Hello my parents have a house with an open vented system. It has an oil boiler feeding 4 circuits of radiators and also an indirect hot water cylinder. It also has a solid fuel fireplace back boiler (with 4 pipes) to it. The fire can heat both the radiator and the hot water. The fire is never lit. The feed and expansion tank is regularly overflowing every so often, mostly when the hot water heating circuit stops (I think). The feed and expansion tank gets sporadic water fill from the vent pipe and I can also feel a small pulse, or in flow, of water from the feed and expansion tank outlet. Here is a diagram. The system has been like this for years, but only started giving this problem a few months ago. Be gentle.
 
1. No diagram visible.
2. Could be blocked / partially blocked feed from F&E into system.
3. If you can identify the feed pipe, try running a magnet along the outside. Assuming it's not a steel pipe, the magnet should not be attracted, unless there is some magnetite (basically rust off the inside of radiators) inside the pipe. The presence of magnetite points (not infallibly) to a blockage.
 
hopefully i can attached it now. sorry i tried to attached a pdf earlier.
 

Attachments

  • plumbingsystem.PNG
    plumbingsystem.PNG
    214.6 KB · Views: 24
1. No diagram visible.
2. Could be blocked / partially blocked feed from F&E into system.
3. If you can identify the feed pipe, try running a magnet along the outside. Assuming it's not a steel pipe, the magnet should not be attracted, unless there is some magnetite (basically rust off the inside of radiators) inside the pipe. The presence of magnetite points (not infallibly) to a blockage.
thanks - i will give that a try!
 
Maybe I didn't look hard enough but it looks as if the OF boiler system is sealed? as the vent is blanked and no cold feed. If sealed, can you indicate where the expansion vessel is teed in.
 
Maybe I didn't look hard enough but it looks as if the OF boiler system is sealed? as the vent is blanked and no cold feed. If sealed, can you indicate where the expansion vessel is teed in
The system doesn’t have an expansion vessel fitted anywhere, but the water in the CH/HW system is expanding and getting into the feed and expansion tank somehow. The only way I can see for expanding water to escape the HW/CH system is via the blue arrowed line in the attached picture. i.e. the water has to go via the back boiler (assuming all 4 pipes lead into one common chamber in the back boiler). Does it make any sense? I'm guessing it is not the way it should be...
 

Attachments

  • diagram.PNG
    diagram.PNG
    218.8 KB · Views: 16
Last edited:
No, that's certainly not correct, here is a idea of the correct way.
The gas boiler is showing gravity flow DHW heating like the solid fuel but doesn't have to be this way, it can be fully pumped.

1610110068734.png
 
Last edited:
No, that's certainly not correct, here is a idea of the correct way.
The gas boiler is showing gravity flow DHW heating like the solid fuel but doesn't have to be this way, it can be fully pumped.

View attachment 47045
Thanks for your post, the comments and diagram are very useful, and I appreciate the time you took. It is food for thought. The current oil boiler has only got two pipes running to and from it, so it would require a bit of digging in the floor. But if it is the only way to fix it then needs must...
 

Reply to Intermittent Overflow of Feed and Expansion Tank in the USA area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
426
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold...
Replies
2
Views
205
Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two...
Replies
2
Views
207
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up...
Replies
2
Views
271
PSxxxxxx
P
Hello all, I'm would like to extend an existing outside tap to another point in the garden. I'm about to pour a concrete patio and was hoping to...
Replies
6
Views
270
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock