Here's some info on DFE ventilation from BS 5871-3:2005
Specification for the installation and maintenance of gas fires, convector heaters,
fire/back boilers and decorative fuel effect gas appliances —
Part 3: Decorative fuel effect gas appliances of heat input not exceeding 20 kW (2nd and 3rd family gases)
8 Ventilation
8.1 General
The appliance shall have a supply of air for combustion and the safe operation of the flue.
COMMENTARY AND RECOMMENDATIONS ON 8.1
Subclauses 8.2, 8.3, 8.4 and 8.5 specify the ventilation requirements for appliances. It should be noted that
whilst BS 5440-2 excludes decorative fuel effect gas appliances from its scope, the references given in 8.3
and 8.5 to BS 5440-2:2000 are applicable in the context in which they are specified.
8.2 Sizing
Unless the manufacturer’s instructions specifically state that purpose provided ventilation is not required,
such ventilation shall be provided in the room or internal space containing the appliance. Where purpose
provided ventilation is required, the air vent free area shall be a minimum of 100 cm2, or, where greater,
as stated in the manufacturer’s instructions.
COMMENTARY AND RECOMMENDATIONS ON 8.2
Normally, appliances covered by this standard will require a minimum of 100 cm2 of purpose provided
ventilation. However, in the case of an appliance of not greater than 7 kW input which generates a clearance
flue flow not greater than 70 m3/h when tested in accordance with Annex A, an air vent may not be necessary.
The manufacturer’s instructions will provide details in such circumstances. It should be noted that Annex
A describes a laboratory test which is not for use by gas installers seeking conformity with this standard.
Hope it helps.