Kerr Gas 1

Hi,

Im fitting a 28I junior tomorrow, my problem is it could be difficult to run the discharge pipework from the PRV to outside i was wondering if it is ok to run it into internall drainage. any advice will be apprechiated
 
sorry it's waste pipe, currently being used for a wash machine but im planning on using it for condi and hopefully the prv discharge. i was hoping if i installed a tundish this would be satisfactory, any ideas
 
its gravity fed at the moment, back boiler with indirect cylinder. usually id use the cylinder drain to connect my prv but on this system it doesnt run straight outside.
 
I have installed hundreds internal into hep v/o trap and have been inspected by gas safe and building cony=trol and never been pulled for it as long as you either have a tundish or air gap to see it blowing off
 
I have installed hundreds internal into hep v/o trap and have been inspected by gas safe and building cony=trol and never been pulled for it as long as you either have a tundish or air gap to see it blowing off

is that on new build jobs ?
 
In the past ive put he prv on a rad tail then discharged it outside in usual way, obviously choose rad on external wall
 
Not allowed on my local contracts, must be ran direct to externall. This then determines where we are allowed to fit the boiler. Does cause us problems at times.
 
Status
Not open for further replies.

Reply to PRV discharge pipework in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, I have a Worcester 28i junior boiler that has started to lose pressure, only when using the central heating. When using hot water I have no...
Replies
6
Views
272
Hi everyone, Just wanted some confirmation regarding a PRV fitted to the mains supply in my building. All 6 flats in the building are now...
Replies
15
Views
1K
Hi - I have a Telford's Tristar Thermal store with a Caleffi 533..h PRV set to 3 bar. The PRV doesn't appear to be drop tight, so static rises...
Replies
2
Views
551
Hi I've got water hammer issues with my cold feed and some with the hot feed. When the cold sink tap, cold bath tap and thermostatic shower in...
Replies
1
Views
452
Good afternoon, I am experiencing a pressure issue with my heating system and was hoping to receive additional insight as to what the problem...
Replies
9
Views
400
Back
Top