Search the forum,

Discuss Boiler short cycling in system with hot water tank in the Central Heating Forum area at PlumbersForums.net

B

Boiler short cycling

Issue with boiler short cycling in system with hot water tank.

We have an ideal heating logic heat2 h15 boiler which feeds a hot water tank upstairs in the house. We have an issue where if the boiler isn’t set to 80c then the boiler will short cycle, the hot water tank thermostat is set at around 60c however if we have the boiler at 65 or 70 it will short cycle constantly, it heats up to over the set temperature and drops immediately and then between 30-60 seconds will fire back up and repeat the process. The only way to stop this is to have the boiler set to 80c and at this point it seems to modulate a lot better and hold itself at that temperature which is fine other than it makes the radiators scolding hot, if we were to have children in the house I would be worried it could burn them. Is there an obvious reason for this or will we have to put up with having the radiators so hot all of the time?
 
What’s the coil capacity of the cylinder eg is it an old copper one
 
IME, 65°C should be (just) enough to heat a DHW cylinder to 60°C in a reasonable time without excessive cycling. The system does need investigating. As well a being hazardous, flow temperatures above 65°C will likely increase the fuel consumption of the boiler by preventing it from operating in 'condensing mode'.

A few extra questions to help diagnosis
  1. How long have you had this problem?
  2. Do you live in a hard water area?
  3. Can you post a photo showing the tank and the relevant pipework?
  4. What sort of pump does the system have and what setting is it on?
  5. Is there a balancing valve that controls how much flow the DHW cylinder receives?
Hot radiators are not only dangerous to children. If an elderly person falls, e.g. in a bathroom, lands against a hot radiator and is unable to move away, the resulting burn can be very nasty.
 
IME, 65°C should be (just) enough to heat a DHW cylinder to 60°C in a reasonable time without excessive cycling. The system does need investigating. As well a being hazardous, flow temperatures above 65°C will likely increase the fuel consumption of the boiler by preventing it from operating in 'condensing mode'.

A few extra questions to help diagnosis
  1. How long have you had this problem?
  2. Do you live in a hard water area?
  3. Can you post a photo showing the tank and the relevant pipework?
  4. What sort of pump does the system have and what setting is it on?
  5. Is there a balancing valve that controls how much flow the DHW cylinder receives?
Hot radiators are not only dangerous to children. If an elderly person falls, e.g. in a bathroom, lands against a hot radiator and is unable to move away, the resulting burn can be very nasty.

We have had this problem since we moved in back in March this year so the boiler and the tank are both brand new.

We live in a hard water area but as mentioned we’ve only been In since March and it is a brand new property.
 
IME, 65°C should be (just) enough to heat a DHW cylinder to 60°C in a reasonable time without excessive cycling. The system does need investigating. As well a being hazardous, flow temperatures above 65°C will likely increase the fuel consumption of the boiler by preventing it from operating in 'condensing mode'.

A few extra questions to help diagnosis
  1. How long have you had this problem?
  2. Do you live in a hard water area?
  3. Can you post a photo showing the tank and the relevant pipework?
  4. What sort of pump does the system have and what setting is it on?
  5. Is there a balancing valve that controls how much flow the DHW cylinder receives?
Hot radiators are not only dangerous to children. If an elderly person falls, e.g. in a bathroom, lands against a hot radiator and is unable to move away, the resulting burn can be very nasty.

IME, 65°C should be (just) enough to heat a DHW cylinder to 60°C in a reasonable time without excessive cycling. The system does need investigating. As well a being hazardous, flow temperatures above 65°C will likely increase the fuel consumption of the boiler by preventing it from operating in 'condensing mode'.

A few extra questions to help diagnosis
  1. How long have you had this problem?
  2. Do you live in a hard water area?
  3. Can you post a photo showing the tank and the relevant pipework?
  4. What sort of pump does the system have and what setting is it on?
  5. Is there a balancing valve that controls how much flow the DHW cylinder receives?
Hot radiators are not only dangerous to children. If an elderly person falls, e.g. in a bathroom, lands against a hot radiator and is unable to move away, the resulting burn can be very nasty.

Hi,

We’ve had this issue since we moved in in March of this year, we do live in a hard water area but the house, boiler and tank are all brand new as mentioned we have only been in since March.

I’ve put a picture in of the tank and the pipe work please let me know if you need any closer view etc.

I’ve also put in a picture of the pump, it’s been on Auto for the majority of the time although I did turn it up to it’s highest setting for only a short time to see if it made any difference which it didn’t seem to.

Finally I’m not too sure on the balancing valve it doesn’t look like there is but I unfortunately don’t have a lot of plumbing experience to go off.

Appreciate your response.
 

Attachments

  • image.jpg
    image.jpg
    527.8 KB · Views: 12
  • image.jpg
    image.jpg
    351.8 KB · Views: 8
Hi Shaun,

It’s a brand new cylinder along with boiler on a new build property we moved into in March, on the label it says the coil rating is 15.9 kw

Cheers

Wouldn’t do anything it’s brand new get them out to sort the issue the boiler should run for 10 mins plus easily

Could be the left brass valve is shut / nearly
 
Wouldn’t do anything it’s brand new get them out to sort the issue the boiler should run for 10 mins plus easily

Could be the left brass valve is shut / nearly
I’ve had the boiler company out previously and they ran tests on the boiler and said there was no issues. Makes me think it’s either the plumbing or to do with the tank itself, who would you recommend requesting first the plumber or the tank fitters coming in
 
I’ve had the boiler company out previously and they ran tests on the boiler and said there was no issues. Makes me think it’s either the plumbing or to do with the tank itself, who would you recommend requesting first the plumber or the tank fitters coming in

The boiler company? The people who installed the boiler or the manufacturers ?
 
The manufacturer of the boiler, ideal heating engineer came and ran tests on it and said there was no issue with the boiler itself.

No the installers need to come out
 

Reply to Boiler short cycling in system with hot water tank in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
1
Views
127
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
123
Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I have changed the 3 port actuator Honeywell head however this doesn’t seem to have solved the issue, does this mean that the programmer is faulty? Or is...
Replies
8
Views
271
Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
224
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
323
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock