Discuss Combining feed and vent piping from F and E tank in the Central Heating Forum area at PlumbersForums.net

Messages
11
It would save me a lot of faff if it was acceptable to combine the feed and vent in the manner shown in diagram below.
Or should I resort to separate pipes for each, as small sketch.

Boiler is Potterton Suprima


cent_heat Layout.jpgright way.jpg

I would be grateful for your advice.

Thanks

Rudy
 
No worries buddy. The only thing I will say about that particular design is sometimes it can prove problematic filling the system from empty and displacing the air

I always make sure the cold feed is sloping slightly upwards on the 'horizontal' part of the pipework towards the F&E tank, to ensure the air escapes. There's then no real need for a vent pipe back into the tank (saves pipe, insulation and the faff of cutting the lid.
 
It would save me a lot of faff if it was acceptable to combine the feed and vent in the manner shown in diagram below.
Or should I resort to separate pipes for each, as small sketch.

Boiler is Potterton Suprima


View attachment 44993View attachment 44994

I would be grateful for your advice.

Thanks

Rudy
In my opinion, you would be better to pipe it correctly if you can do.

1597679661934.png

[automerge]1597680207[/automerge]
Given there's not a check valve in the outlet of the F&E tank I've never understood the need to the vent.
Primary open safety vent.
The purpose of the primary open safety vent is to provide a safety outlet should the system overheat due to component failure and ensure that the system is kept safely at atmospheric pressure. The minimum diameter of the safety vent is 22 mm and the pipe should never be valved. In a fully pumped system, the primary open safety vent should usually rise to a minimum height of 450 mm above the water level in the F&E cistern. This allows for any pressure surge effects created by the pump. The open safety vent also aids the removal of any air that the system might collect, particularly on commissioning or refilling.
(Level 2 Plumbing Pearson Schools and FE Colleges)
 
Last edited:
I always make sure the cold feed is sloping slightly upwards on the 'horizontal' part of the pipework towards the F&E tank, to ensure the air escapes. There's then no real need for a vent pipe back into the tank (saves pipe, insulation and the faff of cutting the lid.

The continuous rise will help with displacing the less dense air for sure mate. And yes I have seen systems without the vent over hanging the cistern. As long as there's an unrestricted and suitably sized pipe it will work fine.
 

Reply to Combining feed and vent piping from F and E tank in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

Hi all, Got a nightmare situation with a central heating system I recently adopted. It's an open vent system with a combined F&E pipe, with a...
Replies
17
Views
2K
    • Like
Hi I recently did some pipe insulating in my loft. The only two I didn't do were the vent pipes. Not sure if that is the right term for them...
Replies
2
Views
377
Hi guys Is it normal for the cold feed pipe from the f&e tank to be combined with the open vent? The cold feed connects to a 22mm tee one end is...
Replies
2
Views
1K
Hi, I'm new to the forum and just some background on myself. I have 4 years experience as a plumber but haven't worked in the trade in 15 years. I...
Replies
13
Views
632
Hi so I changed a towel radiator in bathroom from a normal radiator. I bunged the f&e tank and vent pipe , drained about a pint of water out the...
Replies
3
Views
620
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock