Hello all

I wonder if anyone has any idea what might be ailing my boiler? This requires quite an explanation for afirst post, so congrats to anyone who gets to the end!

So, I have a Worcester Bosch 30 Si Compact boiler, installed just lessthan a year ago by a reputable Gas-Safe registered plumber. Though notrelevant to my current issue, I will mention that within a couple of months thepump went, and it was replaced by a Worcester engineer under their standard warranty(8 year). This was worrying, but I guess components can fail so I try toremain positive about the Worcester brand, having done a fair bit of researchbefore I had the boiler replaced last year.

At the end of last year with the weather turning cold, I felt that thatthe boiler was not heating the house (2 bed bungalow) well enough. Theboiler was functioning, the rads were warm, (I’d bled them before autumn setin), and hot water fine. However, the house didn’t warm up sufficiently,especially on cold winter days. My initial thought then was that my insulationwas insufficient, allowing heat to escape easily, so after Christmas I laiddown another 200mm layer of insulation in the loft but the problempersists. For example, if on a Sat morn the room stat is reading 15 or 16degrees, having been off overnight, even with the heating on full all day theroom did not reach 20 degrees by evening? I can turn the heating onfor 24 hours, set the room stat high (25 degrees), and it will never reach thattemp. Now am I right in thinking something is amiss?


Having looked through the boiler handbook, I see that I can set thetemperature for the heating and also for hot water, so I set the temp of waterfor the heating loop to be 70 degrees. (And let me re-state that the radsare providing heat.) But when I look at the boiler control panel itself,even when my (rf) room stat is on high, and the program set to ON, the boilerdoes not remain on continuing producing hot water for the radiators. After a while, with water temp showing low 70’s,the burner switches off (the flame symbol disappears), and then Iimmediately see the temp of water in heat loop drop, as low as mid-50’s, andjust stays like that a couple of minutes, before the boiler starts up again, theflame symbol appears, and the water tempcreeps back up again. This is cyclical,and I have only measured a few cycles, but this process is being repeated every5 mins or so. And all the time, the roomstat is set to a high temp which has not been reached, so should be demandingheat.

So, my question is, is that normal behaviour, because I think that it isthe reason I seem to be unable to heat up my house sufficiently. I don’t know if there is an ‘average time’ toraise the house temp by one degree C, and I’m sure this varies depending onhouse size, but I have had boiler on for 12+ hours and not failed to achieved atemp increase of 5 degrees. That justdoesn’t seem right to me.

Apologies for the long explanation, but hopefully it conveys all theinfo reqd for one of more of the experts here to provide an opinion, which Ilook forward to reading.

Thanks and regards
Damian

 
Did you have new rads when the boiler was installed ? If not was the system flushed and a mag filter installed ?

Also no not normal
 
Did you have new rads when the boiler was installed ? If not was the system flushed and a mag filter installed ?

Also no not normal
 
Have you got a one pipe system ?

It sounds like it but obviously I haven't seen it.

If it is, and it's a slow one then the water can move around the circuit and back to the boiler before the rads get chance to warm ( because they work by gravity ).

I may of course be wrong, i'm just thinking out loud !

do you find that the rads warm in sequence or all at the same time and evenly ?
 
Thanks for the prompt replies.

In answer to ShaunCorbs, no the rads were already in place, but there was a power flush as part of new boiler install, and there is a mag filter in place. All the pipework is microbore, if that is relevant.

In response to Last Plumber, I did not know what a one pipe system was until 10 mins ago (good on Google!), and now I would say I have a two pipe system. There are two separate microbore pipes for each rad, and I believe that all rads get warm at the same time. I certainly haven't noticed some being hotter than others. 6 rads in total.

The reason I think that something is wrong is that even with my previous old boiler, I didn't experience this problem before. But of course I am not a heating engineer, so I have no real idea what the problem may be, if in fact it is one.

I do have a Worcester engineer coming out at the end of the week, after a 2+ week wait, but I just wanted to see if there were any opinions I could share with him if he turns round and says all is well.

Thanks again.
 
30 kw for 5 rads is alot do you have a combi ? post a picture of the boiler and pipework please may help diagnose your problem cheers k.
 
For anyone interested, the chap from Worcester popped round yest to check the boiler, and his prognosis is that there is nothing wrong with the boiler itself, my problem is one of poor circulation via the microbore. The boiler was off for a couple of hours before his arrival, so everything was cold. Within a few (5 tops) mins of switching it on, the heating loop temp had reached target temp of 70, both the flow and return pipes at the boiler were piping hot, but the rads still lukewarm. He got into the loft to have a look at the bypass setup, and said that probably due to blockages / restrictions in the pipework, the water was finding it easier to use the bypass to go directly from the flow to the return pipe. He suggested a re-flush may help, (it was power flushed as part of installation 11 months ago), or failing that change pipework as microbore is sh*t ! (He also said that a proper 'power flush' is not possible with microbore, and sometimes does more harm than good.)

Anyway, just thought I'd update you on status. The microbore/rads have been in place for 15 years, so perhaps they are past their shelf life? I don't know if there is a time beyond which microbore gets too clogged up. If so then no fault of original installer I guess, though hopefully he will be returning soon to see if he can address the issue.
 
For anyone interested, the chap from Worcester popped round yest to check the boiler, and his prognosis is that there is nothing wrong with the boiler itself, my problem is one of poor circulation via the microbore. The boiler was off for a couple of hours before his arrival, so everything was cold. Within a few (5 tops) mins of switching it on, the heating loop temp had reached target temp of 70, both the flow and return pipes at the boiler were piping hot, but the rads still lukewarm. He got into the loft to have a look at the bypass setup, and said that probably due to blockages / restrictions in the pipework, the water was finding it easier to use the bypass to go directly from the flow to the return pipe. He suggested a re-flush may help, (it was power flushed as part of installation 11 months ago), or failing that change pipework as microbore is sh*t ! (He also said that a proper 'power flush' is not possible with microbore, and sometimes does more harm than good.)

Anyway, just thought I'd update you on status. The microbore/rads have been in place for 15 years, so perhaps they are past their shelf life? I don't know if there is a time beyond which microbore gets too clogged up. If so then no fault of original installer I guess, though hopefully he will be returning soon to see if he can address the issue.
 
Thanks for coming back.

All to often people start threads and once they have their answer, swan off into the sunset leaving us wondering !
 
Thanks for coming back.

All to often people start threads and once they have their answer, swan off into the sunset leaving us wondering !
 
If I was you I would get a price for a repipe and change from 10mm to 15mm drops if you can
 
30kw output for a 5 rad system say 2kw each max making 10 kw your way over bud , I can only think you must have a combi I would get your engineer back put some sentinel x 400 in the system and let it run for a week then drain down and flush out, take the rads off and flush em through outside replace the rads and if the rad valves were not changed a year ago change em sentinel x 100 inhibitor infill up got to be worth a go before re piping a picture would help boiler and bypass set up regards k
 
30kw output for a 5 rad system say 2kw each max making 10 kw your way over bud , I can only think you must have a combi I would get your engineer back put some sentinel x 400 in the system and let it run for a week then drain down and flush out, take the rads off and flush em through outside replace the rads and if the rad valves were not changed a year ago change em sentinel x 100 inhibitor infill up got to be worth a go before re piping a picture would help boiler and bypass set up regards k

You can set a max kw for heating mate so no worries there
 
Yes bud but has it been down rated ? matey still not said if it's a combi I had a similar problem couple of years ago 24kw valliant eco tec plus system boiler down rated to 15 kw job done .
 
10 mm not the best to power flush, would try adding Fernox F5 heavy duty cleaner and consider replacing all radiator valves
 
Thanks for the updates again.

Sorry, forgot to reply to you question kop, it is a combi boiler, and I don't know if it has been down rated or not. I didn't know having an over powered boiler was a problem. I am hoping for the original installer to get in touch soon, so should I mention that to him? (I am also including some pics as requested. The bypass is in the loft, would a pic of that be helpful?)

It sounds like I should try the cleaners you suggested first, as a re-pipe would be a really disruptive exercise, especially I have recently been redecorating. It would cause a hell of a mess to replace with 15mm pipe, not to say expensive I imagine, but if that is what is required then possibly I have no choice. It's a shame that wasn't suggested at the time, as I had to have new pipe work installed in loft and to/from boiler, as a new larger pipe had to run from the gas meter to the boiler. Anyway, it is was it is for now I guess, I'll see what the guy says when he comes to look at it.

Oh yes, and the rad valves are the same ones originally in place when I arrived. So there is a benefit in fitting new valves by the sounds of things. That sounds a much les painfull path than a re-pipe.

But many thanks for all your opinions and advice, much appreciated.

20170203_195206[1].jpg20170203_195251[1].jpg
 
Thanks for the updates again.

Sorry, forgot to reply to you question kop, it is a combi boiler, and I don't know if it has been down rated or not. I didn't know having an over powered boiler was a problem. I am hoping for the original installer to get in touch soon, so should I mention that to him? (I am also including some pics as requested. The bypass is in the loft, would a pic of that be helpful?)

It sounds like I should try the cleaners you suggested first, as a re-pipe would be a really disruptive exercise, especially I have recently been redecorating. It would cause a hell of a mess to replace with 15mm pipe, not to say expensive I imagine, but if that is what is required then possibly I have no choice. It's a shame that wasn't suggested at the time, as I had to have new pipe work installed in loft and to/from boiler, as a new larger pipe had to run from the gas meter to the boiler. Anyway, it is was it is for now I guess, I'll see what the guy says when he comes to look at it.

Oh yes, and the rad valves are the same ones originally in place when I arrived. So there is a benefit in fitting new valves by the sounds of things. That sounds a much les painfull path than a re-pipe.

But many thanks for all your opinions and advice, much appreciated.

View attachment 28834View attachment 28835

the rad valves arnt the type with two pipes going into one valve is it ?

if yes get them replaced should be much better

also with combis you need to rate them on hot water not heating so your fine there, but as we have said need to be down rated
 
As mentioned previously get an engineer to run a heavy duty cleaner in the system for a week or two and then clean each rad out individually replacing each thermostat (TRV) while the rads are off (do not opt for another power flush unless they have specific experience of doing so). That really should improve circulation or bite the bullet and replace the microbore.
 
Last edited:
All looks tidy there bud a picture of the loft may help is the system vented in the loft ? It may just be air locked the boiler can modulate down to 7 - 8 kw on heating side so providing you have flow it should work ok , did the engineer have a look in the filter that would be a tell tale sign of how bad your system is .
 
Adding pic of the bypass pipework in loft. The engineer was going to switch off the bypass to prove his point, but when he tried it started to leak so he didn't want to continue. But he was convinced that was the problem. He didn't bother looking at the filter as kop asked, as he said that that catches rubbish just before the return to the boiler, and it was his opinion that the blockage(s) were in the hot water loop itself.

Thinking about it, prob won't be too messy for pipe replacement. Being a bungalow, all pipes come down from the loft in room corners with plastic boxing, so I guess not too much to be disturbed. Only in bathroom has it been boxed behind some t&g woodwork, and I guess that can be replaced fairly painlessly. But I would only go down that road if that is the best long term option.


Am happy to remove and clean rads myself, I took them all off years ago when I first moved in and decorated, and can get a fitter to put new valves on. But if the 'gunk' is inside the rads, might it also be an option for me to replace those? (I was even thinking of increasing size of one or two of rads, so good to know I have capacity to do so in boiler by sounds of things.) I know the cost/job is creeping up, but if microbore and rads block up over time, what's point of replacing pipework if I still have old rads with crap inside them? At least then I know whole system should be good for another 10 years (hopefully)! If that is the case, I think that's a job for summer, when rads not required.

Thanks for all the advice.

20170204_130319[1].jpg
 
There's your problem bud that bypass valve should be sprung loaded type not a normal 15mm isolating valve a honeywell or similar the water is finding the easiest route up through better to move the bypass below the ceiling and make sure your flue fittings are drilled and screwed together and also get your engineer to clean the filter have a look at it to see how much magnatite is stuck to it . Regards k
 
Last edited:
So, I've been looking at info re the spring-loaded bypass valve, and it seems like that is definitely the way forward these days. But again, the one in place is left over from the original CH install about 15 yrs ago, when I from what I've read it was normal to have a valve like I have partially open.

So in order to try and resolve the problem, which is definitely still persisting, what is the best order of suggestions from above to carry out? I will get a price for a re-pipe, but I would prefer not to go down that road until summer unless absolutely necessary. Then I may consider changing rads, valves, etc if reqd. For now, however, perhaps just adding one of the cleaning compounds to system followed by powerflush & replacement bypass valve change. Might that be a good plan of attack?

Cheers
 
Last edited:
Get your installer to take the old bypass valve out and just cap it off both sides , 15 mins work if that turn your boiler stat down to 2-3 give it a try , you will know if you need a chemical clean .
 
Get your installer to take the old bypass valve out and just cap it off both sides , 15 mins work if that turn your boiler stat down to 2-3 give it a try , you will know if you need a chemical clean .

Thanks for that again kop. Just to check I understand you correctly tho, by suggesting to remove the old bypass valve, are you also implying that he install one of the newer spring-loaded ones you mentioned previously?
 
So, I've been looking at info re the spring-loaded bypass valve, and it seems like that is definitely the way forward these days. But again, the one in place is left over from the original CH install about 15 yrs ago, when I from what I've read it was normal to have a valve like I have partially open.

So in order to try and resolve the problem, which is definitely still persisting, what is the best order of suggestions from above to carry out? I will get a price for a re-pipe, but I would prefer not to go down that road until summer unless absolutely necessary. Then I may consider changing rads, valves, etc if reqd. For now, however, perhaps just adding one of the cleaning compounds to system followed by powerflush & replacement bypass valve change. Might that be a good plan of attack?

Cheers

Use Fernox F5, replace old rad valves, don't waste your money on power flush with 10mm pipes , not recommended, Places sludge usely collects is in valves due to size of waterways, rads,and I have had blockages in the man-a-folds, so replace them as well
 
Just try what I advised first you can install a external bypass later there is one in the boiler so will be ok just don't run it flat out until you have proved you have flow .
 
Status
Not open for further replies.

Reply to Worcester 30Si misbehaving ? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
231
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
137
I have an ideal vogue max S18 boiler and I’m considering fitting auto balancing TRVs, my question relates to the boilers pump. I see a boiler pump menu for either 70% or 100%, so, is the pump set at either one of two fixed speed percentages or does the pump actually vary speed, (modulate)...
Replies
1
Views
147
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
2
Views
174
PSxxxxxx
P
Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...