Hi all,

This is my first commercial quote for fitting a couple of 65KW Worcester GB162s. I went to have a look at the job today and it seems quite a straightforward one to be honest. There are 2x Keston 55KW boilers in there at the moment, side by side in a plant room. Both fed from a 42mm gas pipe teeing off down to 22mm for each boiler.

Existing boilers have condensate connections through walls and they will be flued straight through the external wall on 80/125 horizontal flues.

No isolation valves on the primary pipework into the low loss header so we were going to freeze the pipework and fit them to avoid any draining down of both heating circuits and the hot water circuit to the cylinder.

It's a competitive quote against 2 other companies locally. They want us to supply and fit the boilers and the pump group set for each one.

Cost price to me for the boilers and pump sets is £3,300 each. With sundry materials and a 10% markup on the lot I get to £3,914 materials per boiler. I've put down for £750 + VAT for installing each boiler so total per boiler is £4,814 for a total of £9,628 inc. VAT.

Does that sound fair/too low/too high? Really want to get this job as it would be a decent commercial job to start our portfolio off and make it worthwhile doing the commercial gas course too (would pay for it).

Thanks for all advice,

Keiran.
 
I am not gsr just yet but to be honest, it does sound alright. I believe some other engineers would charge a lot more for the labour due to the fact it's commercial. But if you would like to start your portfolio I think it's more then fair.
 
I would have thought the other companies would be dearer than that
It's always difficult to price it right. But I would not go too low in as you still want to earn. I always think quality has a price. I think labour money seems very reasonable and regarding the materials that's what it is on the market.
 
is there any commercials oon the forum who could give accurateadvice without guess work?
 
No desperate rush to be honest. I said I'd submit the quote before the end of the week. Took lots of photos of the plant room today but it all made sense to me and from what I could see the install should be a quite straight forward one.
IMG_0277.JPG
IMG_0278.JPG
IMG_0279.JPG
IMG_0280.JPG
 
Hi all,

This is my first commercial quote for fitting a couple of 65KW Worcester GB162s. I went to have a look at the job today and it seems quite a straightforward one to be honest. There are 2x Keston 55KW boilers in there at the moment, side by side in a plant room. Both fed from a 42mm gas pipe teeing off down to 22mm for each boiler.

Existing boilers have condensate connections through walls and they will be flued straight through the external wall on 80/125 horizontal flues.

No isolation valves on the primary pipework into the low loss header so we were going to freeze the pipework and fit them to avoid any draining down of both heating circuits and the hot water circuit to the cylinder.

It's a competitive quote against 2 other companies locally. They want us to supply and fit the boilers and the pump group set for each one.

Cost price to me for the boilers and pump sets is £3,300 each. With sundry materials and a 10% markup on the lot I get to £3,914 materials per boiler. I've put down for £750 + VAT for installing each boiler so total per boiler is £4,814 for a total of £9,628 inc. VAT.

Does that sound fair/too low/too high? Really want to get this job as it would be a decent commercial job to start our portfolio off and make it worthwhile doing the commercial gas course too (would pay for it).

Thanks for all advice,

Keiran.

In my opinion. It sounds cheap. Have you checked the output of those heating circuits?

Obviously I'm only looking at the photos ( not seen job in real life), but the boilers sound too big for that pipework I can see on the header.
I think the boilers you're talking of will be 1 1/4 inch at least but I'm also questioning the heating circuit size.
What size are they ( look like 28 on photo?)
If it were me pricing that, I'd want more info on sizes before I did the job !
Price wise, I'd expect people to be higher to be honest !
Just my opinion.
 
Hi and thanks a lot for your feedback, your probably exactly the sort of person I wish I had there on the day to be honest!

The existing boilers have 42mm flow and returns which is actually the same as the new boilers. Existing ones are 55KW Kestons and new would be 65KW WBs.

Secondary circuits (2x heating) are in 42mm as well with mixing valve to control circuit temperature. There is also a HW Circuit to a 300L twin coil cylinder with solar also attached.

It is a very large 3 floor office and drug rehabilitation building in the centre of Lincoln and from a quick look round the heat output doesn't seem to be too far off though.

What would you quote for labour to replace them or of curiosity?

Don't want to sell myself short price wise but equally whilst I'd be happy taking this one on I am sure I will learn a fair bit from it and don't feel i can charge for my time learning!

Thanks,

Keiran.
 
Croft
That llh looks like it's leaking or has at some point. Have you considered it might need new gaskets?
What are the walls like? How long to core two new flues?
I personally always add 20% mark up and I think you'll fine most bigger companies will be getting there material cheaper.
I don't think your to far off on the price
 
I do work for two commercial companies one massive one and to be honest neither like big labour charges max £250 a day.
Commercial guys are coming more common place now.

All the stuff I price has massive material charges tho .I upgraded some pumps other week and overcharged them by a grand on materials.
Oddly they seem to accept that.
 
Hi and thanks a lot for your feedback, your probably exactly the sort of person I wish I had there on the day to be honest!

The existing boilers have 42mm flow and returns which is actually the same as the new boilers. Existing ones are 55KW Kestons and new would be 65KW WBs.

Secondary circuits (2x heating) are in 42mm as well with mixing valve to control circuit temperature. There is also a HW Circuit to a 300L twin coil cylinder with solar also attached.

It is a very large 3 floor office and drug rehabilitation building in the centre of Lincoln and from a quick look round the heat output doesn't seem to be too far off though.

What would you quote for labour to replace them or of curiosity?

Don't want to sell myself short price wise but equally whilst I'd be happy taking this one on I am sure I will learn a fair bit from it and don't feel i can charge for my time learning!

Thanks,

Keiran.


Hello.
I'd put 33% mark up on all materials so you're getting at least 25% gross profit on those.
Labour wise, I would want around £1500 Plus VAT. (Going off pictures and info you've given)
I haven't seen it in real life as you know. If I used your material price (net) I would be working it out at around £10500 plus VAT for that job I reckon. Don't hold me to it.

There can be things you didn't see or think of if you are not used to commercial so beware of those. It looks a simple enough job though so it should be fairly straightforward.

Have you allowed for shunts ? or are those the pumps you mentioned? I don't use Worcester Bosch so I don't know if they come with shunt pumps built in.

Is that existing header large enough for the two new boilers?

Have you thought of controls?

Have you allowed for a non return valve on each Boiler?

Just thinking out loud.
 
  • Winner
Reactions: Dan
Thanks a lot for the ideas to think about. I've allowed £200+Vat per boiler for contingencies such as valves etc I need. Hopefully that will be enough! The pump sets that go under the WB boilers have most of the bits you mention in them though.
 
Remember commercial size fittings are going to be expensive and that £200 can disappear very fast. Have you counted what fittings are required, not try to patronise but don't want you out of pocket either
 
Atouchofgas is right there. Some prices of materials can be stupid. I would do what you've done and add on just in case you go over on time and materials and I always estimate, don't quote unless you've worded it accurate.

Same as above, not being patronising at all, I hope you do well out of it, I just know from experience how wrong it can go financially.

It will be good to get your teeth into though. Enjoy!
 
Hello.
I'd put 33% mark up on all materials so you're getting at least 25% gross profit on those.
Labour wise, I would want around £1500 Plus VAT. (Going off pictures and info you've given)
I haven't seen it in real life as you know. If I used your material price (net) I would be working it out at around £10500 plus VAT for that job I reckon. Don't hold me to it.

There can be things you didn't see or think of if you are not used to commercial so beware of those. It looks a simple enough job though so it should be fairly straightforward.

Have you allowed for shunts ? or are those the pumps you mentioned? I don't use Worcester Bosch so I don't know if they come with shunt pumps built in.

Is that existing header large enough for the two new boilers?

Have you thought of controls?

Have you allowed for a non return valve on each Boiler?

Just thinking out loud.


Sorry last,
I just wanted to ask you what you mean by 30% mark up? Does it mean 30% on top of the original quote ?
 
Remember commercial size fittings are going to be expensive and that £200 can disappear very fast. Have you counted what fittings are required, not try to patronise but don't want you out of pocket either

Yes thanks, no offence accepted. I've counted the fittings and isolation valves I will need for the 42mm flow and return pipework to connect onto the boiler. Was quite surprised at the cost, i.e. £20 ish + VAT per full bore lever valve and of course the cost of 42mm copper pipe too!

I have used the catch-all on my estimate that the price assumes that all existing fittings and controls are suitable for the job, if not additional charges will apply.

They sounded keen when I submitted it today, will keep you updated!
 
Yes thanks, no offence accepted. I've counted the fittings and isolation valves I will need for the 42mm flow and return pipework to connect onto the boiler. Was quite surprised at the cost, i.e. £20 ish + VAT per full bore lever valve and of course the cost of 42mm copper pipe too!

I have used the catch-all on my estimate that the price assumes that all existing fittings and controls are suitable for the job, if not additional charges will apply.

They sounded keen when I submitted it today, will keep you updated!

Yes, good luck, I hope you get it!
 
hi croft sorry about getting here late
few questions

wheres the pumps for the circuits (not the shunt pumps) ?

i wouldn't freeze it, as its going to be a pita with a llh (always moving)

close the two red gate valves, they should work good yorkshire valves, cylinder in the same room? by the looks it is maybe

pop the heads off the actuators (marking which one is which) and turn them to bypass (return)turn the pump valves off

open the bottom lever valve on the llh (drain) should be drain but might be expansion vessel, also at this time replace llh top and bottom flange gaskets

you should be fine now and fit lever valve straight onto the llh flow and lockshield gate valves on llh return

and if boilers were combined eg one flow and return would need to be increase but as there separated 42mm is fine

would use pressfit tbh

price for boilers and shunt pumps seem high where did you get the price from bss??

also would think about 1k to install would be fine
 
Will you need an etra flue bend on each to get 600mm apart?
 
Will you need an etra flue bend on each to get 600mm apart?

30cm if there both inline eg same height or 1.5m if above
 
I have always had to fit commercial boilers with 600mm between flues for the clean air act. Vaillant insist on it when they comission
 
I have always had to fit commercial boilers with 600mm between flues for the clean air act. Vaillant insist on it when they comission

isnt that for anything over 70kw, im 80% the instructions say 300mm
 
3.6 Clean Air Act
The act applies to gas fired appliance installations exceeding 366.4 kW total gross heat input. It specifies requirements for chimney heights for open flued, mechanical flued and room sealed appliance installations.

so dont need to worrie about it
 
Thanks Shaun,

Circuit pumps are all on the right hand side of that wall, should be on the photos.

I got the price for the boilers online but looks like I can get them a lot cheaper.

Waiting to hear back on Monday I think!

Cylinder is in the same room yes, basically a domestic hot water circuit in 22mm off the LLH.

Curious why you would use press fit? Just to avoid setting off fire alarms and needing hot work permit??

Keiran.

hi croft sorry about getting here late
few questions

wheres the pumps for the circuits (not the shunt pumps) ?

i wouldn't freeze it, as its going to be a pita with a llh (always moving)

close the two red gate valves, they should work good yorkshire valves, cylinder in the same room? by the looks it is maybe

pop the heads off the actuators (marking which one is which) and turn them to bypass (return)turn the pump valves off

open the bottom lever valve on the llh (drain) should be drain but might be expansion vessel, also at this time replace llh top and bottom flange gaskets

you should be fine now and fit lever valve straight onto the llh flow and lockshield gate valves on llh return

and if boilers were combined eg one flow and return would need to be increase but as there separated 42mm is fine

would use pressfit tbh

price for boilers and shunt pumps seem high where did you get the price from bss??

also would think about 1k to install would be fine
 
cant see any pumps in the pic other than the one for they cylinder

if you mean the pumps are the black boxes no there control valves / actuators

and thats good

yes as you will need to stay an hour after you finish and fill in the hot works permit

and tbh its faster and less hassle doesnt matter if theres water in
 
Sorry mate just checked the pictures again. 2x heating pumps can't be seen on the pics but they are at high level just out of sight above the boilers. Definitely in the room, remember seeing them!
 
Sorry mate just checked the pictures again. 2x heating pumps can't be seen on the pics but they are at high level just out of sight above the boilers. Definitely in the room, remember seeing them!

thats fine :) you would surprised how many i see just going off the boiler shunts

hope you get it as looks like an easy change

you have done your commercial already tho?
 
Nah I have it all lined up if I get the job though! Just have to make sure I pass it all!

Didn't want to shell out for it until I got my first decent commercial job tbh.

TBH didn't even know it was a commercial quote when they asked me as initially they wanted 1x65Kw boiler so sounded like could be done on domestic ticket. Totally forgot to mention the one sitting next to it.

Does the system work properly with no pumps on the heating circuits and just shunt pumps then?
 
be careful last time i went for my re up it took 3 months for the quals and new card to be issued from gas safe

and they normally do best response i got is

o that one is for back up only so doesnt run, so we dont class it as working
 
Status
Not open for further replies.

Reply to Can I Run This Commercial Quote Past You Guys?? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi there, thanks for your time to look at this record long post!! I work on the operational management side or a small building contracting firm...
Replies
9
Views
1K
H
Hi there, thanks for your time to look at this record long post!! I work on the operational management side or a small building contracting firm...
Replies
0
Views
657
HRP123
H
    • Useful
I have been quoted for works to install a new heating system in a project we are doing in Kent (one large house and adjoining small house). This...
Replies
25
Views
4K
Hi All, I am so glad I found this forum whilst looking for advice on the net. I am not a plumber as such but I do know a thing or two about DIY...
Replies
25
Views
6K
  • Locked
Hi, what is the best method to obtaining a quote for a full install? eg. I would like to get central heating put into my 1 bedroom flat...
Replies
11
Views
1K
Dotty
D
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock