If fitting a combi boiler into a airing cuboard in the centre of the house ,how would you get the safety discharge valve to the outside wall is there a maximum length.
Could you run 15mm copper into the loft and then out onto the gable end?
 
no you cant go up with the discharge ,it must fall from the boiler . cant you run it under the floor to an external wall. if not some manufacturers do a remote discharge kit which can be piped into the return to the boiler .seen so many going up though .

regards ant
 
Cheers for that i was just after some advice so when im gas safe im going to install a new boiler in my own house and was just weighing everything up
 
Is it right you can run it into the condesate pipe with a tundish?
Im sure ive seen it discussed on here.
 