As per the title?

I've only ever seen domestic system/conventional system boilers with an F&E tank and combi boilers which are closed systems.

Is there any reason a system boiler cant have an expansion vessel fitted and be made a closed system?

Or

Is there any reason you couldn't install a combi with an open vent/F&E?
 
The following applies to the UK and its regulations:
1. You can have sealed systems with combi (always sealed), system boilers or open vent boilers provided the manufacturer allows this - these days they nearly all do.
2. You can't really run a combi boiler off an F&E tank, as the pressure is unlikely to be sufficient to pressurise the system. Also, you'd lose the benefit of mains pressure hot and cold.
 
You would need to consult the manufacturers installation manual for that particular boiler.
I have seen all manner of configurations over the years but the manufacturer is the place to start if you're thinking of altering or installing something.
 
The following applies to the UK and its regulations:
1. You can have sealed systems with combi (always sealed), system boilers or open vent boilers provided the manufacturer allows this - these days they nearly all do.
2. You can't really run a combi boiler off an F&E tank, as the pressure is unlikely to be sufficient to pressurise the system. Also, you'd lose the benefit of mains pressure hot and cold.

Hadn't thought of the system pressure, that makes sense with a combi.
[automerge]1597826034[/automerge]
You would need to consult the manufacturers installation manual for that particular boiler.
I have seen all manner of configurations over the years but the manufacturer is the place to start if you're thinking of altering or installing something.

It was more out of curiosity as a newbie, @stedysons comment on pressure makes sense with the combi.
 
As per the others a consultation with the manufacturer would be a worth while chat. This is an extract from the Intergas (Netherlands based) eco rf30 manual which gives different configurations:
 

Attachments

  • D53A57C6-08D9-4FF0-946B-079B845C1A20.jpeg
    D53A57C6-08D9-4FF0-946B-079B845C1A20.jpeg
    26.4 KB · Views: 11
The following applies to the UK and its regulations:
1. You can have sealed systems with combi (always sealed), system boilers or open vent boilers provided the manufacturer allows this - these days they nearly all do.
2. You can't really run a combi boiler off an F&E tank, as the pressure is unlikely to be sufficient to pressurise the system. Also, you'd lose the benefit of mains pressure hot and cold.

Why does a combi boiler require pressure to operate yet a system boiler doesn't?

Is this a protection mechanism or is it designed to increase the boiling point of the heating medium?
 
Why does a combi boiler require pressure to operate yet a system boiler doesn't?

System boilers do require pressure to operate, it’s heat only/open vent boilers that do not. A sealed system only gets rid of the feed and expansion cistern in the loft. It can be fed onto a gravity hot water system or an unvented cylinder.
 

Reply to Can a conventional system boiler be a closed system? in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up...
Replies
2
Views
266
PSxxxxxx
P
I have an ideal vogue max S18 boiler and I’m considering fitting auto balancing TRVs, my question relates to the boilers pump. I see a boiler...
Replies
1
Views
178
Recently had a Viessmann Vitodens combi boiler installed, quite often when the adjacent cold mixer tap is opened the boiler starts for a few...
Replies
3
Views
228
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold...
Replies
2
Views
198
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is...
Replies
5
Views
538
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock