Filled up a large heating system yesterday and one of the rad wouldn't heat up and also the towel rail.
Most of the pipework is Polyplumb which I has been installed. I managed to trace the pipework back and found 2 of the black 15mm pipe stiffeners to have no hole in. Half a days work to trace and change. I just hope I haven't missed any on other jobs.
 
Filled up a large heating system yesterday and one of the rad wouldn't heat up and also the towel rail.
Most of the pipework is Polyplumb which I has been installed. I managed to trace the pipework back and found 2 of the black 15mm pipe stiffeners to have no hole in. Half a days work to trace and change. I just hope I haven't missed any on other jobs.

Glad it's not just me that has had an issue with Polyplumb, had one blow off due to a faulty grab ring, held up for 4 mths , pulled rep about it, says they don't get any faulty fittings as they are all checked at the factory, they are not responsible once they leave factory, they have a list of get out clauses longer than the Chanel tunnel, blame the outlet you get it from, the way that you store them, or just blame you.
 
your not the first to find this koz and you wont be the last (not made in the uk)
 
your not the first to find this koz and you wont be the last (not made in the uk)

That's interesting where are they produced ? don't tell me its China ! its bound to be somewhere that has rubbish quality control.
total different story I got from rep,
 
That's interesting where are they produced ? don't tell me its China ! its bound to be somewhere that has rubbish quality control.
total different story I got from rep,

cheap labor and shipped in containers to the uk as there part of the terrain group
 
Thanks from what rep told me they are produced in the UK.

:D the custom stuff i believe is but not the normal off the shelf and tbh not much is made in the uk these days
 
Status
Not open for further replies.

Reply to Polyplumb pipe stiffeners in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I need to extend my central heating from my newly built extension in to the old part of my house. I need to feed 3 rads in separate bedrooms on...
Replies
2
Views
200
Bungalow built in 2001. All copper pipework (water and heating) runs in channels of expanded foam polystyrene between a concrete floor and OSB...
Replies
8
Views
411
Hi guys, These sleeves cover 10mm PVC central heating pipes (see picture and ignore tape measure) and I believe this is what makes it possible...
Replies
2
Views
375
Hi thank you for letting me join this forum . We have an air to water heat pump but the bungalow is piped in micro bore 10mm pipe which doesn’t...
Replies
4
Views
376
Hello guys, an easy one: I recently had to drill through two outside walls to run 15mm pipes for a shower and sink. The holes are neat enough but...
Replies
1
Views
490
Back
Top