I would really like some advice about a problem with a hot water issue. I am a registered plumber and fitted all the heating pipes and hot and cold water pipework for my sisters house back in 2012. I also fitted a Megaflow unvented heating cylinder. Everything has worked really well until last week where she is having issues with her hot water. Her shower works fine and supplies good hot water, however she is not getting any hot water in her kitchen tap, or she has to run the water for at least 2 minutes until she gets some hot water from that tap. Then the water temperature varies and comes and goes.

I went to the property last Friday and could get hot water from the bath hot tap and the washbasin hot tap, also in the bathroom. I was also getting hot water in the downstairs bathroom washbasin tap but could not get any hot water from the kitchen hot tap.

The only taps or valves which have thermostats is the shower, which is working fine.

I have checked the megaflow and that is working fine and the pipework going out of the megaflow feels hot. The megaflow is on the 1st floor and next door to the upstairs bathroom. The kitchen is on the ground floor and the downstairs bathroom is next to the kitchen.
The kitchen tap is almost directly below the megaflow.

I just cannot understand what has caused this problem.

Does anyone have any suggestions on something I might have missed

Many thanks

Paul Cockhill
 
Is the kitchen tap a monobloc mixer?
Presumably the kitchen cold is fed directly from mains?
Is there a NRV on the kitchen hot?

Can you isolate the cold (only) at the kitchen tap, and/or same on the shower mixer?
Hi Basher, thanks for the reply.
Yes it is a monoblock mixer but I turned off the cold supply and just ran the hot through it but is was still just cold coming through
Yes the kitchen cold is coming from the mains
The is no NRV on kitchen hot

I can isolate the cold to kitchen tap but not on the mixer shower
 
Hi Basher, thanks for the reply.
Yes it is a monoblock mixer but I turned off the cold supply and just ran the hot through it but is was still just cold coming through
Yes the kitchen cold is coming from the mains
The is no NRV on kitchen hot

I can isolate the cold to kitchen tap but not on the mixer shower
Thanks Paul
Well that's shot down my theory!

I have a kitchen monobloc which doesn't take h&c separately to the spout, but mixes them directly after the valve/cartridge. I'm ashamed to say there's no NRV on the hot (yet), and if I turn both hot and cold full on, cold goes back up the hot into the cylinder etc. (So next time you don't get hot water for ages!) I had wondered if you had a faulty cartridge there might be something similar going on, but you've tried with the cold supply isolated, so not that ☹️

I also wondered if something similar might be going on at the thermostatic shower.
If that's fed from balanced cold, can you turn off balanced cold somewhere so as not to affect hot, and see if the problem still persists?
 
The fact that the shower is delivering hot water does not rule out the possibility that it is not isolating the hot and cold feeds.

For a simple no-dismantling check: Run the shower so that its DHW feed hot to the touch. Keep your thumb on the shower feed and get someone to run the problematic kitchen tap. If the shower is passing your thumb will get cold rapidly as soon as the kitchen tap is run.

I'd take the opportunity to fit NRVs to the shower.
 
Thanks Paul
Well that's shot down my theory!

I have a kitchen monobloc which doesn't take h&c separately to the spout, but mixes them directly after the valve/cartridge. I'm ashamed to say there's no NRV on the hot (yet), and if I turn both hot and cold full on, cold goes back up the hot into the cylinder etc. (So next time you don't get hot water for ages!) I had wondered if you had a faulty cartridge there might be something similar going on, but you've tried with the cold supply isolated, so not that ☹️

I also wondered if something similar might be going on at the thermostatic shower.
If that's fed from balanced cold, can you turn off balanced cold somewhere so as not to affect hot, and see if the problem still persists?
Hi Basher

There could be something in this. The kitchen tap is the first mains cold water feed after the stopcock. So could the cold be going up through the tap and pushing it way up the hot pipe, so when the hot tap is turned on it just pushes out the cold water? Perhaps if I put a NRV on the hot tap this might sort it??? A long shot but what do you think

Paul
 
The fact that the shower is delivering hot water does not rule out the possibility that it is not isolating the hot and cold feeds.

For a simple no-dismantling check: Run the shower so that its DHW feed hot to the touch. Keep your thumb on the shower feed and get someone to run the problematic kitchen tap. If the shower is passing your thumb will get cold rapidly as soon as the kitchen tap is run.

I'd take the opportunity to fit NRVs to the shower.
Thanks Chuck, will try that

Paul
 

Reply to Hot water issue which has me baffled in the Bathrooms, Showers and Wetrooms area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
126
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
323
Hi bit of a weird issue, I installed a grohe bathroom tap successfully 2 months ago bought from screwfix. Last week the right hand hot tap makes a squeak noise as I turn it on or off, left tap is 100% perfect and noiseless. This grohe tap is like one unit, so no screw notch or way I can remove...
Replies
1
Views
90
Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I have changed the 3 port actuator Honeywell head however this doesn’t seem to have solved the issue, does this mean that the programmer is faulty? Or is...
Replies
8
Views
277
Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
2
Views
117
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock