dont ideals come with built in by-passes? If valves are on returns are they the right way>?
Discuss Zoned central heating problem in the Plumbing Zone area at PlumbersForums.net
Hi Fred I've never put them on the return if they are on the return what's to stop the heat on the flow going where it wants Evan with one return it only creeps up getting the nearest rad warm you must have linked them somewhere is a new build might have put a downstairs rad in upstairs loop or other way round easy mistake to do
Hi Guys,
Just had my heating sorted after a short 4 months wait! just glad we've had a nice summer. Anyway just thought I would update you on what the issues were.
1st no by-pass circuit installed.
2nd zone valves on return instead of flow.
3rd 2 flow pipes fitted (1 to each zone) but only 1 return for both zones.
Pleased to say that the chap today knew what he was doing and has put it all right. Thanks for all your advice, looks like everyone on he was correct in one way or another.
cheers fellas