Hello,


I have a non-combiboiler (Vaillant), non-condensing, non-vented with an integratedexpansion tank, that is used to heat radiators in my house. It ismaybe 10 years old and I am hoping to get a few more years from it.All of my water is heated with electrical point-of-use heaters, whichis expensive. I would like to also use my boiler for hot water byadding a cylinder and zones to my existing system. I have read a biton the forum about the S and Y plans. I have my boiler set to 70C,but in my house the boiler temperature rarely rises above 40C, unlessthe boiler has been off for a long time, and the house is very cold.In order to prevent the growth of bacteria, I would like the cylindertarget temperature to be 55 or 60C. It seems the hot water requires amuch higher boiler operating (return) temperature than the radiators.


From what I have read there are a few possibilities:


S-Plan: When onlythe cylinder calls for heat, all is fine, the boiler can go to 60C+.If only radiators call for heat, everything is also fine. If bothcall for heat, both zones will be open and heat will be taken fromthe cylinder (assuming it is up to temperature) to heat the rads.Maybe this is not a problem? In any case some kind of bypass isrequired since the Vaillant pump runs for quite some time after theflame stops, and both zones will be closed.


Y-Plan: This wouldseem ideal if there were no middle position, in middle position youhave the same issue as with S-Plan, in that heat can be taken fromthe cylinder to the rads. Maybe it is possible to find a valve withno middle position? I also have read on the forum that some kind ofextra valve is required for an unvented cylinder for Y-plan but Idon't really understand why.


Which brings me tomy question. If one makes the assumption that the cylindertemperature will always be hotter than the radiators, why not let thecylinder run wild (always open) and use only one 2-port zone valvefor the radiators. In this configuration no bypass is needed sincethe cylinder loop is always open.


Am I missingsomething?
 
Every boiler must have in interlock, ie it must be able to shut off the boiler with a there instant of sorts.
Your hot water should be set for 60 degrees and your boiler ( if connected and wired properly) should be able to easily reach 70degrees.
An s plan is far better than a y plan.
 
Sorry, I missed one point. I was thinking of putting a relay in place of the end switch for the hot water zone valve. it would behave like the zone valve electrically, but without the hydraulic switch, hot water loop would be always open.
 
I am not sure if one 3 way is more complicated than 2x2-way valves, but it it seem to me that the system can be made with 1x2-way, and no need for the bypass valve.

Am I missing something?
 
No, I am not an installer, but I would like to be able to have an informed discussion with one when the time comes. Are you an installer? and if so, can you answer the question?
 
You can't have a cylinder open circuit really. Could boil over and inefficient. Also not using a standard system and wiring may confuse people who come to work on it.
 
If you only had one valve then you'd be doing exactly what you appear to be trying to avoid ie potentially robbing heat from the cylinder.

The zone valve on the cylinder is to turn that circuit off when up to temperature, preventing any heat being further transferred to or from the cylinder.

No disrespect intended, but I would suggest you stop reading and start phoning, as you sound like you're going to get into a whole load of bother. As the saying goes, a little knowledge is dangerous!
 
I don't really see how an indirect cylinder can boil over, however I do understand the wisdom of having a standard system.
 
No worries, I am here for information.

As I said previously, I would like to understand my options before I start phoning installers.
 
You can get external 3 way valves that link to the boiler and provide hotter water to cylinder then lower temp to rads. I use atags, not sure about your model of vaillant. Your installer should know!
 
Agreed, but I would like to avoid this because it is expensive, and I don't know how long my Vaillant will last. I need to install something now, knowing that I will need to upgrade my boiler to a newer condensing model in 5 years or so.
 
An S plan is a much better solution, it's more logical, simpler and more reliable generally.

Heat is never taken from the cylinder to heat rads, I'm not sure where you have gained that assumption.

The cylinder will require a min flow temp of around 70, return of 60ish to ensure the bottom of the cylinder can reach 55.

The radiator circuit is another matter. If you're saying you can run them at 40 comfortably then great, however when you add a cylinder you'll need to have the boiler temp set to satisfy the cylinder. Short of turning the boiler stay up and down like a yo yo, you could blend the radiator circuit down with a mixing valve if required. If not then just run them at a higher temp. With your current boiler, there's not a huge saving to be made running a lower temp.

Unvented cylinders need to be able to be shut off from the heat source in the event of overheating, a 3 port valve doesn't achieve this, a zone valve does.
 
Last edited:
When both heating and hot water zones are open, I don't see how heat will not move from the cylinder to the rads. I am not sure if this is a problem since eventually the house will heat, the rad zone will close and the boiler can then heat the water. However, I would prefer the priority be the other way round.

I have my boiler set at 70C. It rarely goes over 40C. This will need to change if a cylinder is installed.
 
C-plan looks exactly as I envisioned, with the zone valve on the rads. Is this a common setup?
 
Because the zone valve to the cylinder will only be open when the cylinder is below set point eg 55 degrees. When the flow temp is greater than 55, heat will only be transferred into the cooler medium, ie the water in the tank.
The laws of physics prevent it doing any different.

When the cylinder is satisfied eg > 55 degrees, the zone valve will close, preventing circulation, although this is still preventing it from being heated further as opposed to any heat being removed.

If your boiler stat is 70 yet you can only get a flow temp up to 40, something is wrong.
 
Look up balancing.

My current setup seems reasonably well balanced, no hot or cold spots in the house. All the rads have thermostatically controlled regulators. What do I need to know about balancing that can help me in this?
 
C-plan looks exactly as I envisioned, with the zone valve on the rads. Is this a common setup?

You will be having work carried out that means your new heating system & controls will need to be compliant with Building Regulations AD Part L1b.

The C-plan system will not meet these & it will not be suitable when you have to install a new boiler.
 
We do not understand this statement please explain what you mean?

I set the boiler temp to 70C. Before it gets much over 40C, the main house thermostat stops calling for heat. I guess my house has more radiator capacity than it needs, but I guess low return temps will be good when I eventually have to convert to a condensing boiler.
 
It sounds as if there is possibly a problem with your boiler if it doesn't get up to 70°.

S Plan meets you're needs don't over complicate it . if you go for and Unvented ("mains pressure") hot water cyclinder your installer will also need to be 'G3' certified.

If you want to reduce the flow round the radiators to a lower temperature, then use a weather compensated blending valve.

You'll also need an auto bypass as the boiler with have a pump overrun so it doesn't overheat when both valves are shut.

C Plan only normally used on gravity feed - download the Honeywell wiring guide you'll see the options.
 
My current setup seems reasonably well balanced, no hot or cold spots in the house. All the rads have thermostatically controlled regulators. What do I need to know about balancing that can help me in this?

Your primary and Heating circuits need to be balanced.
 
I set the boiler temp to 70C. Before it gets much over 40C, the main house thermostat stops calling for heat. I guess my house has more radiator capacity than it needs, but I guess low return temps will be good when I eventually have to convert to a condensing boiler.

It's marginally possible, but much more likely to be a sign of an underlying fault on the system.
 
Because the zone valve to the cylinder will only be open when the cylinder is below set point eg 55 degrees. When the flow temp is greater than 55, heat will only be transferred into the cooler medium, ie the water in the tank.
The laws of physics prevent it doing any different.

When the cylinder is satisfied eg > 55 degrees, the zone valve will close, preventing circulation, although this is still preventing it from being heated further as opposed to any heat being removed.

If your boiler stat is 70 yet you can only get a flow temp up to 40, something is wrong.

Heat exchange is a 2-way street. If the cylinder temp drops below 55C, say 54C and wants heat, and the rads are running with a boiler temp of 40C, then heat will be taken from the cylinder.

I do not believe there is something wrong with my boiler setup. I probably just have way more radiator capacity than the house needs.
 
You will be having work carried out that means your new heating system & controls will need to be compliant with Building Regulations AD Part L1b.

The C-plan system will not meet these & it will not be suitable when you have to install a new boiler.

I said I want to simply extend my existing system by adding a cylinder.
 
W plan EVEN :)

What is difference between W-plan and Y-plan? If it W-plan uses a 2-way valve (with no middle position), is it possible to get hardware for that?
 
Your primary and Heating circuits need to be balanced.

I only have a heating circuit. What do you mean by primary circuit.
 
It's marginally possible, but much more likely to be a sign of an underlying fault on the system.

From what I understand, when you set the boiler temperature, this will be the max temp before the flame is turned off. At our place, when the rads reach 40C the house is 21C and the thermostat stops calling for heat.
 
Status
Not open for further replies.

Reply to Different boiler temps required for hot water vs radiators. in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

G
I've just bought a 3-floor house with a gas boiler on the ground floor and hot water tank on the middle floor. When I switch on the hot water at the timer panel, it works but it also heats up all the radiators above ground floor. I have to close them individually to stop this. The rads aren't...
Replies
1
Views
522
Hello all, I've just had a new radiator installed and it comes on with the heating as expected but then also came on when the hot water came on without the heating. Ours is a system boiler worcester greenstar 30cdi with an unvented cylinder. The new radiator has been hung in the w/c on the...
Replies
3
Views
469
Firstly I won't be touching or going anything... I only want advice if this is right.. my partners dad has a aga that is solid fuel unregulated heat source and a oil boiler. The problem the hit water cylinder doesn't have a stat thus why the hot water is roasting hot but there is a pipe stat on...
Replies
3
Views
374
Hi all. I noticed this winter my living room rad only get hot in the top half. Radiator is 1600mm(DP SC) double panel single convector. System was flushed just last year. Both flow and return values are fully open and don't stick. Boiler is serviced each year. Baxi combi boiler about 8 ton9...
Replies
1
Views
432
Hi, I need to drain my vokera 29 boiler in the attic as Im going away for 4 weeks at least to make sure there are no frozen pipes. In my small 3rd floor flat, I have a radiator in the front room and one in the hall (very close to each other), there is a drainage valve on one of these. My back...
Replies
1
Views
289
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock