Ok then, if I assume that the heating demand is 5.5kw from the fan speed, a deltaT of 8C means the flowrate has to be 0.59m3/hr, Also, it means that the total rads output at max (50 deg) output is 7.9kw, which implies that you only have maybe 4/5 rads in service just now?.
If I assume the heating demand based on a flowrate of 1 m3/hr and the same deltaT of 8c then the output is 9.3kw and implies that the max output of the rads in service (at 50C) is 13.3kw.
A different approach is to monitor your gas meter.
Your gas flowmeter probably measures the flowrate in m3/hr, the older type (here anyway) measure in 1/10ths of a m3 which means a very quick/accurate spot check can be made in a short time, if the meter only turns over every m3 then you would have to monitor it over a hour, a m3 of gas around here is ~ 10.8 kwh so easy to calculate the real boiler output from this assuming a boiler efficiency of ~ 88% (or whatever).
Have a look at your meter and see its scale.
"UPDATE
boiler outlet fell to 54oC with D0 5KW, increased to 7KW fan now 170 outlet climbing slowly now at 59oC.***.think it will settle around 6KW with the fan around 160-170...DT currently changing during heat up"
I think the fan speed is a pretty good indication of your boiler output, from the above, fan speed 1650 rpm so output = 18*1650/5200, 5.7kw.
So, how many rads are currently turned on or in service?.