Hi. I'm new to all this, and not sure it's appropriate,
Flue1.jpg
Flue2.jpg
so be gentle with me.
This flue is to my newly fitted replacement Ideal Logic Max boiler. The position is the same as it was with my old boiler. I have been told in the past that it was incorrect, but my fitter has assured me it is now OK with this plume kit. It certainly seems OK, and the plume directs away from the door nicely. I realise it's not a Balcony, a Car Port or a Soffitt, but reading the guidelines I'm not too sure it's right. I obviously don't want any problems with Ideal if a warranty claim is ever required.
Any advice, reassurance would be appreciated. Thanks

Flue3.jpg
 
Last edited:
Definitely not right to me. But cannot see much in the Manufacturer’s Instructions. Cannot even see a flue locations drawing and table. I would say needs changing. Is that passage a public right of way? Or just to your house?
 
Totally agree mate, I just don’t understand why some engineers force an install in sometimes why make it difficult or run the risk of someone telling you to change it
 
Definitely not right to me. But cannot see much in the Manufacturer’s Instructions. Cannot even see a flue locations drawing and table. I would say needs changing. Is that passage a public right of way? Or just to your house?
Just my house. I'm finding the flue location drawings very confusing.
Changing in what way. The Boiler / flue location, on just the plume kit?
 
If it were me, I would extend the flue to above the roofline above and point the flue terminal towards the neighbouring property or back towards the tiled roof.
I would have the terminal a minimum of 500mm above the tiled roof.

Tricky and grey area, but I would do this as a minimum to at least attempt to get the plume away from the entrance.
 
Just my house. I'm finding the flue location drawings very confusing.
Changing in what way. The Boiler / flue location, on just the plume kit?

You would need to speak to ideal, but I would come out the wall with an elbow and an horizontal flue extension. Then the terminal and plume management kit, so that it clears that low roof. Making sure that the flue is correctly supported. I wouldn’t go vertical. There looks like that there could be boundary issues. This is just an idea and would need to be checked by ideal first as not sure there standard flue can be used externally.
 
If it were me, I would extend the flue to above the roofline above and point the flue terminal towards the neighbouring property or back towards the tiled roof.
I would have the terminal a minimum of 500mm above the tiled roof.

Tricky and grey area, but I would do this as a minimum to at least attempt to get the plume away from the entrance.
I suggested taking the plume kit up through the false ceiling, and 90' through the back. I'm guessing it's not allowed to box in the elbow though.
 
Totally agree mate, I just don’t understand why some engineers force an install in sometimes why make it difficult or run the risk of someone telling you to change it
Annoying thing is, shifting the boiler wasn't a massive issue, but fitter insisted this option would be OK, and much cheaper. Now What though? Fork out for more plume kit, or a days work to resite the boiler?
 
You would need to speak to ideal, but I would come out the wall with an elbow and an horizontal flue extension. Then the terminal and plume management kit, so that it clears that low roof. Making sure that the flue is correctly supported. I wouldn’t go vertical. There looks like that there could be boundary issues. This is just an idea and would need to be checked by ideal first as not sure there standard flue can be used externally.
This isn’t just extra plume kit mate
 
It might actually be ok. Looking at the measurements for the plume kit you can actually run the outlet 25mm away from the wall. The only thing which may flag it up, is the distance from the door. I know it's not a carport or balcony but the characteristics of the opening are similar and this instance I would aim for the 1200 measurement.

20190202_201910.png
 
It might actually be ok. Looking at the measurements for the plume kit you can actually run the outlet 25mm away from the wall. The only thing which may flag it up, is the distance from the door. I know it's not a carport or balcony but the characteristics of the opening are similar and this instance I would aim for the 1200 measurement.

View attachment 36751
Where did you get those figures from?
 
Google ideal boiler flue accessories and download this pdf. It's worth a note that only one minimum measurement can be taken down to 25mm and then all others would be subject to the standard minimum distances, and I feel this may be too much info for the public forum so remove it if you feel it's necessary

20190202_203414.png
 
Google ideal boiler flue accessories and download this pdf. It's worth a note that only one minimum measurement can be taken down to 25mm and then all others would be subject to the standard minimum distances, and I feel this may be too much info for the public forum so remove it if you feel it's necessary

View attachment 36752
I would still check with ideal though as that isn’t in the MI’s
 
If you think about it, the outlet up against a wall shouldn't be an issue, it won't cause a negative effect on the boiler output and the only reason we have a min measurement for internal corners is due to possible POC build ups entering back down the air intake.
 
Thanks for all your help guys. As suggested, I contacted Ideal tech support, and they came back with:

Thank you for your email regarding the flue. The flue has not been fitted to manufactures instruction,


  • The air intake is too close to the door
  • The flue is not open at 3 sides (only 1)
  • The air intake is under a different pressure zone to the exhaust


We would recommend your installer would need to rectify the flue.

My installer has agreed to sort it at no cost to me. Whether that is a complex flue arrangement or resiting the boiler. Up to him I guess.
 
That would be boiler move as the air intake is too close
 

Reply to Flue Location.. Is it a Balcony, a Car Port or a Soffitt? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi all. Hope you have all been keeping well. A while back I decided I only wanted to fit one brand of boiler and decided on Viessmann due to...
Replies
9
Views
264
I have an ideal vogue max S18 boiler and I’m considering fitting auto balancing TRVs, my question relates to the boilers pump. I see a boiler...
Replies
1
Views
173
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason...
Replies
3
Views
304
Hi guys....we have an old Astracast sink top....I think its a composite sink....has a big single bowl. My wife thinks it looks scruffy....looks...
Replies
2
Views
190
I was stupid enough not to check the position of the pipes under the tiles when installing a toilet and drilled right through the center of a 16...
Replies
0
Views
221
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock