Anybody have a good way to calculate this please? Cold water expansion vessel on an unvented. Vessel is not ruptured, PRV is OK but every now and again it drips a bit. I suspect the vessel pressure is too high for the system...
 
The vessel should be charged to the same pressure as the mains static pressure or to the pressure reducing valve setting (usually 3 bar), whichever is less.
 
Last edited:
I spotted that and edited it as soon as I posted. Was hoping to change it before anyone saw it!
 
Charge it to 0.1 or 0.2 bar greater than the Pressure Reducing Valve, Mas

You can't use the static pressure as it fluctuates you could set it up for a 10M head to find that at night when the Economy 7 is on & water is heating the mains is at 20 or 30Metre.

Think about it, you want the bladder held flat with the air pressure when cold, only allowing water in as the pressure in the system starts to rise as it heats, thereby creating more volume in the system when hot that when cold = controlling pressure rise.
 
Charge it to 0.1 or 0.2 bar greater than the Pressure Reducing Valve, Mas

You can't use the static pressure as it fluctuates you could set it up for a 10M head to find that at night when the Economy 7 is on & water is heating the mains is at 20 or 30Metre.

Think about it, you want the bladder held flat with the air pressure when cold, only allowing water in as the pressure in the system starts to rise as it heats, thereby creating more volume in the system when hot that when cold = controlling pressure rise.

Thanks Chris! I had the figure of 0.2 floating around in the back of my head but I was getting mixed up with calculating expansion vessel size and got a mental block!
 
I set them for system design pressure + 10%.

Same thing as Chris really!
 
I've found it depends where you look it seems. I've seen to charge it to match incoming pressure, which does seem wrong as pointed out by Chris because the pressure fluctuates anyway. Also to charge it to .20 bar over the reducing valve pressure.

Reliance Water Controls says to charge the vessel to .20 bar under the reducing valve pressure.

So my conclusion is follow the manufacturers instructions (as always) or "about 3 bar!"



Tribune says to match pressure reducing valve in the manual I read (usually 3 bar),
 
Status
Not open for further replies.

Reply to Calculating pre-charge in CW expansion vessel.. in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
2
Views
170
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
161
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
384
Our kitchen mixer tap has started dripping. Like so much of the plumbing in our almost new build bungalow, it is lacking! The plumber didn't install any isolating cocks in the H&C feed to the tap so how can I identify which of the valves is passing? Shut the whole H&C water system down?
Replies
12
Views
386
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
2
Views
237
P
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock