We have moved last year to an older house which has 25 rads and there is a Grundfos 15/60 pump in CH system. Basically not all radiators get hot when system running, there are two honeywell controllers and if downstairs is off then upstairs gets hot and vice versa, however when full system on then upstairs doesnt get that hot.

I have tried to balance the system from furthest radiator but still not helping so my question is can I replace the 15/60 with a UPS2 25/80?

Are there any complications with doing this ? I know the 25/80 is around 50mm longer but is there anything else?

Thanks for any help in advance.
 
open vent or sealed system?
 
you probably need to flush and clean out your system before swapping pumps, more likely to be clogged up, a bigger pump may just move the muck to another position
 
Can you not zone the radiators and a pump on each zone?
 
Hi
Thanks for the replies, its a sealed system.
If both upstairs and downstairs get hot when the other system is not on/calling could that still be a clogged radiator?
Thanks
 
could be or maybe slightly blocked flow pipe

you could try turning a few rads off down stairs and see if if a few upstarts start to get hot

and it would help / better if you put some cleaner in the system for a week or two
 
Status
Not open for further replies.

Reply to Can I replace a Grundfos 15/60 with a 25/80 - Hlep Please in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
2
Views
174
PSxxxxxx
P
Hi, My current hot water system needs to be replaced. Anyone got any suggestions or can recommend any plumbers around Derrimut area that won't rip me off? An office guy recommended me to apply for government rebates and get it installed through timetosave.com.au. How reliable is this...
Replies
6
Views
301
Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I have changed the 3 port actuator Honeywell head however this doesn’t seem to have solved the issue, does this mean that the programmer is faulty? Or is...
Replies
8
Views
291
Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
2
Views
130
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
138
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock