any one see anything wrong with this eg t rule etc sealed system
View attachment 27845
as normally any suggestions welcome and thnx again
No PRV to expansion vessel and it's discharge pipe.
Probably just the way it's drawn but the blue return pipe bypasses the mag filter.
Have you drawn that ?
Well, I can't say it's wrong, cos I can't tell if I'm reading the drawing right so excuse me if I've misunderstood Shaun. I would put fill/expansion in behind pump. You may have done that so apologies if you have.
You want as much of system under positive pressure as poss, so neutral point needs to be close to back of pump
P.s. Don't change your day job to become a draughtsman.