Wondering if you could offer some advice, we have just bought our first house and we are having a nightmare with the CH. I will be having the full system replaced in the next 12 months (when we have the £'s), but for now, I am hoping to keep the old system going. We have a Worcester Greenstar Ri which has worked fine for the past week then the other day the CP53 circulating pump started making a whirring noise and ( I am assuming this is linked) the heating stopped working. The boiler fires upon demand and the green flame-shaped light comes on, then after a couple of minutes it turns off again, the thermostat is on full and the timer on constant. I am a bricklayer by trade so know very little about the magic of CH, but we are a bit hard up at the moment so hoping its something I can sort out for now. I have attached a photo of the pump and boiler. I am wondering if this could be a case of replacing the pump? If so, which pump would you recommend? Any advice would be appreciated.

Thanks

thumbnail_20180908_163146.jpg


thumbnail_20180908_170310.jpg
 
Sounds like your pump is goosed and will need replacing. Touch the pipe from the boiler to the pump is it warming up ? And the one after the pump to the port valve is that also warming up ?

As far as you know has the system been drained down could be air in the system too.
 
Hi AMGas Services, thanks for the reply. The pipe connected to both the top of the pump and the bottom are red hot. Dont know if it has been drained down recently, it was working a few days ago. Seen online that to let any air out you undo the black bolt shaped plastic cap and let some water out? Is this correct? Would replacing the pump be a straight swap out? Thanks
 
Yep I am with amg on this ,but before you try a new pump , carefully hold it , can you feel any slight vibration, if not just see if its getting power ( you may need a friendly sparkie) before you try a new one .
 
If you are lucky both valves should turn off , you wont be able to buy the exact pump , the nobs in Brussels decided to change our heating pumps back in 2015 . A good swap would be the standard grunfoss , screwfix sell them .
 
Would something such as this do the job? https://www.NoLinkingToThis/p/grundfos-ups2-15-50-60-central-heating-pump/42635
Looks like the isolator valves above and below turn so fingers crossed they are ok!
 
might give this a go,
151711 Central Heating Boiler Hot Water Circulation Circulating Pump
only needs to last 12 months or so and its only £29 on Amazon. Will just get the buckets at the ready! Thanks for the help.
 
Would something such as this do the job? https://www.NoLinkingToThis/p/grundfos-ups2-15-50-60-central-heating-pump/42635
Looks like the isolator valves above and below turn so fingers crossed they are ok!

yep that one will work
 
might give this a go,
151711 Central Heating Boiler Hot Water Circulation Circulating Pump
only needs to last 12 months or so and its only £29 on Amazon. Will just get the buckets at the ready! Thanks for the help.

i wouldnt tbh
 
If you are going to change the pump make sure it’s aligned ie flow direction. Otherwise it won’t work.

The easiest way is to make sure the arrows match up ie if the arrow is facing up after changing the pump the new pump arrow must also face up.
 
Hi Guys,

Wondering if you could offer some advice, we have just bought our first house and we are having a nightmare with the CH. I will be having the full system replaced in the next 12 months (when we have the £'s), but for now, I am hoping to keep the old system going. We have a Worcester Greenstar Ri which has worked fine for the past week then the other day the CP53 circulating pump started making a whirring noise and ( I am assuming this is linked) the heating stopped working. The boiler fires upon demand and the green flame-shaped light comes on, then after a couple of minutes it turns off again, the thermostat is on full and the timer on constant. I am a bricklayer by trade so know very little about the magic of CH, but we are a bit hard up at the moment so hoping its something I can sort out for now. I have attached a photo of the pump and boiler. I am wondering if this could be a case of replacing the pump? If so, which pump would you recommend? Any advice would be appreciated.

Thanks

View attachment 34408

View attachment 34409
Hi if you only moved into house could be pump is stuck get yourself a big screw driver loosen nut on pump turn on heating there is a nut with a screw driver turn this gently this will free it up and heating should fire the boiler you have is one of the best on the market failing all of the above get yourself a volt ohms meter disconnect live and netural set meter to ohms touch the probes to L and N if you get 100 ohms pump is ok anything less than this its on its way out if you have to replace pump nock of valves to pump get 4mm hex key take pump head off and replace with same reason I say replace with same is some times these new energy saver pumps do not get full power weather it be from time clock or else were you might have to replace the programmer hope this helps good luck stick with the heating system you have do not go for a system boiler if its not broke do not fix bye
 
Lock open your 2 ports in the manual position and see what happens. If one or both are not responding and are closed the pump will make a noise and the boiler will go off after a min or two. So check power to pump and if it is spinning if power there but not spinning or weak impellar. Change pump. If no power then check 2 ports are opening and activating the microswitch. If micro switch is activated but no power out then change microswitch. If switch not operated check power to motor if power present then change motor. If no power to motor check room thermostat continuity or power in and out. Power in but not out change stat. No power in then check programmer.
 
You can check pump is spinning by undoing the plastic nut and pulling it out slightly it should spin freely then turn on heating and see if it spins if not then it is probably that, if one or both valves are open, then just push nut back in and tighten again
 
Hi Guys,

Thanks again for the last post, got the old boiler going again!

Wondering of you could offer some further advice.
The boiler is now working with the new pump (kind of), we have hot water and the boiler fires when there is a requirement for HW. However, not when there is a call for CH. But when the boiler fires for the HW the radiators get warmed up for a short period. Im wondering if it could be down to a faulty motorised valve as pictured previously. The valve for the HW is working fine but the CH automatic valve is not, I think the internal motor is shot as the lever on the side doesn't not move when under demand. Would this stop the boiler from firing up under a demand the CH?
The CH valve is open (i think) as we are getting some heating when the HW is on. At the moment, the CH valve motor has been taken off and the valve left in what we think open.

Could this all be down to the automatic valve or is it something else, thermostat maybe?

The thermostat is on full and demand for heating set to constant on the programmer.

Any help would be much appreciated as I'm left scratching my head here.

Many thanks

Lewis
 
Lock open your 2 ports in the manual position and see what happens. If one or both are not responding and are closed the pump will make a noise and the boiler will go off after a min or two. So check power to pump and if it is spinning if power there but not spinning or weak impellar. Change pump. If no power then check 2 ports are opening and activating the microswitch. If micro switch is activated but no power out then change microswitch. If switch not operated check power to motor if power present then change motor. If no power to motor check room thermostat continuity or power in and out. Power in but not out change stat. No power in then check programmer.
Just seen this. Sorry mate
 
Hi Harvest Fields.

Apologies if not written correctly. Just trying to explain the situation the best I can.

Do you think if I was to replace both the automated valve on the CH side of things and also replace the thermostat, it may resolve the issue?

Many thanks

Lewis

Thinking of purchasing a new valve such as the attached as it looks like for like.

Screenshot_20181030-100937_Chrome.jpg
 

Reply to Worcester Bosch Greenstar - No CH in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two...
Replies
2
Views
213
Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer...
Replies
4
Views
282
I have an ideal vogue max S18 boiler and I’m considering fitting auto balancing TRVs, my question relates to the boilers pump. I see a boiler...
Replies
1
Views
187
Hi all. Hope you have all been keeping well. A while back I decided I only wanted to fit one brand of boiler and decided on Viessmann due to...
Replies
9
Views
307
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is...
Replies
5
Views
543
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock