Hi all,

I'm having problems with my boiler and am hoping someone can offer me advice. Few days ago our heating and hot water stopped and on inspecting the boiler I was met with the F.75 error. We had a plumber come out and the first thing he asked was if I had the owners manual which didn't fill me with confidence. Anyway, I didn't have one as we recently moved in so the plumber tried refilling the system to bring it up to 1.4/1.5 as he said this what Vaillant's were supposed to be at. It got it working which was great until yesterday morning when we lost heating and hot water again. As I had watched what he had done, I refilled it and again this morning the pressure had dropped.

Now before I call a plumber out again, I want to try and narrow the issue. I have been searching and found that it could be a number of things but I want to try and establish if it's a leak in the system or if it's a problem with the boiler. Is it possible for a DIY'er to do this? I have checked the visible areas around the radiators for a leak but can't see any signs of one (assuming that going from 1.5 to 0.9 in less than 24 hours would mean a reasonable size leak!). Also, there are a few "valves" with screw slots underneath and one was at 45 degrees. Should all the valves be closed? If not, which ones should be open and which should be closed?

Any help/advice appreciated.

Thanks. :)
 
Last edited:
Hi all,

I'm having problems with my boiler and am hoping someone can offer me advice. Few days ago our heating and hot water stopped and on inspecting the boiler I was met with the F.75 error. We had a plumber come out and the first thing he asked was if I had the owners manual which didn't fill me with confidence. Anyway, I didn't have one as we recently moved in so the plumber tried refilling the system to bring it up to 1.4/1.5 as he said this what Vaillant's were supposed to be at. It got it working which was great until yesterday morning when we lost heating and hot water again. As I had watched what he had done, I refilled it and again this morning the pressure had dropped.

Now before I call a plumber out again, I want to try and narrow the issue. I have been searching and found that it could be a number of things but I want to try and establish if it's a leak in the system or if it's a problem with the boiler. Is it possible for a DIY'er to do this? I have checked the visible areas around the radiators for a leak but can't see any signs of one (assuming that going from 1.5 to 0.9 in less than 24 hours would mean a reasonable size leak!). Also, there are a few "valves" with screw slots underneath and one was at 45 degrees. Should all the valves be closed? If not, which ones should be open and which should be closed?

Any help/advice appreciated.

Thanks. :)

Get a different engineer if you don't trust the one you have. I'd be looking at filling loop and expansion vessel with a drop that big.
 
I will be calling someone else, someone who's knows the Vaillant like the back of his greasy hand! :) With a drop that big, are you saying it's more likely to be the boiler at fault? If that's the case then it's a slight relief as I don't fancy having to gut the flooring to redo the pipework!
 
I will be calling someone else, someone who's knows the Vaillant like the back of his greasy hand! :) With a drop that big, are you saying it's more likely to be the boiler at fault? If that's the case then it's a slight relief as I don't fancy having to gut the flooring to redo the pipework!

How old is the boiler?

To lose pressure that quickly, you either have

a. A big leak that suddenly sprang out of nowhere, or
b. a pressure increase resulting in a PRV operating.
 
Tbh asking for the manual isn't necessarily a bad sign as all boilers have different fault codes and no engineer can be expected to know them all off top of his head.

Agree with comments about prv and leaks.

Sent from my GT-I9100 using Tapatalk 2
 
Tbh asking for the manual isn't necessarily a bad sign as all boilers have different fault codes and no engineer can be expected to know them all off top of his head.

Agree with comments about prv and leaks.

Sent from my GT-I9100 using Tapatalk 2

Agreed. Always ask for a manual unless I have my ipad handy.
 
How old is the boiler?

To lose pressure that quickly, you either have

a. A big leak that suddenly sprang out of nowhere, or
b. a pressure increase resulting in a PRV operating.

I believe it was installed in 2007/2008. We've been here 6 months and haven't had any problems until few days ago. What does b. mean? Would you mind elaborating?
 
Last edited:
Tbh asking for the manual isn't necessarily a bad sign as all boilers have different fault codes and no engineer can be expected to know them all off top of his head.

Agree with comments about prv and leaks.

Sent from my GT-I9100 using Tapatalk 2

best not call me either because first job is 'the installation manual' i dont like guessing too much.
rather, i like guessing then checking first.
bet the prv's passing.
 
I guess it was a good sign that he asked for the manual. I did offer to bring it up on my iPad but he said he would check the basics first.
 
I believe it was installed in 2007/2008. We've been here 6 months and haven't had any problems until few days ago. What does b. mean? Would you mind elaborating?

Can't elaborate too much in case you try to do a DIY fix and blow yourself up.
 
Is there a way of "isolating" the boiler from the rest of the system to see if it still drops in pressure? I mean without fiddling with the internals or disconnecting pipes etc
 
Try this site to download vaillant manuals, [DLMURL="http://www.vaillantdownloadservice.co.uk/Pages/Default.aspx"]Vaillant Technical Download Service[/DLMURL]
Find the Isolating Valves on the Flow and Return pipes under the boiler, turn them Off, and leave overnight to see if it makes any difference to pressure loss. ( don't use the central heating during this time ).
You can check the PRV ( Pressure Relief Valve ) is letting by, by looking for the pipe which goes from the boiler through to the outside.
 
Last edited by a moderator:
Use the right size Allen key to turn the flow and return isolation valves off or you'll find you rip and damage them using a slotty. Prv can be easily checked. A vaillant savvy engineer will be able to cycle back through the faults on a three year old v combi, might be able to detect some other previous fault that might shed some light on this one. Any pipes on ground floor that might be letting by, under screed or floor boards, fernox leak sealer will only deal with small weeps not drops of your like.
 
if you say that the boiler runs ok when pressurised but loses pressure overnight, probably what's happening is the expn vessel has failed and this means when the boiler runs, there's nowhere for the hw to expand and the prv operates until 3 bar is established, then everything is tickety until the heating goes off, water cools, pressure drops and next morning boiler wont work due to low system pressure. So ask engineer to check expn vessel first before looking at prv and other leak possibilities.

from memory doesn't gsr state you shouldn't work on a gas appliance without access to the mfis
 
Last edited by a moderator:
we are not actually supposed to work on any appliance with out the manufacturers instructions present a lot of engineers will have a laptop with them onyears ago we had a plate on the boiler which told us everything we needed to know now the plate would need to be as big as the boiler
 
I advise u get a vaillant listed engineer in - mucking about with pressurised systems when you
have little knowledge is v. dangerous. Combi systems and other pressurised set ups have highly
pressurised v. hot water all around the circuit. Get it wrong and if you unlucky someone dear to you
can get scalded - last one i read about was a baby in bed - pipe above over pressurised - 2-3 degree burns.

centralheatking
 
Well... the boiler is screwed. Had a leak which wet pretty much the whole of the inside. It's water tight now but still getting errors and I think due to water getting everywhere it may be beyond economical repair.

So my question is, what is a reasonable price for a new Ecotec Plus 831 and like for like replacement fitting? I'm also thinking about getting a Magnaclean and some sort of limescale filter fitted at the same time. Probably need a power flush too.

Im in NW London and for the boiler plus fitting have been quoted £1600 (excluding the extras). Is this reasonable?
 
cheap price, check your house insurance some policys cover this, worth a phone call
 
£1600 in London seems pretty good to me - but just what is the quote for ? - post it on here and we can all go over it - have you tried an independant Vaillant specialist - they can work wonders -
magnaclean is only one ferric sludge capture device there are others - which are better in my opinion and can do more - pm me if you want more totally independant info cause the centralheatkings do not do N London - we stick to West Lancashire
Well... the boiler is screwed. Had a leak which wet pretty much the whole of the inside. It's water tight now but still getting errors and I think due to water getting everywhere it may be beyond economical repair.

So my question is, what is a reasonable price for a new Ecotec Plus 831 and like for like replacement fitting? I'm also thinking about getting a Magnaclean and some sort of limescale filter fitted at the same time. Probably need a power flush too.

Im in NW London and for the boiler plus fitting have been quoted £1600 (excluding the extras). Is this reasonable?
 
Sure be worth a try i had Baxi heateam out on a 7 year old solo pretty much rebiult the whole thing after the hex leaked , will be much cheaper than a new one if they will do it
 
Yeah the thread may be 4 weeks old but READ what Roger wrote the op posted again about it Today
 
ok so maybe iam but new to this give a guy a break ha ha vaillant good shout though, needs to be sure its on the boiler though
 
I will be calling someone else, someone who's knows the Vaillant like the back of his greasy hand! :) With a drop that big, are you saying it's more likely to be the boiler at fault? If that's the case then it's a slight relief as I don't fancy having to gut the flooring to redo the pipework!

Sorry I disagree with the comment that asking for MI's that tells me he is professional. And is going to follow manufacturers fault finding guide.

Check for big leaks around rads, look outside on the blow off pipe that boiler is not blowing off, if it is then get a GSR engineer to check PRV and expansion vessels and the pipe to the vessel.
 
expansion vessel definate common fault i agree but to call vaillant to represurise is over the top unless the vessel is faulty and even then
 
I think an internal leak has been repaired (I'd hazard a guess at one of the rubber hoses) but electrics have taken a soaking so poss pcb, fan, gas valve, pump, etc. deff a job for Vaillant IMHO.
 
i agree though have dried them out before when the hoses have gone usually due to expansion vessel loss of pressure
 
Status
Not open for further replies.

Reply to Vaillant Ecotec Plus 831 losing pressure overnight in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two...
Replies
2
Views
187
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up...
Replies
2
Views
261
PSxxxxxx
P
Hi, I have a Worcester 28i junior boiler that has started to lose pressure, only when using the central heating. When using hot water I have no...
Replies
6
Views
238
I have done pressure test for 2" high pressure pipe line by closing the pipe with rubber plugs at the ends. It was 3 bar and I kept it for 24...
Replies
6
Views
277
  • Article
A Plumber Who Worked Illegally Gets A Suspended Sentence After Falsely Claiming To Be Gas Safe Registered. A Plumber in Herefordshire was...
Replies
0
Views
230
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock