We are looking to zone our central heating system into 2 zones. 1 for the central heating and one to heat the hot water tank via indirect coil.

Do we need a auto bypass valve installed (all radiators have TRVs installed) when we move to having 2 motorised valves installed?

We have a Worcester Bosch 24i Junior Combi boiler.

Any help would be appreciated.
 
yes you will need an auto bypass

becareful of wiring, this boiler doesnt support 240v switching
 
which worcester combi is it, is it the GREENSTAR junior or the Junior
 
ok, forget my earlier post

to make your boiler safer to use, it would be best to re route some wires

on the diagram you have provided, the GREY wires going to block 1, should be connected to LS connection on boiler

the ORANGE wires going to connection block 10 should then been re routed to LR on boiler

you can ommit the pump from the diagram also

hope that helps
 
Hi, so just to confirm, ok for 230v switching and I do need a bypass valve installed.

So I understand, the LS from the boiler to valves supplies the permanent live connection from the boiler to the valves? and the LR is the switched live from the valves to the boiler i.e. sends the call for heat signal from the valve to the boiler. Is that right?

Do I need to do anything with NS?

Can you explain why it makes it safer so that I fully understand.

Many thanks again.
Rob

Rob
 
1, yes
2, forget ns
3, so that when you turn boiler off at switch on wall or unplug, all of the connections inside are dead,
if you was to wire this with a different supply, you could have a live connection inside boiler. prob not a problem for you BUT what about when someone else is working on it!

just good practice
 
Hi, so just to confirm, ok for 230v switching and I do need a bypass valve installed.

So I understand, the LS from the boiler to valves supplies the permanent live connection from the boiler to the valves? and the LR is the switched live from the valves to the boiler i.e. sends the call for heat signal from the valve to the boiler. Is that right?

Do I need to do anything with NS?

Can you explain why it makes it safer so that I fully understand.

Many thanks again.
Rob

Rob
electrics on a gas appliance are you competant
 
Ok, we will wire as you have detailed above.

The one thing I don't get understand on the original diagram is, if the supply is turned off (via say switched spur) does this not turn the whole wiring off.

Or, do you mean on the diagram, the boiler would end up having its own supply on the L,N, E. The supply to the programmer and the wiring centre and then the GREY would go to LS and ORANGE to LR coming from another supply. This would then result in the situation where programmer etc could be turned off but the boiler still live via its own supply. Is this right?

Cheers,
Rob
 
I don't know the inns and outs of your house or how your going to do it.

It is better and should be fed by the same supply. Im just trying to make it bette for you.
 
Status
Not open for further replies.

Reply to Zone Central Heating Question in the Plumbing Zone area at PlumbersForums.net

Similar plumbing topics

Afternoon Fellas If anyone has time to help with this snag it'd be much appreciated. We have a wet-floor system controlled by John Guest UH3 and...
Replies
2
Views
500
A bit of clarification - I have extended a 3 bedroom semi detached and at the time central heating pipes were going in I told the plumber could I...
Replies
0
Views
481
I have an older gas boiler HW heating system with a taco circulator pump for each zone that worked fine last season. When turning it on for the...
Replies
4
Views
478
Hi. A new house regulation for a 2 zone heating system because it's bigger that 150sqm. I'm I right in saying zone 1 should be all of the...
Replies
10
Views
2K
We have UFH throughout downstairs. I have had one coil replaced. I have had the thermostats checked that they are linking to the correct...
Replies
8
Views
626
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock