ok, so I went to a job last week, custard had just bought the house, unluckily for them it had an Alpha CB28 in it. She said it kept cutting out (heating, dhw was fine)so she would have to reset and then it would work again.


I told her to try it on DHW only mode until I could get there late last week. She reported it had been working fine for DHW only.

I tried it on heating, ran it up for a while till the system got hot and bingo, it cutout. Downstairs rads were blazing but upstairs cold. CHecked them, some moron had closed a lot of them off, so I was wondering if the boiler had reached its set temp and cutout. Adjusted all the rads, hunky dory, nice warm house. Left it running half an hour, all good.

I had taken a new CH overheat stat but they had supplied a thermistor when I opened the bag. I couldn't test resistance on current one as Alpha gives no resistance readings in their crappy manual. I checked the pump which I had expected to be the culprit. It was nice and free, spinning like a dream, so I thought it was cured...

Nope, just had a call saying it has cutout on her twice this weekend and I am scratching my head a bit... Thinking it could be the pump overheating, but if I cant get it to repeat it could be one of those nightmare jobs...

Anyone got much Alpha experience? I hardly ever get them, only know that they are sh*t!!
is it worth getting a new overheat stat before I go?:ack2:

thanks in advance
 
I did think about the primary temp sensor for heating flow as well, but again, got no readings as to what it should be and I don't like throwing parts at boilers ever. That's for British Gas!!
 
Blocked bypass maybe?

Was the heating water ok?

Try reducing the heating temperature to see if it makes any odds?
 
Last edited:
Blocked bypass maybe?

Was the heating water ok?

Try reducing the heating temperature to see if it makes any odds?

Internal bypass?

I turned it down when I left, seems to have still done it when Id gone...aaaggh
 
Sorry mate, missed the 'heating water' bit?

yes it got up to temp nicely, all was working as it should be and all rads were toasty for at least 30 minutes, until I had gone anyway !!
 
Internal bypass?

I turned it down when I left, seems to have still done it when Id gone...aaaggh

Yeah, just a thought if the system has a room stat. Did you follow the fault finding in the manual? Was it definitely locking out due to over heat?

Water clean or mucky?
 
Cheers!
No stat that I could find and custard wasnt aware of one. There is an old programmer under the boiler and then the boiler heat control for temp control. I suppose I could link out the programmer just to eliminate it, but it has to be worse than that!!

Fault finding in the manual seemed pretty useless. Didn't really give me any info that helped or that I didn't know(like resistance readings for overheat stat etc)

Water was dirty when I checked the pump, seen worse though! thanks
 
Last edited:
Yes, Neon 'A' is flashing the lady has kindly informed me! On checking the manual that means overheat stat has operated. Would be nice if it was just the OH stat, but....
 
Another thought I have had is if the PCB is goosed. There seems to be a few cases where OHS has indicated a similiar fault where engineers have ended up replacing the PCB. I will try a new Overheat Stat, then if the pump still seems ok I will have to look at PCB :(
 
Status
Not open for further replies.

Reply to Alpha CB 28 headscratcher... any advice chaps? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

    • Like
Hello, my Mothers heating failed in the recent UK cold snap. I found the pump was stuck. I have a question about pump orientation. The...
Replies
8
Views
675
Hello, We had an extension built seven years ago. Initially the builders' plumber connected the heating to the house system but this didn't work...
Replies
23
Views
832
Hi Everyone, For those who like a long read but I could rally do with some advice. Might be a bit long this. For background. A...
Replies
3
Views
287
I have a Vaillant eco plus 837, year installed 2008. It works well. We have one large zone for the house with 13 rads running off it. We also...
Replies
1
Views
337
Hello all, I have a WorcesterBosch Greenstar 42CDi classic combi, which is providing DHW fine, but not heating. Was working fine in spring...
Replies
11
Views
1K
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock