southcoastboile

Plumbers Arms member
Plumber
Gas Engineer
Messages
1,279
Went out to this one. Found locking out on air flow fault.
fan runs but no ignition most of the time. Sometimes will fire and run for around 40 secs before locking out on air flow.
dead tested aps and had continuity when I blew through it. Removed and cleaned Venturi, ran water through fan to clean impeller, quite dusty, sprayed heavily with wd40 incase it was running to slow. Still doing the same.

it locked out on air flow after firing red led flashing only on left hand side. Then it went back into operating mode again and went through ignition sequence without being reset. This made me think pcb.

what threw me though was after cleaning fan and spraying with we etc I removed both wires to aps with fan running and checked for continuity. It was open circuit so that made me think aps or fan at fault.

any ideas?
 
Only issue I've had with the he is the spark gen failing in cold weather.
 
I didn't look to see if there was a spark generator separately. Is it not part of the pcb?
 
That's another possibility then. I think there must be 2 faults though because surely if the fan was running fast enough and Venturi clear and Aps hoses okay the Aps should make and it didn't.

That at added to the fact that the boiler restarts itself after a lockout indicating pcb.

its one of those awkward faults.
 
Status
Not open for further replies.

Reply to Potterton subprima 60 (not the one with side pcb the pcb is at bottom of boiler) in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I'm looking for some advice on a frustrating problem I'm having with my old Eurostar 50-60s oil boiler please? Although it's old, most parts...
Replies
3
Views
767
Dear All New member here, coming looking for help. A few weeks ago I had work carried out by a British Gas Homecare service technician. It...
Replies
14
Views
1K
Context for issue: Last winter the temperature switch on my boiler shorted somehow, the boiler was then running WAY too hot and ended up...
Replies
6
Views
604
B
Context for issue: I'd like to start by saying I'd rather not read 100 "Hire a professional comments", I will do that when/if it comes to it, but...
Replies
0
Views
379
Butchy10
B
Hello, recently our boiler stopped working properly, causing a lack of heat in our 14-radiator splitter in 3 storeys. having only one boiler at...
Replies
4
Views
428
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock