Thanks @chris watkins and @king of pipes. I appreciate your input, basically I just wanted to absorb your expertise and report back to him. To clarify further the wastes do not run into a stack with an external high level vent, or air admittance valve installed above highest flood point. It is simply many metres of 40mm before going through external wall and down into a gully, the only air admittance if you will is one tee with an upright piece of overflow pipe with a tube from a machine going into it. I’m right in thinking this not a vented system?
 
Yes it is a trap not an open vent.
Open vent pipe suitable terminated on the end of the run (last fitting connected) will stop it self siphoning all the traps connected. Albeit that gully on the end is trapped so no drain smells there will still be a stink from the pipework & if fitted it will not matter if it runs full bore. (might even need another half way)
 
Last edited:
Ok. That overflow did not have a trap on it though, it was simply an open ended pipe which could easily emit drain smells into the room.
So now you can picture the layout a bit better and know that the 40mm pipes do not enter any 100mm stack anywhere (just through wall and into gully) what should I suggest he has done? I’m not interested in this type of work personally so will strongly urge him to get a reputable plumber in who knows what he’s doing but I at least want to give him all the info he needs.
Thanks for your time Chris by the way
 
Thanks Chris. I’ll report back to him. Sorry if my questions sounded stupid, I did do my NVQ 1-2 at college, so know a little, however my Monday to Friday was spent on my knees servicing and repairing oil fired appliances, that’s all we did lol.
Thanks again buddy!
 
Yes that’s what I’ll suggest. My concern is if he does do anything to it, he might just get the same person/firm back who installed it all in the first place, when clearly it’s not up to scratch. Either way I’ll advise him on what you guys have said and leave it with him, it’s on his head then if anything goes wrong.
 

Reply to Commercial waste pipe. in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Sorry if this is stupid question. We have waste water pump in our first floor flat (not sure what it is called)? It failed and wouldn't drain...
Replies
3
Views
99
Hi, We're in the process of upgrading 2 bathrooms in our house: the ensuite and the family bathroom. These adjoin one another. The ensuite is...
Replies
3
Views
81
    • Like
Hello hello,, Hoping there are some experts or experienced Bulgarian plumbing chaps in this site ?. Here in the UK I can fit a bathroom just with...
Replies
2
Views
296
Hi all I really need some help or advise….. Back story….. Some years ago my dad had an extension to his house which included a newly built...
Replies
2
Views
349
Total refit of of bathroom. I've got a 40mm waste from the shower running beneath the floorboards to an external wall and out. Just above where...
Replies
1
Views
2K
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock