J

Jim63

Would appreciate any advice please. I am trying to add some underfloor heating in the kitchen using the existing oil fired boiler and hot water system.

Have installed 10mm pipe loops around the floor (not yet covered over with the screed), but boiler is not coping with this.
If I turn off all 2 or 3 radiators the pipes get nice and hot. With all downstairs radiators on but upstairs off the pipes are only luke warm.

The boiler (Trianco 25kw, with grundfoss 15/50 pump) has always seemed ok before for size of house (5 beds) although rooms on one side sometimes cooler.

Some websites seem to suggest a larger boiler for this size of house, is this the problem or I am expecting too much from the new underfloor heating circuit, or any other suggestions?
 
Jim
This is not a DIY job get someone in who understands what they are doing before it ends in tears. What mixing manifold are you using, why are you using hight resistants 10mm pipe.
What insulation are you using, what is the existing pump head, are the controls linked / are you using thermostat so that it is Building regs compliant, should I go on ?????
Not trying to be clever just giving you a flavour or what U/F involves.
 
Hi Chris
I have done this in conjunction with a heating engineer, he had done something similar and it seemed to work ok.
We have not used a manifold, it is connected to the radiator tails. The plan was to not to replace the radiator heating but just to get some circulation under the floor to take the chill off.
I appreciate that the subject can be complex but hoped to achieve a little extra heat in this one floor area.
 
Hi Chris
I have done this in conjunction with a heating engineer, he had done something similar and it seemed to work ok.
We have not used a manifold, it is connected to the radiator tails. The plan was to not to replace the radiator heating but just to get some circulation under the floor to take the chill off.
I appreciate that the subject can be complex but hoped to achieve a little extra heat in this one floor area.
Sorry but he does not know what he is doing, you should not run U/F directly from the heating the max water temp is around 50deg C. It will not work !!!!
Get someone who knows Jim.
 
Jim, listen to Chris. Your heating engineer doesn't have a scooby doo. There are regulations with regard to maximum floor temps.

10mm pipe :) Made me chuckle.
 
Sorry but he does not know what he is doing, you should not run U/F directly from the heating the max water temp is around 50deg C. It will not work !!!!
Get someone who knows Jim.


10mm pipe :) Made me chuckle.

The "engineer" seems to have forgotten the Bernoulli law. 10 mm pipe...
It may be ok for the drip feed... :wink: not for the CH...

Use at least 15/22/25mm one (depending on loop length).
Also maximum system system design temperature should be <50 degrees.
You can do it without mainfold IF your radiators are BIG ENOUGH,

So they chunk out enough heat when the delta is <25 degrees.

Replace underfloor pipes with 22/25 mm one and put your boiler's thermostat at 45 degrees max.

Then make sure that it doesn't cylce (and there is enough flow through it).
 
hot feet hot feet hot feet, it will be like running across hot sand!!!!!!!!!!!!!!
 
Status
Not open for further replies.

Reply to Oil boiler capacity and underfloor heating advice in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, I have a Worcester 28i junior boiler that has started to lose pressure, only when using the central heating. When using hot water I have no issue, however, when running the heating the pressure drops. Im looking for some ideas on what could be causing this. I have no sign of pipe leaks...
Replies
6
Views
213
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
2
Views
237
P
Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
265
Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I have changed the 3 port actuator Honeywell head however this doesn’t seem to have solved the issue, does this mean that the programmer is faulty? Or is...
Replies
8
Views
327
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
503
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock