hi need some advice as getting bit confused.
action point for combustion ratio for a combi not condensing is 0.008
what is the action point for a condensing boiler as have read 0.008 is I.D and 0.004 is A.R is the right????


many thanks
 
MI's dictate. Worcester for example state 0.0020 for a ratio, if there is no specific readings in the manuals then go off the generic guidelines. Anything over would be AR. If for example the inner flue had perished and was causing vitiation to give a high reading on a boiler it would be ID.
 
An unsatisfactory combustion reading on a room sealed boiler is only ever going to be 'AR'. Only if these POC's were to enter the room would it be 'ID'.
The MI's are required to confirm the ratio action points for a condensing appliance as most also dictate CO² limits. The Ideal HE boilers specify ratio of 0.004 and Worcester 0.002. So MI's are definitely required to confirm these limits.

The general limits for a standard eff. room sealed boiler are 0.004 or 0.008 after strip clean.
 
in the case of a performa 30 he,baxi dont want you to do a fga the boiler will never be in any spec,duotecs are 0.004 or under
 
Have a read of TB 126. GSR recommends that boilers with air/gas ratio valves and manufactured by members of HHIC are classified as:

Exceeds .008 = ID
Exceeds .004 but not exceeds .008, or exceeds manu's guidance = AR

This TB has been around for a while and it's a bit of a shame they've never incorporated the guidance into Unsafe Sits.
 
That seems a bit odd! So do they typically exceed .008?
yes,its to do with the resistance trough the recuperator oddly the 24kw does give a good reading typically 0.002 flat out on dhw
 
I have found very few outside spec, and I have serviced hundreds.
 
We have a few hundred of these. I've seen a couple pushing year 3-4 to be slightly out on the CO/CO2 ratio.
 
Status
Not open for further replies.

Reply to combustion ratio? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer...
Replies
4
Views
280
Recently had a Viessmann Vitodens combi boiler installed, quite often when the adjacent cold mixer tap is opened the boiler starts for a few...
Replies
3
Views
226
Hi they used to say as a last resort you could discharge the D2 pipework at high level and turn it back to the wall. Similar to a combi boiler. I...
Replies
11
Views
330
We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the...
Replies
5
Views
311
I have had a look at previous posts and think I know the answer to this but just before I make it worse could I just check what you think about...
Replies
7
Views
244
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock