that installers have to offer a 2 year installation guarantee as well as the manufacturers warranty... so i am hoping that MCS have something (insurance/an agreement with another installer) in place to cover me for the next 12 months... any thoughts on this?

Also the same 2 directors from the failed New World Solar have now set up New World Energy in Cheltenham but as a new entity they would have no obligations to their previous companies customers.. so they'll just leave a wake of bad installations behind them and jump ship...
 
FYI - latest update - my last contact with the installer 'New World Solar Installations' was back in April when they still denied they had wired up the boiler original boiler correctly... even though it was proven adn the same faults on the second boiler, they said they would need to arbitrate this to find who was liable for the cost of the new boiler !! disgraceful behavour !!

New World Solar went into Liquidation about 4 weeks ago so i'm left high and dry.. I'm trying to contact MCS who said that installers have to offer a 2 year installation guarantee as well as the manufacturers warranty... so i am hoping that MCS have something (insurance/an agreement with another installer) in place to cover me for the next 12 months... any thoughts on this?

Also the same 2 directors from the failed New World Solar have now set up New World Energy in Cheltenham but as a new entity they would have no obligations to their previous companies customers.. so they'll just leave a wake of bad installations behind them and jump ship...


The insurance will have been issued to you by New World Solar, you should have a copy of it in your handover pack (Big document lots of paperwork all needed to be MCS compliant and takes about 4 - 6 hours to prepare for each job...)

Have you actually received your MCS certificate for the installation yet?

Unfortunately our experience to date has been that to almost every site that we've gone to fix installation problems where the original installation company is no longer trading, we also find that they never bothered to purchase the insurance that they had to on behalf of their clients.

MCS rules are: - you must be a member of RECC, RECC rules are you MUST issue a deposit and warranty insurance.

You need to find your policy document, then we (or someone else equally close can help) else in the politest possible way, you've been shafted and there is nothing you can do.

MCS wont help nor will RECC, they'll both just bounce you back to your insurance document.

Unfortunately the new company will be nothing to do with the old company (it certainly wont have purchased the liabilities and probably purchased the assets at a knock down price) So once again neither MCS nor RECC will help.
 
Status
Not open for further replies.

Reply to RED365 Compact 18 Wood Pellet Boiler ISSUES - MCZ / RED365 in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I have changed the 3 port actuator Honeywell head however this doesn’t seem to have solved the issue, does this mean that the programmer is faulty? Or is...
Replies
8
Views
311
Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
261
We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the man-door to the boiler room. It's intent is to 'halt' the operation of the boilers in the room should there be an emergency. He is demanding that I do...
Replies
5
Views
283
Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
2
Views
157
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
498
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock