Hi folks. I have a couple of issues, any help advice much appreciated.
1. When my hot water tank thermostat demands hot water (wired into Honeywell wiring centre), I do not get a switched live to the boiler. I get 69 volts ac for both on and off wires from the tank stat. I have fitted a new tank stat, same results.
2. When my heating comes on, it stays on. ie the spring on the Y plan motorised mid position valve stays open. I have to turn the power off and then back on in order for the spring to recede and stay there (once CH temperature is satisfied).
 
1. Have you checked the voltages from programmer to wiring centre and cylinder stat? You should have 230volts on grey wire when HW is off or cylinder stat satisfied and 230 volts to cylinder stat common when in HW mode.
2. What you're describing is how the mid position valves work, it holds the last port of call
 
Hi folks. I have a couple of issues, any help advice much appreciated.
1. When my hot water tank thermostat demands hot water (wired into Honeywell wiring centre), I do not get a switched live to the boiler. I get 69 volts ac for both on and off wires from the tank stat. I have fitted a new tank stat, same results.
2. When my heating comes on, it stays on. ie the spring on the Y plan motorised mid position valve stays open. I have to turn the power off and then back on in order for the spring to recede and stay there (once CH temperature is satisfied).

These may be of assistance.

View: https://www.youtube.com/watch?v=F5m8f6HN2Us
 
The 69 volts is normal . It’s a back voltage from the 3 port when both HW and Heating are on



my guess is you have a wiring problem.
Heating off HW on
trace voltages from programmer, in to stat, out of stat, and common (3 wires needed)
Connection 1 (demand)from stat should give 240 on orange.
Test schedule
hW on heating off

240 orange from cyl stat(demand)
Turn cyl stat off
240 Volts Grey wire from stat (no demand)
Turn programmer heating off cyl on same result
Heating on HW off
240 V grey 240V white
Both on
3 port mid
240 v orange 240 V 69v Grey


Hope this helps
 
The 69 volts is normal . It’s a back voltage from the 3 port when both HW and Heating are on



my guess is you have a wiring problem.
Heating off HW on
trace voltages from programmer, in to stat, out of stat, and common (3 wires needed)
Connection 1 (demand)from stat should give 240 on orange.
Test schedule
hW on heating off

240 orange from cyl stat(demand)
Turn cyl stat off
240 Volts Grey wire from stat (no demand)
Turn programmer heating off cyl on same result
Heating on HW off
240 V grey 240V white
Both on
3 port mid
240 v orange 240 V 69v Grey


Hope this helps
Thanks Ziggie. It was the Honeywell wiring panel. It was one with a circuit board and some cut links. I binned it and replaced with a length of screw in electrical connectors. It’s worked perfectly ever since.
 

Reply to No switched live to boiler when hot water tank thermostat demands heat + CH staying on. in the USA area at PlumbersForums.net

Similar plumbing topics

  • Question
Have a sytem boiler with unvented cylinder with 2 heating zones plus hot water in a house we moved into recently. To start with we were always...
Replies
8
Views
417
M
Hello, We’ve recently moved into a fairly old, fairly big detached house (i.e. fairly draughty, but not too bad by any means) with a fairly new...
Replies
0
Views
278
MartinPod81
M
Hi, We moved into a new property yesterday and are a little baffled by the heating/water tank situation. The previous owners unhelpfully left any...
Replies
3
Views
338
Hi, I have a Vailant EcoTec Boiler with a Megaflo. These are controlled by a Honeywell controller. I have one 3 port diverter, where one of the...
Replies
5
Views
259
B
Issue with boiler short cycling in system with hot water tank. We have an ideal heating logic heat2 h15 boiler which feeds a hot water tank...
Replies
10
Views
1K
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock