I have an issue with lack of flow to an upstairs bathroom and wonder if adding an extra feed from the header tank to just above the gate valve would increase flow, I know it will add pressure. I'm also moving the header tank to the highest possible location in the loft as I only have about 300mm head to the shower. by doing this I hope to increase the head to 3000mm.
 
First of all, - have you considered other options?
An unvented cylinder will provide excellent mains fed supplies if you have decent flow and pressure from mains. Plus it does away with your cold tank. Needs G3 plumber though.
Or a seperate power shower, or a twin pump for shower or other supplies.
Putting a new cold pipe will not increase pressure, but might help flow and would be advisable for a shower or property with more than one bathroom.
Raising the cold tank a lot will help pressure but be careful to allow space above it for vent pipe height. Needs a seriously strong base constructed and new location needs to be strong enough or reinforced
 
Tried pump which failed in 5 months, costumer wants a different solution and hasn't the mains flow to go un-vented at this time. I should be able to increase head by 2.5m.

Cheers
 
Adding 2.5 m to the head will definitely help because you are going from virtually nothing of 300mm.
The shower valve would need to be a good flow valve and - shower head for that matter.
No point in expecting really good flow out of a bar shower.
Aqualisa valves have great flow on gravity as are very unrestricted internally, but I don't like their quality of build.
 
You must have a big loft space if it's going from 300mm to 3000...

Are you sure it's nothing simple like a scaled up hot outlet pipe?
 
Tried pump which failed in 5 months, costumer wants a different solution and hasn't the mains flow to go un-vented at this time. I should be able to increase head by 2.5m.

Cheers

Most decent pumps have a good warranty and even the cheapies have a year. You can't go wrong with a Stuart turner
 
Are there restrictions to flow in the hot pipe coming FROM the cylinder? Is it all 22mm pipe minimum and as few bends as possible, pulled rather than elbows? Is the cold feed TO cylinder 22mm minimum also?
 
Raising tank as well as increase the size of tank .... what size of tank do you have at the moment. Also where's the HW tank in relation to the cold one ? Also your outlets?
 
Was the pump directly off the cylinder? And if so did the cylinder have an anti cavitation valve? Pumps do not do well with air in them!
 
Status
Not open for further replies.

Reply to More than one cold feed to Cylinder in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two...
Replies
2
Views
184
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold...
Replies
2
Views
187
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
414
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock