I have a grant vortex combi and it keeps tripping the main fuse when the programmer calls for heating.
This has just started, it was working fine before.

Anybody got any thoughts
 
Or water inside the pump power connections be careful do it with the power isolated
 
When does it trip when the power is on or when there’s demand ?
 
Contributing as a spark in the boiler and wiring there could be many reasons for the "trip" - but as you suggest the fuse / MCB are tripping as well as the MCB then the likelyhood of a live - earth fault is possible.

Is there any water dripping from the boiler?
Valves?
When you say call for heating - are you really running the heating ATM?
Has anybody changed anything - like tried to fit a smart thermostat or programmer?
Have you done any DIY?

Tricky to give much more by the way of advice without seeing the installation first hand tbh
 
No water leaking.

Trips when demand for heating comes on from the programmer.

Nothing has changed, just started doing it today

Murdoch, what do you mean by ATM, if you mean at the moment the answer is no the heating is switched off, the domestic hot water is on and running fine, it happens when i switch the heating to on then it trips.

Thanks

Regards
 
You could do with an engineer to run some tests.
I personally would disconnect and make safe the live, neutral and earth to pump and then bring on at programmer again to rule in or out the pump.
If its not the pump then somewhere inside the control panel is the fault, providing of course you only have one heating zone and not multiple as mentioned above.
You really need an engineer to do all this for you.
 
No water leaking.

Trips when demand for heating comes on from the programmer.

Nothing has changed, just started doing it today

Murdoch, what do you mean by ATM, if you mean at the moment the answer is no the heating is switched off, the domestic hot water is on and running fine, it happens when i switch the heating to on then it trips.

Thanks

Regards

what type of controller do you have?
 
I have a grant vortex combi and it keeps tripping the main fuse when the programmer calls for heating.
This has just started, it was working fine before.

Anybody got any thoughts

What fuse is it tripping?

Is it the fuse in the fused connection unit or the MCB (or is it the RCD) in the consumer unit?
 
Success i think, i disconnected the pump and turned the programmer on and it didn't trip.
Will post again after i get a new one fitted.

Thanks for your help.
[automerge]1596718140[/automerge]
Problem solved, when we went to remove the pump the pump cable was jammed between the front of the flame box and flame box casing, when we took the front off the cable was fried.

Put a new cable in and it's all working now.

Thanks for all your help

Regards
 
Last edited:

Reply to Boiler keeps tripping main fuse in the USA area at PlumbersForums.net

Similar plumbing topics

Recently had a Viessmann Vitodens combi boiler installed, quite often when the adjacent cold mixer tap is opened the boiler starts for a few seconds! Can anyone tell me what is causing this? And how to cure?
Replies
3
Views
218
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
362
I have a green star ten yrs old keeps increasing pressure, feel on off filling valve not working, drain off to recommended, but after few days it's increased whilst cold...is this a regular problem.
Replies
1
Views
164
Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
251
Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I have changed the 3 port actuator Honeywell head however this doesn’t seem to have solved the issue, does this mean that the programmer is faulty? Or is...
Replies
8
Views
308
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock