I have 1 cold rad in a downstairs cloakroom.
I have flushed it, tested the valves ( not trv ) and connected a hose from the o/side tap to each valve to blast any air-locks.
I have turned off all other rads and it still won't work.
I have replaced rad with a length of 15mm pipe and the pipe gets hot immediately! Put a new rad back on and it works for 2/3 days then fails.
If I draw 1/2 a bucket from the return pipe, hot water is drawn thru the flow pipe and the rad works for 2/3 days.
I know it could be a blockage, either air or sludge, but how come I can always draw hot water thru if I drain from the return pipe?
It seems as if there is something stopping the free flow thru the system which I can by-pass by encouraging the flow when draining.
I would be interested in advice as to what should be my next step.
Someone must have come across this before!!
Thanks
 
Take the rad outside and blast cold mains through it with an house pipe, is it an old system / old rad?
 
Take the rad outside and blast cold mains through it with an house pipe, is it an old system / old rad?
Thanks for the reply.
Did that with old rad but made no difference.
Put a length of 15mm pipe between valves and hot flowed as normal so thought it must be the old rad.
Bought new rad and installed and it got hot immediately, worked for 2/3 days and then packed up.
I've been told it could be air building up over 2/3 days and I thought of putting in an automatic release valve but I'm not sure where in the flow pipe I'd put it!
Frustrating because it works every time with the 15mm pipe and that's just a small rad!!!
 
try flushing out with hose again, could be that the sludge is building up in this rad, Automatic air valve would look a bit weird coming from radiator. Can get automatic bleed valves for radiator I think. have you tried bleeding radiator?
 
try flushing out with hose again, could be that the sludge is building up in this rad, Automatic air valve would look a bit weird coming from radiator. Can get automatic bleed valves for radiator I think. have you tried bleeding radiator?
Yeah I've bled the rad and the automatic valve was to go in the pipework in the ceiling ( the highest point ).
I've now had a mate suggest its not sludge or air but a "cold water barrier" stopping the hot water getting thru.
He's suggested turning the pump round the other way to see if it dislodges the cold water. Don't know if there are consequences doing that but I can see where he's coming from.
It's so frustrating because if I take off the rad and replace it with 15mm pipe the pipe gets hot immediately!!!
I'm wondering whether to put a piece of pipe between the flow and return pipes, with a valve in, below the rad. In effect, short-circuiting the rad.Then when the pipe gets hot, turn off the valve in the pipe so the hot water has to go thru the rad.
Seems like a lot of trouble but I'm beginning to clutch at straws.!!!
 
what type of system is it? what is the water in the system like? is the radiator near/far away from pump? is the system balanced correctly? what pump do you have and is it set on max?

sounds like air lock/problem.
 
if valves work, no air, rad clear it is circulation fault, is it 2 pipe system, balanced properly etc, check all connections and valves and then shut down ther rads to try to force round, if it goes round u need to balnce
 
what type of system is it? what is the water in the system like? is the radiator near/far away from pump? is the system balanced correctly? what pump do you have and is it set on max?

sounds like air lock/problem.

Gravity fed open vented system.
Ignore balancing because if I turn off all other rads, it still doesn't get hot!
Pump is new and identical to old pump, set to max.
Water in system is ok, fernox added and nice and clean when I drain some.
I know it seems like an air-lock but I don't understand why hot water comes thru ok when I remove rad and replace with 15mm pipe!
I like the idea that it could be a "cold water barrier" stopping the hot coming thru because I don't detect any signs of air when draining it. Also, the rad works for 2/3 days until the water in the pipe feeding it gets cold again.
Is there a problem with turning the pump around ( even for a short time ) so reversing the flow in the system, to see if it works by having the hot water coming thru the "return" pipe and pushing the cold water ahead of it in the " flow" pipe?
The TRV's I have are bi-directional so I can't see a problem there.
Thanks
?
 
if valves work, no air, rad clear it is circulation fault, is it 2 pipe system, balanced properly etc, check all connections and valves and then shut down ther rads to try to force round, if it goes round u need to balnce
New valves and pump.
Agree with circulation problem, now I need to solve it!
2 pipe system.
Would turning the pump round and reversing the flow be ok?
Thanks
 
bi directional trvs can still stick in off position

dont turn pump round shut off other rads and see if it gets round
 
Where does your friend suggest this cold water is??

Is the system 15mm to rads or microbore? has this rad been joined onto existing system?
It sounds like a problem with the pipework, either a long draw off to the rad or it has been bent, squashed causing a restriction of flow.
 
Last edited:
bi directional trvs can still stick in off position

dont turn pump round shut off other rads and see if it gets round[/

Thanks, tried that, no luck.
Been told to turn pump down as it might be pushing hot water past the joint before it has a chance to enter pipe.
Gonna try that now.

Also, I will try putting in an automatic bleed valve in pipe at highest point, in case it is an air-lock.
Running out of ideas. Hoped someone else had come across a similar problem.

Thanks
 
Where does your friend suggest this cold water is??

Is the system 15mm to rads or microbore? has this rad been joined onto existing system?
It sounds like a problem with the pipework, either a long draw off to the rad or it has been bent, squashed causing a restriction of flow.

15mm.
The pipe run looks to be quite long. I can't see it all the way because it passes over a wall about 4 feet away.
The pipe is under the floor at 1st floor level, it then drops vertically to a rad in a downstairs cloakroom.
We think the cold water is in the long horizontal run below the floorboards.
I don't think its an air lock, but just in case, I'm going to drain down the system and fit an automatic air vent in the pipe because there's nothing to lose.
I've turned off all the other rads and felt the 2 pipes ( flow + return ) to see if they warm up.
The flow pipe remains stone cold + the return warms up slowly ( I think its just the water flowing thru the system gradually heating up the water in the pipe from the other end )
When I drain off 4 pints from the drain valve in the return pipe, the flow pipe gets proper hot and the rad works for 2/3 days.
Its as if the drained water is replaced by the cold water in the flow pipe, closely followed by the blocked hot water.
Then when the system cools, the cold water blocks the hot again.
It's an existing rad ( now replaced with a new one ) that worked fine for 18 years. Coincidentally, I drained the system down to replace a bathroom rad with a towel rad, and that's about the time it stopped working.
No damage to pipework.

Thanks
 
its not a 1 pipe system so dont see how it can pump past the rad? youve tried shutting down all other rads and it didnt work but youve pulled it through return and it does? youve altered the towel rad and it stopped working? this is puzzling? is there a trv on the towel rad? is the rad linked from/to the towel rad? could it be the trv shuts down both rads? this could be so if piped wrong

is there a cylinder on the system?
 
I still reckon it is a badly balanced system.
You have definitely tuned off all the other rads? Do the rads have TRV's fitted?
Seen a similar problem dozens of times and 99% are badly balanced systems due to dodgy pipework and long runs, the other 1% is due to a blockage causes mainly by bent or squashed pipes.
The way I would be doing this is to make sure every rad is off at the lockshield valve not TRV, including hall rad if its got 2 x Lockshields. This almost always sends water to cold rad, then you need to balance the system accordingly. Just opening them all back up will not sort the problem out.
It could be air gradually building up and blocking it up, air will always rise to the top so the thing to look for is where the pipe goes up over something then back down. imagine the pipe going over a door frame. This could happen if a new pump has been replaced, the old pump may have been powerfull enough to keep pushing the air around the system.
 
Last edited:
yes the smart money is on badly balanced which can be enhanced by badly piped

but if he has shut off all the other rads?
 
bi directional trvs can still stick in off position

dont turn pump round shut off other rads and see if it gets round

Done that and flow pipe still doesn't get hot.
Seems like I need to drain water from the return pipe just to encourage the hot to come thru the flow pipe.
Once the rad heats up it stays working until the system shuts off + the water in the pipes cool down. Then I need to drain water to get it started again.
Gonna try draining down and taking out a piece of the flow pipe,( as high as I can ) replacing it with a "T", and fitting an air bleed valve on the arm of the "T". Just to satisfy myself that it's not an air-lock.
I've also tried turning down the pump in hope that a lesser force will give the hot water more chance of entering the flow pipe,( rather than by-passing it ) but that hasn't worked.
If all else fails, I'm going to buy a towel rail with a heating element in it!!!
Thanks again, keep the ideas coming.
 
I still reckon it is a badly balanced system.
You have definitely tuned off all the other rads? Do the rads have TRV's fitted?
Seen a similar problem dozens of times and 99% are badly balanced systems due to dodgy pipework and long runs, the other 1% is due to a blockage causes mainly by bent or squashed pipes.
The way I would be doing this is to make sure every rad is off at the lockshield valve not TRV, including hall rad if its got 2 x Lockshields. This almost always sends water to cold rad, then you need to balance the system accordingly. Just opening them all back up will not sort the problem out.
It could be air gradually building up and blocking it up, air will always rise to the top so the thing to look for is where the pipe goes up over something then back down. imagine the pipe going over a door frame. This could happen if a new pump has been replaced, the old pump may have been powerfull enough to keep pushing the air around the system.

Ok I'll give it another go and I'll try and fit an air bleed valve of some sort as high in the pipework as possible.
Thanks again
 
dont see how it can be an air lock unless theres a leak or wrong vent inlet position, bu if you say it worked before there must be an issue with what has been altered surely?
 
dont see how it can be an air lock unless theres a leak or wrong vent inlet position, bu if you say it worked before there must be an issue with what has been altered surely?

The only change I've made is to remove a bathroom rad + replace with a towel rad. I fitted one side to the existing pipework.
The other side had to be altered to line up with the rad. So I cut the pipe + extended it by 150mm. That's all.
Can't see how that would affect the other rad. They're not directly connected and I've tried turning off the towel rad to see if it helps.
I will drain down again + fit an automatic air-vent in the horizontal run in the ceiling leading to the rad. At the same time I'm going to fit 2 full bore in-line isolating valves in the flow + return pipes, so if I have to work on the rad, at least I won't have to drain down the whole system.
Thanks for all the help, I'm sure we'll solve it in the end.
 
I was wondering if I could put 2 tees in the return pipe. Have 2 flexible hoses coming off the tees connected to a drill driven pump so that, when the rad stops working, I could encourage the circulation by helping the flow thru the rad.
I know it seems like a lot of trouble but I'm clutching at straws here!
It seems as though I just have to get the hot water started and the rad will work for 2/3 days, so a little boost in the system every 3/4 days is better than a cold rad all winter!
 
The only change I've made is to remove a bathroom rad + replace with a towel rad. I fitted one side to the existing pipework.
The other side had to be altered to line up with the rad. So I cut the pipe + extended it by 150mm. That's all.
Can't see how that would affect the other rad. They're not directly connected and I've tried turning off the towel rad to see if it helps.
I will drain down again + fit an automatic air-vent in the horizontal run in the ceiling leading to the rad. At the same time I'm going to fit 2 full bore in-line isolating valves in the flow + return pipes, so if I have to work on the rad, at least I won't have to drain down the whole system.
Thanks for all the help, I'm sure we'll solve it in the end.

is it a trv on the rad? if so it could be faulty, i always use manual valves on towel rails
 
is it a trv on the rad? if so it could be faulty, i always use manual valves on towel rails

The rad that won't work has 2 wheelhead valves on--brand new. The rads with TRVs on are all new valves.
Sure it's not the valves because I've replaced them all. New rad too.
I think its a combination of a long pipe run, having to flow up and over a partition wall.
It might still be an air-lock but it doesn't feel like it. When I drain 2/3 pints from the return pipe there is no spluttering or air in the top of the rad.
I will drain down and put an automatic air release valve in the long horizontal run anyway, just in case.
I'll also put in 2 full-bore isolating valves in the flow + return pipes at the same time, so I don't have to keep draining down the whole system.
Any advice on my idea of fitting a drill-driven pump in the return pipe, to assist with the circulation.
I get the feeling that if I can get the circulation going and the hot water thru, the rad will continue to work for 3/4 days before I'd need to help it again.
It might even work continuously once the weather turns colder and we have the heating on longer and every day.It only stops working at the moment when the water inside cools right down.
Thanks again.
 
If there's an up and over section (partition wall) does the pipe have a bleed point there?
 
i wouldnt bother with putting a drill point on, easier to find a permanent solution

the up and over sounds the obvious problem area, do you draw water from return only? try the same with the flow.

can you redirect the flow or return? leave one connected at the same point and move one connection closer the boiler?
 
i would track back along the pipes to see where the hot water stops my bet is a pair of ballofixes left under floor, half off,with some build up of dirt in them but that wouldnt explain the link pipe working ????
 
If you are having problem with possible flow to rad, the last thing you want to do is decrese it even more with iso vlaves.
Unless the pipe work is going up over something then back down (making an air trap in high point) then I doubt its air.
Still say its a blockage, either on pipework or rad/valves.
 
connect the flow closer to the boiler, leave the return, therefore create a reverse return system
 
Ok guys.
The pipe to the rad does go over a wall and is horizontal for about 2 metres. I can't see the other side of the wall but I think it probably dips down so, yes, it could be an air-lock.
It doesn't "feel" like air though because when I drain from the return pipe, there is no spluttering and no air trapped in the rad.
I will still put in an automatic air vent, just in case.
I was going to put in full-bore iso valves so the flow would not be decreased.
If it was a blockage, I don't understand how the hot water is able to get thru if I drain some water from the return pipe. Surely a blockage would stop all flow?
It does seem to be a circulation problem because draining water from the return pipe encourages the water in the flow pipe and the rad will get hot and work for 2/3 days, until the water cools.( or until air builds up in the pipe ).
I just thought putting a small pump in the return pipe might be enough to keep the system working.
Thanks
 
Ok guys.
The pipe to the rad does go over a wall and is horizontal for about 2 metres. I can't see the other side of the wall but I think it probably dips down so, yes, it could be an air-lock.
It doesn't "feel" like air though because when I drain from the return pipe, there is no spluttering and no air trapped in the rad.
I will still put in an automatic air vent, just in case.
I was going to put in full-bore iso valves so the flow would not be decreased.
If it was a blockage, I don't understand how the hot water is able to get thru if I drain some water from the return pipe. Surely a blockage would stop all flow?
It does seem to be a circulation problem because draining water from the return pipe encourages the water in the flow pipe and the rad will get hot and work for 2/3 days, until the water cools.( or until air builds up in the pipe ).
I just thought putting a small pump in the return pipe might be enough to keep the system working.
Thanks

i wouldnt bother with a pump, your far better solving the problem. you say you drag water through the return, have you also tried it with the flow?
blockage, if the blockage is in the flow of course you can get water out of the return as theres no blockage there

can you re connect the flow or return closer the boiler (not both) reverse return system

url
 
Can I just clarify what has been said,
1. radiator not working
2. heat is passing through when radiator disconnected and pipe placed instead
3. replace radiator and stops working
4. drain down from one side and radiator is working fine for a couple days then stops.
5. pipe work comes from attic across house and down.

my theory would be pipework, where is it coming from? does it connect to 22mm or 15mm pipe, is the pipework to radiator 15mm, 10mm or 8mm?

just seems like there isnt enough pressure to push water all the way through, when radiator is disconnected it is pushing it far enough, but when connected there isnt enough pressure to push it along. either that or partial blockage at joint that is blocking completely when heating is cold and when you are pushing heat through it is unblocking slightly.

the way I would go would be to find where radiator connects to rest of system and replace. or connect radiator pipework to somewhere closer.

water finds easiest route, so possibly passing straight past join and not going to your radiator.
 
try replacing the trv. also ensure you hsve no restrictions on the return pipework, or partial blockage in the feed from the top up cistern, which can cause flow restriction
 
i wouldnt bother with a pump, your far better solving the problem. you say you drag water through the return, have you also tried it with the flow?
blockage, if the blockage is in the flow of course you can get water out of the return as theres no blockage there

can you re connect the flow or return closer the boiler (not both) reverse return system



url

I can't drain water from the flow pipe because the drain valve is in the return pipe.
If there is a blockage how can the hot water get thru the flow pipe when I drain from the return pipe?
When I do this, the rad works ok for 2/3 days!
Thanks
 
the water may not be coming from the flow pipe is my point, it CAN come from the return pipe

and you havnt answered my question, can you tee either the flow or return closer the boiler?
 
I think you're right. The problem is in the system before the rad but I can't get at the pipework there.
I just find it strange that I can get it working for 2/3 days before it packs up again.
As long as the water in the pipes is hot, the circulation seems to be ok.
The problem occurs as the water cools down.
I thought putting a small drill-driven pump in the return pipework might give the system the boost it needs to keep working.
I would only need to activate the pump for seconds, until the hot water comes thru again.
Thanks.
 
The hot water is definitely coming from the flow pipe because I can feel it coming down the pipe as I drain cold water from the return. It then circulates ok for as long as the heating is on. It seems that once I have the system flowing, it works ok but stops when the water cools.
Not sure if I can tee closer to the boiler.
Thanks
 
would still look to balancing the system, and changing trv. The pipework after the rad is more likely the problem, unless as already stated there is a restriction in the feed
 
This is worth a try . Remove RAD close flow valve leave return open and close all other radiators.If this is a gravity system cap the vent pipe to the Fill and expansion,if a pressurised system no problem .Connect mains pressure to the heating system and open the return on the problem rad .The idea is to blow all the crap back out of the return pipe of this problemed area ,it may take some serious flow and keep pulling water off ,sounds like a bottle neck has become blocked and needs reverse flow to clear it. Hope this helps.
 
it seems to me that you are looking for an easy fix and imho there is no quick fix,

your options.

1. Put the pump on and AAV push the pump every few days, this will get the system running and like you say maybe when it gets hotter, you will not have to keep doing it, but if it is a blockage in the summer it will get worse. Remember to put 2 iso valves on there so it doesnt leak after you finnished and a iso valve on pipework that is being taken out so it doesn't just circulate in a circle.
2. Take floorboards/ walls up, replace joins and check for dirt
3. Get the system powerflushed and hope it is sorted by this (not sure this will work but might do)
4. Re-pipe the pipework so that it is connected to another rad

My opinion is get a proffesional in to do the work properly, get it fixed now and you wont have problems later
 
when hot it works when cold it doesnt. sound like a section is working on gravity and therefore the pump is missing the rad out as such. can you swap the tee for a swept tee
url
 
when hot it works when cold it doesnt. sound like a section is working on gravity and therefore the pump is missing the rad out as such. can you swap the tee for a swept tee
url

I was thinking something like that but didnt know it was possible, thanks fuzzy, learn something new every day
 
this rad isnt run on when hot water only selected by any chance?
 
You definately need a permanent solution to this.....

There seems to be 2 major changes to the system since the rad hasnt worked (but did for 18 years?) A new towel rad and a new pump. I agree with an earlier post that the pump may not be as powerful as the older pump (so hot water is having a harder time trying to get to this lonely rad through longer than normal pipework over obstacles etc) If this is the case? Then if you tee this rads flow closer to the boiler you will be removing an awkward dead leg of pipework which may work??

But we need to also look at the other changes you have made since it stopped working... Can you remove the towel rad and place a temporary bridge between the flow and return (like you did in the cloakroom, using 15mm) Just to rule out the fact since this rad was installed with its new (but could be faulty) TRVs the cloakroom rad didnt work? worth a shot?!

The other major defect could be a possible blockage in the system (air or debris)? Again the original pump may have not had an issue....
The best fix is probably to power flush piipework to be on the safe side, although I would also recommend re-doing the flow and/or return pipework to rad?

Just a brainstorm here, but will the system all on max, including all TRVs and lockshields (and thermostats) to maximum WHERE exactly does the hot pipework stop? If you can feel around the system, along flow/return to the problem rad, where does the pipework stop being hot? If it is at a tee to the problem rad, then a swept tee (as suggested earlier) may work or the fact that this rads tail offs from the 2 pipe system are too long??
 
could just be that the new towel rail is stealing all the heat and after a couple of hours the rad may kick in? Have you balanced the system?
 
if the towel rail replaced a previous rad its unlikely to be stealing heat as its probably a lower output

it may be more restrictive and with a less powerful pump it simply doesnt get there
 
The way this thread's going you won't need that radiator as it will be nearly summer ...
 
PaulRB.....you are not alone.
I have the exact same problem as you but on my kitchen rad. I thought i was all alone with this problem!!
If i shut off all other rad lockshields eventually, and i say eventually the rad warms up but does not get HOT,so frustrating.
New rad and valves fitted ( no trv on kitchen rad), tried balancing, tried pump speeds, tried bleeding the air........water coming out of all rads when bled. Have drained system and refilled again....put in inhibitor. NOTHING!!!
return pipe is hot, flow is cold!
Even the plumber i called was baffled.
1 THING THOUGH,
With all the above done, i am getting a constant noise of flowing water at the boiler and also at the pump in the airing cupboard.
Boiler fires but only for about 30 seconds
PLEASE HELP.
 
But he has said he has turned off all other rads, so it would have nothing to do with the towel rad. As with them all off it still dont get hot.
 
have you taken the automatic valve apart and checked the components inside the needle sticks in that aswell ,and peronally i would put a trv and lockshield on the rad
 
Status
Not open for further replies.

Reply to cold rad in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold...
Replies
2
Views
230
I have a green star ten yrs old keeps increasing pressure, feel on off filling valve not working, drain off to recommended, but after few days...
Replies
1
Views
210
P
  • Question
Boiler is SIRIUS THREE FS 70 Potterton commercial. Situation: We are small building contractors and my labourers managed to damage the radiator...
Replies
2
Views
147
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
474
S
Hi, I seemed to have a blockage in kitchen sink. A plumber came and cleared all the pipework that is visible inside my home (there was debris and...
Replies
2
Views
166
Sonya K
S
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock