Looking for peoples views of best setup, location and any points to consider that I don’t mention please

2000 built home, 4 bed, family bathroom, en-suite, downstairs toilet, radiators

Currently set up with gravity fed system. Showers are a terrible. Want to rip out everything and start over, without Compromising at any point. Aim is never to feel a change in temp or velocity of water, up to 2 showers run simultaneously

Leaning towards unvented cylinder, new boiler, 22mm new cold supply, accumilator.

Guesstimate my flow rate to currently be 12ltrs per minute using kitchen sink test. So that’s why I would install new supply. Not sure about pressure. Probably ok. But not amazing. So I’ve read a accumulator helps that.

Been offered by first plumber 42kw combi. But I’ve read that doesn’t matter what the boiler is capable of. Unless you can get succifiant water coming in. You can’t run 2 decent power showers simultaneous. So ruling out combis unless I missed anything on this

Would ideally like to move boiler and unvented to loft. A full unvented setup is massive and a complete eyesore. Would be prepared to fully board and insulate roof. But I keep reading frost will affect boiler even with frost free. Not sure how cold Loft will get once insulated. But without a radiator up there. I would speculate it won’t be much above freezing most of winter. So this puts me off. Any comments positive or negative on this. Or fixes

If I go with loft I read this:
Gas, water, and electrical isolation points should be provided outside of the roof space so boiler can be isolated without gaining access to roof space. Lag pipes. Especially the “condescending pipe” ?
Anything else anyone can add please

Also running a new 22mm water supply up the side of the house to loft. Will this mean I’m going to loose a ton of pressure? Really wanting to avoid pumps. They noisy and one broke down on me in year. So have little confidence in something with that many moving parts. So if I do loose pressure something to help with this. I believe accumulator is the answer

Other questions
Is g3 certified the same as gas safe or are they different qualifications

Probably will change radiotors. Will there be change in pressure in the central heating with the new setup. How likely is any of my pipe work connections gonna give way with new pressure and need accessing and sealing

Any other factors and considerations? Please

There is a option to put it all in an internal garage. But this means I would use a ton of useable space and take away the option to convert the garage in the future. Without garage heating, I can’t see it being much warmer than the loft.

current cylinder is in a airing cupboard on floor one. But I don’t think you’d get a Unvented in there

cheers
 
  • Like
Reactions: Lou
You already well informed compared to some whom ask this question. I think your first action is to accurately test your incoming water for
1. volume. 2. Pressure.......they are separate but inter related. Test at a reliable place like an outside tap. Not at a tap with reducers or fancy airation inserts Test at specific times. Sunday morning 7am when demand is least
Weekday morning 7.30am and NOT in school holidays when the demand peaks.
Then we will know what you are dealing with. Where are you because some areas are diabolical. the suppy crawls out of the main. centralheatking
 
The system you want is right but where to locate it?

Convert the loft and stick it in the garage, it's an almighty faff to do a loft install plus folks despite the actual risk of failure tend not to like the thought of many hundreds of litres of hot water residing above their heads. Temperature shouldn't be an issue for either if everything is insulated (even the boiler) and you need G3 qualified engineer to install an unvented cylinder.
 
The system you want is right but where to locate it?

Convert the loft and stick it in the garage, it's an almighty faff to do a loft install plus folks despite the actual risk of failure tend not to like the thought of many hundreds of litres of hot water residing above their heads. Temperature shouldn't be an issue for either if everything is insulated (even the boiler) and you need G3 qualified engineer to install an unvented cylinder.
In the garage all day long wack a honeywell frost stat in the coldest corner near the door
off you go....get two quotes loft or garage its obvious which one will be cheaper and thats the best location ...centralheatking
 
Loft or garage, combi or unvented?? Everyone you ask will have a slightly different perspective. Only you can choose.

The only point I would be (very) uncomfortable with is running the 22mm mains supply to the loft externally to the property.

If you opt to go down the (pumped ?) accumulator route - I would not consider installing that in the attic.

If you go for the loft installation, the area must be properly prepared with good access and support for the UV tank. Without teaching you to suck eggs - the limiting factor is (in my experience) hatch size and overhead clearance to get a decent UV tank into place.
 
OK, I'm not a plumber but was in your exact situation last year. 3x bathrooms, downstairs toilet in a large victorian semi, gravity-fed. Also 15mm mains feed, 13 litres per min at garden tap with 3bar.

Like you I considered a large combi, but having spoken to people who had actually had this done, it wouldn't sustain 2 high flow showers simultaneously, which was my requirement.

I did a lot of research and decided for an unvented cylinder and an accumulator until I could upgrade the mains feed (it's under the front driveway which I'm planning to redo in a couple of years). In the end, had the unvented cylinder fitted while waiting for the accumulator to come into stock (it was on 3 weeks order). The flow and pressure was so good out of the unvented cylinder I ended up cancelling the accumulator order and haven't yet upgraded the mains supply to 22 or 28mm. I don't really need to upgrade it but will end up doing so when the drive is being done as it would be a shame not to.

Guess what I'm saying is have an unvented cylinder fitted and see if you are happy. If not, upgrade your mains feed. If still not happy, add an accumulator. You might end up saving some cash.
 
Another vote for the garage too. If your cylinder leaks in future then I wouldn't want it leaking through my ceiling, at least in the garage it can do little damage. Also from a maintenance point of view of servicing etc it's a lot easier. And you notice things when they go wrong, when it's tucked away in the loft you'd only know there's a problem when something starts leaking or something stops working!

I'd bet it's easier getting a new water main to the garage too than the loft....
 
If temperature is a real concern for either boiler location especially if the system is going to be off at critical times and for long periods you can always use an antifreeze protector like Alphi 11, pricey to dose a large system at the right levels but that is relative.
 
In the garage all day long wack a honeywell frost stat in the coldest corner near the door
off you go....get two quotes loft or garage its obvious which one will be cheaper and thats the best location ...centralheatking
So no one likes the loft placement:)
I get the reasons why having big heavy equipment is better on a lower level and closer to the feeds etc. It just meant when I converted the garage. I had nothing in the way.
This is my house.
picture 1 is the old boiler position on the wall in the utility room I want to get rid of
Picture 2 the red is the other side of the wall the boiler is on. The blue is where I’m considering now positioning a new boiler. Far enough away from the wall so it can be knocked down with having to move it again
I have this tiny utility room. The wall backs on to the internal garage. So my idea was to get rid of the wall in the future and make the garage living space. I didn’t want to use a large portion of the garage new living space already used for the boiler and unvented and potentially accumulator. But maybe if he can fit the unvented in the airing cupboard upstairs. It would be as bad. Anyone know what minimum size what be for a cupboard to fit standard unvented. Including pipe work etc.
[automerge]1571394087[/automerge]
Loft or garage, combi or unvented?? Everyone you ask will have a slightly different perspective. Only you can choose.

The only point I would be (very) uncomfortable with is running the 22mm mains supply to the loft externally to the property.

If you opt to go down the (pumped ?) accumulator route - I would not consider installing that in the attic.

If you go for the loft installation, the area must be properly prepared with good access and support for the UV tank. Without teaching you to suck eggs - the limiting factor is (in my experience) hatch size and overhead clearance to get a decent UV tank into place.

I had organised a quote from instaloft to look at the loft. Was thinking to strengthen joists. Make a bigger hatch. Completely board. And insulated the roof rafters. Before I put any plumbing stuff up there.Good point about running a pipe externally up the side of the house. I wouldn’t have considered that. It’s amazing what some plumbers will recommend just so they can do the easiest way for them. And not what’s best. Which is why I’m researching and using this forum. Thanks
[automerge]1571394629[/automerge]
OK, I'm not a plumber but was in your exact situation last year. 3x bathrooms, downstairs toilet in a large victorian semi, gravity-fed. Also 15mm mains feed, 13 litres per min at garden tap with 3bar.

Like you I considered a large combi, but having spoken to people who had actually had this done, it wouldn't sustain 2 high flow showers simultaneously, which was my requirement.

I did a lot of research and decided for an unvented cylinder and an accumulator until I could upgrade the mains feed (it's under the front driveway which I'm planning to redo in a couple of years). In the end, had the unvented cylinder fitted while waiting for the accumulator to come into stock (it was on 3 weeks order). The flow and pressure was so good out of the unvented cylinder I ended up cancelling the accumulator order and haven't yet upgraded the mains supply to 22 or 28mm. I don't really need to upgrade it but will end up doing so when the drive is being done as it would be a shame not to.

Guess what I'm saying is have an unvented cylinder fitted and see if you are happy. If not, upgrade your mains feed. If still not happy, add an accumulator. You might end up saving some cash.

Thanks. Gives me some hope everything will be ok. Tho I don’t want to retro fit Equipment if I can try and work out the problems before they arise. I don’t believe my original plumber was on about digging up my drive. Just taking the feed from where it comes in the house And running 22mm pipe from there. Again I’m not sure on this. Tho he didn’t mention new connection to the outside main. Which I believe can be a good solution but costly

got a new plumber comin sat hopefully hel have some ideas
 

Attachments

  • 0D0E0F9C-570D-46C3-AD9C-858614954576.jpeg
    0D0E0F9C-570D-46C3-AD9C-858614954576.jpeg
    1.4 MB · Views: 18
  • CB73E833-DDFA-4130-8482-43B5BA1D890D.jpeg
    CB73E833-DDFA-4130-8482-43B5BA1D890D.jpeg
    556.7 KB · Views: 20
  • F4CA16A9-CCAA-4244-B8E6-AD0213E40064.jpeg
    F4CA16A9-CCAA-4244-B8E6-AD0213E40064.jpeg
    1.5 MB · Views: 18
Last edited:
I think you know the way fwds now, let us know the final plan...ohh now you
have to choose which boiler ...thats a good one ...plenty of advice on PF regarding
which Manu which model and then which components ...these boys really do know
their stuff...no % driven sales people on here just hard advice based on practical
experience...I have my opinion in this area but will hold back
have a good weekend
 
Min space I would say would be a meter by 800mm deep for a standard 600mm dia unvented

Pressure and flow is key with an unvented setup

Min spec would be 2.5 bar and 15lpm just for one outlet open

If you want multiple 4bar and 25lpm minimum

Right now down to the brass tacks

If you don’t have the flow eg 15lpm etc you can install an accumulator but this would need to be sized correctly allowing for the 50% rule so potentially around 400-600l accumulators

You can try and ask the water board to see if they could up your flow and install a new main of it isn’t a 25mm blue plastic one

If you don’t have the pressure then only option is a pump as you can’t pump directly from the mains have a look at the dab easy sys
 
Just had my second boiler guy come round.

He was most keen like my first plumber to put in a combi. Less to go wrong and cheaper was his words. Checked and He is g3 qualified.

He didn’t check my flow rate or pressure. Am now considering buying a pressure gauge myself off amazon. But he said from running the kitchen tap flow rate looks “ pretty good”, whilst waggling a finger under it. So not that that means much.

To be honest I’m comin around to the combi option. It means compromising on multiple showering but it’s positives is it doesn’t occupy much space. I don’t like the idea of turning a liveable area of my home into a pumping station. And I can’t fit the cylinder in my airing cupboard.

Plus then Getting a uv cylinder alone doesn’t guarantee me multiple hot water use without the flow rate coming in and would take up such a large part of my garage. It would be more negative to have a sacrifice of useable floor space over the occasional que to use shower. No one likes the loft idea and I feel like if it was a good idea. Houses would be built with all the stuff in the loft in the first place. It’s such a wasted of area.

If I get a combi. If I go a large as poss, 42kw and get a 22mm feed from the first point In the house (I think it’s under the sink). Is this going to give the best shower In terms of power type shower? I’m guessing as with this system, flow rate is going to affect how much you’ll notice if someone does the washing up whilst someone else is showering ???
 
If I go back to your first post, you believe that your incomming flow rate is around 15 litres per minute. Any Combi fitted should be sized to that flow rate. A 42kw Combi requires a much higher flow rate than that.

You have clearly set out what your requirements are - you need a decent heating engineer to design a system to deliver them and give you some guarantees.

A Combi solution (without an accumulator) winot address the fundamental issue that you have - low flow.


At the moment, with the route you are following, the likely outcome is that the showers won’t perform significantly better than they do now.

I would also talk to your neighbours as to how they have addressed and resolved this issue.

Apologies, but I have seen it so many times - systems ripped out, an enormous Combi on the kitchen wall - and the shower still trickles.

As the previous poster succinctly said - pumping the shower from a vented hot water tank will at least show some imorovement.
 
If I go back to your first post, you believe that your incomming flow rate is around 15 litres per minute. Any Combi fitted should be sized to that flow rate. A 42kw Combi requires a much higher flow rate than that.

You have clearly set out what your requirements are - you need a decent heating engineer to design a system to deliver them and give you some guarantees.

A Combi solution (without an accumulator) winot address the fundamental issue that you have - low flow.


At the moment, with the route you are following, the likely outcome is that the showers won’t perform significantly better than they do now.

I would also talk to your neighbours as to how they have addressed and resolved this issue.

Apologies, but I have seen it so many times - systems ripped out, an enormous Combi on the kitchen wall - and the shower still trickles.

As the previous poster succinctly said - pumping the shower from a vented hot water tank will at least show some imorovement.
The other dynamic to consider is ...you install pump assistance to achieve desired rate from your combi then as you are legitimately taking your neighbours water they go and get
similar pumps installed and you are all back to square one. I watched a whole cul de sac in
Hightown go this way we did our fair share. Stored water is the best way it can build up overnight for the morning onslaught and recover during the day. Then in the summer you will be laughing when your neighbours cant even suck it out of the main
centralheatking
 
Just bolt on a pump or power shower(s), easier all round.

I tried this originally I installed a pump for I think £300. It was so noisy and it lasted 1 year before it broke. It now sits unplugged. Redundant
[automerge]1571787227[/automerge]
If I go back to your first post, you believe that your incomming flow rate is around 15 litres per minute. Any Combi fitted should be sized to that flow rate. A 42kw Combi requires a much higher flow rate than that.

You have clearly set out what your requirements are - you need a decent heating engineer to design a system to deliver them and give you some guarantees.

A Combi solution (without an accumulator) winot address the fundamental issue that you have - low flow.


At the moment, with the route you are following, the likely outcome is that the showers won’t perform significantly better than they do now.

I would also talk to your neighbours as to how they have addressed and resolved this issue.

Apologies, but I have seen it so many times - systems ripped out, an enormous Combi on the kitchen wall - and the shower still trickles.

As the previous poster succinctly said - pumping the shower from a vented hot water tank will at least show some imorovement.

That’s fine. Appreciate being told the facts. Thinking now that I agree that flow rate and pressure is going to determine setup. Not just wacking I’m a big system without decent flow rate. I Just don’t understand why 2 separate plumbers came and recommended a combi. I guess finding a plumber who’s thorough and very competent is the next step. Any recommendations for one who works in Northampton please let me know
[automerge]1571787357[/automerge]
The other dynamic to consider is ...you install pump assistance to achieve desired rate from your combi then as you are legitimately taking your neighbours water they go and get
similar pumps installed and you are all back to square one. I watched a whole cul de sac in
Hightown go this way we did our fair share. Stored water is the best way it can build up overnight for the morning onslaught and recover during the day. Then in the summer you will be laughing when your neighbours cant even suck it out of the main
centralheatking

That explains a lot. As a general member of society it didn’t enter my mind that the mains coming into my house ever varies and or wouldn’t be sufficient to run any size powershowers. Without thinking it through I just expected a limitless flow rate from the outside main pipe. I always thought that people stored water in cylinders primarily because the boiler was unable to produce enough hot water on demand. And not that the incoming cold supply may not be able to keep up.
 

Attachments

  • BCB6BC4A-4D5B-4F1D-9AA1-69E3D6639EDA.jpeg
    BCB6BC4A-4D5B-4F1D-9AA1-69E3D6639EDA.jpeg
    1.7 MB · Views: 10
Last edited:
I tried this originally I installed a pump for I think £300. It was so noisy and it lasted 1 year before it broke. It now sits unplugged. Redundant

Looking at that install I'm not surprised...no insulation (for pipes or pump), pipes insufficiently clipped and poorly installed, unsuitable pump location ( right next to cupboard door). Was it even screwed down or did it just bounce around on it 's rubber feet while knocking the outlet pipes on that dividing wall? Anyhow there are better ways and much much longer lasting and quieter pumps say by StuartTurner or Grundfos so perhaps you should revisit the idea.
 
Last edited:
I tried this originally I installed a pump for I think £300. It was so noisy and it lasted 1 year before it broke. It now sits unplugged. Redundant
[automerge]1571787227[/automerge]


That’s fine. Appreciate being told the facts. Thinking now that I agree that flow rate and pressure is going to determine setup. Not just wacking I’m a big system without decent flow rate. I Just don’t understand why 2 separate plumbers came and recommended a combi. I guess finding a plumber who’s thorough and very competent is the next step. Any recommendations for one who works in Northampton please let me know
[automerge]1571787357[/automerge]


That explains a lot. As a general member of society it didn’t enter my mind that the mains coming into my house ever varies and or wouldn’t be sufficient to run any size powershowers. Without thinking it through I just expected a limitless flow rate from the outside main pipe. I always thought that people stored water in cylinders primarily because the boiler was unable to produce enough hot water on demand. And not that the incoming cold supply may not be able to keep up.
There is a wealth of experience on PF, we do not always agree on everything, I think you are getting the picture now. Combi Boilers are smashing for the correct circumstances and an absolute inadequate bind in unappropriate usage. centralheatking
 
We cover a number of properties in Rushden - if that is close to you.
I live approximately 18 miles away/30 min drive from Rushden. However I would have a preference to someone local to Northampton if possible.
Would anyone recommend using sites like mybuilder to find someone? The purpose isn’t to find someone to undercut someone, cost is secondary to achieving a good result . Just someone who is has a good local reputation and will be accountable
[automerge]1571838604[/automerge]
Looking at that install I'm not surprised...no insulation (for pipes or pump), pipes insufficiently clipped and poorly installed, unsuitable pump location ( right next to cupboard door). Was it even screwed down or did it just bounce around on it 's rubber feet while knocking the outlet pipes on that dividing wall? Anyhow there are better ways and much much longer lasting and quieter pumps say by StuartTurner or Grundfos so perhaps you should revisit the idea.
It wasn’t clipped down. Want pressurised hot and cold now for mixer taps . So vented boiler system is defo not an option. And would like to avoid Standalone pumps
 
To anyone still following this
Managed to get Anglian water round to check my outside feed. Which is surprisingly good.

Outside Mains
3.9 bar
50ltrs/min He was using a Weir cup (Googled the name) which seems optimistically high

Back tap approx 15 m ish away from mains
3.5 bar
25 ltrs per min
So it’s lost half of the flow

I then run a jug test myself running each cold tap on full and putting a jug under for 6 seconds. Multiply x10 for ltrs/min

1200ml /12ltrs kitchen tap

1500ml /15 ltrs Bath

2800ml / 28ltrs sink tap upstairs

For some reason the kitchen tap is terrible. And the bath cold feed appears to coming from the tank upstairs. Not the outside supply.

My questions are:
  1. how much loss is normally expected between mains and house?
  2. If I install a 22mm cold pipe to feed new boiler. what start point do I ask him to attach it at in order to loose the least flow.
  3. Any rules of thumb of how much loss in flow will there generally be going from ground level to floor 1 of a house in the 22mm pipe.
  4. Based on the fact I have an existing gravity heating system working. Could I install the new water pipe. Check the pressure and flow. And then buy according to what I actually get?
  5. Would digging a new 32mm supply to the mains be overkill. Looking at prices. It seems approx 1k ish. Which is what any accumulators might cost and would mean It wouldn’t take any space up in the house. And should mean I’m always gonna be in a good supply of water.
 
To anyone still following this
Managed to get Anglian water round to check my outside feed. Which is surprisingly good.

Outside Mains
3.9 bar
50ltrs/min He was using a Weir cup (Googled the name) which seems optimistically high

Back tap approx 15 m ish away from mains
3.5 bar
25 ltrs per min
So it’s lost half of the flow

I then run a jug test myself running each cold tap on full and putting a jug under for 6 seconds. Multiply x10 for ltrs/min

1200ml /12ltrs kitchen tap

1500ml /15 ltrs Bath

2800ml / 28ltrs sink tap upstairs

For some reason the kitchen tap is terrible. And the bath cold feed appears to coming from the tank upstairs. Not the outside supply.

My questions are:
  1. how much loss is normally expected between mains and house?
  2. If I install a 22mm cold pipe to feed new boiler. what start point do I ask him to attach it at in order to loose the least flow.
  3. Any rules of thumb of how much loss in flow will there generally be going from ground level to floor 1 of a house in the 22mm pipe.
  4. Based on the fact I have an existing gravity heating system working. Could I install the new water pipe. Check the pressure and flow. And then buy according to what I actually get?
  5. Would digging a new 32mm supply to the mains be overkill. Looking at prices. It seems approx 1k ish. Which is what any accumulators might cost and would mean It wouldn’t take any space up in the house. And should mean I’m always gonna be in a good supply of water.
PF never forgets anybody...Dan does That..
Is your area rural or built up suburban ?
1. these figures .great in both departments ..your figures are a flow most london people would kill for. It was also good to get your utility out as well normally they are quite reticent.
2. You cannot loose out with a new supply to your gaff from the meter/utility stop...but is it really 1km ?...perhaps its 1metre.
3. so your analysis 4 & 5 is valid
let us know...you are tenacious ...quite right too. centralheatking
 
PF never forgets anybody...Dan does That..
Is your area rural or built up suburban ?
1. these figures .great in both departments ..your figures are a flow most london people would kill for. It was also good to get your utility out as well normally they are quite reticent.
2. You cannot loose out with a new supply to your gaff from the meter/utility stop...but is it really 1km ?...perhaps its 1metre.
3. so your analysis 4 & 5 is valid
let us know...you are tenacious ...quite right too. centralheatking
£1000 not 1kilometre
 
Did he test from your stop tap / there supply

Kitchen tap could have flow restrictors installed

All depends on what pipe you have coming in
Best option is either a 25mm or 32mm alk that will give you the best flow rates off there figures

If your going for a Combi Boiler tbh no point upgrading as the max you will require is around 14lpm so 15mm supply close by

Depends on pipe size and bends etc pulled bends / benders restrict less than an elbow eg soldered if you can’t get around use swept bends

Yes you could get the new main installed and then make the decision based on real world figures etc

No as you can always reduce the flow and pressure can’t always increase it easily also depends on what there supply is (water board to the meter / stop tap) as if it’s 20mm not worth upgrading to a 32mm etc
 
If you go down the large combi route, for a Vailliant 938, you will need 24 lpm at the point of entry into the boiler to achieve full utilisation.

Apologies for being a nerd, but we have worked extensively with these type of boilers (installed in properties by mistake) in North London matching them with pump accumulators to improve shower performance.
 
Did he test from your stop tap / there supply

Kitchen tap could have flow restrictors installed

All depends on what pipe you have coming in
Best option is either a 25mm or 32mm alk that will give you the best flow rates off there figures

If your going for a Combi Boiler tbh no point upgrading as the max you will require is around 14lpm so 15mm supply close by

Depends on pipe size and bends etc pulled bends / benders restrict less than an elbow eg soldered if you can’t get around use swept bends

Yes you could get the new main installed and then make the decision based on real world figures etc

No as you can always reduce the flow and pressure can’t always increase it easily also depends on what there supply is (water board to the meter / stop tap) as if it’s 20mm not worth upgrading to a 32mm etc


Anglian water tested from the mains 50l

And then I asked Anglian water to test from my outside back tap. Which is off from my stop tap directly on the other side of the wall, under 1/2 meter away. 25ltrs flow approx

Interestingly non of the heating guys have tested my water pressure. Just told me it’s good

So Leaving out the idea of moleing a new pipe to my mains for now.

In The last visit I had the heating engineer said there was no point upgrading internal feed to a 22mm pipe. As my pipe work coming in was smaller and stepping up after a smaller pipe coming in wouldn’t achieve anything . He could only see this pipe as pictured. Is unlikely this pipe is any larger below this cupboard? Is this likely to be the same size all the way to my mains is what I’m asking?
[automerge]1573046091[/automerge]
If you go down the large combi route, for a Vailliant 938, you will need 24 lpm at the point of entry into the boiler to achieve full utilisation.

Apologies for being a nerd, but we have worked extensively with these type of boilers (installed in properties by mistake) in North London matching them with pump accumulators to improve shower performance.

this in my head at the mo is my most likely option. If I can achieve 25ltrs feed to my airing cupboard upstairs. Then I’m thinking to put the largest combi that’l physical fit in the cupboard. I think the one you mentioned is a storage combi, so maybe one of those. To give me the best output.

the other option. Is still the unvented in the loft. But I’m worried about the weight of it up there and would spend a lot upgrading the rafters and using crossbeams brackets etc to spread the load across the whole of the roof rafters. Before I’d feel comfortable sticking up the unvented. Also. I need a hand rail everywhere and probably better lighting and maybe rafter insulation
[automerge]1573046452[/automerge]
PF never forgets anybody...Dan does That..
Is your area rural or built up suburban ?
1. these figures .great in both departments ..your figures are a flow most london people would kill for. It was also good to get your utility out as well normally they are quite reticent.
2. You cannot loose out with a new supply to your gaff from the meter/utility stop...but is it really 1km ?...perhaps its 1metre.
3. so your analysis 4 & 5 is valid
let us know...you are tenacious ...quite right too. centralheatking

I live in a suburban area. New built (ish) 2000 aged property detached.
Hoping to try and install pipe work and get away without installing a new feed to Mains (yeah I meant £1000 ish cost). If I can achieve 20ltrs plus to any boiler system, this should be enough to run and shower and wash up at the same time without a dramatic loss of flow?
 

Attachments

  • EA3EABF2-D023-4BF0-A07C-AE7E380A1F28.jpeg
    EA3EABF2-D023-4BF0-A07C-AE7E380A1F28.jpeg
    76.9 KB · Views: 16
Last edited:
I would say that’s unacceptable for what your purposing 15mm incoming/20mm alk won’t do a shower and washing up at the same time

Best way to test this

Open the outside tap then open the kitchen tap (cold) this will give you an idea
 
I would say that’s unacceptable for what your purposing 15mm incoming/20mm alk won’t do a shower and washing up at the same time

Best way to test this

Open the outside tap then open the kitchen tap (cold) this will give you an idea

sorry what is alk term?

the kitchen tap has flexi hoses feeding it that look even narrower, as a guess i'd estimate it uses like 10 litre per minute, maybe could restrict it slightly?

and a decent shower (i googled the answer)use 15-20 ltrs p/min? so if my incoming is to boiler and i put in a gigantic combi, 25 ltr/per min should this not be enough?

I will try you experiment of opening both taps when i finish work

do u think that it'l be 15mm pipework that run under that cupboard all the way to the mains? i'd rather up the water flow if possible and not be under powered, i will mole to the mains if i have to (price dependant) or go back to the unvented in loft, both may work out similar in price
 

Reply to New boiler location and ultimate setup recommendation please in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I would like some guidance regarding the Worcester CDi 29 Classic boiler. According to the manual it has a holiday mode and frost protection mode...
Replies
3
Views
481
M
I have a viessman vitodens 222F combi storage boiler on the ground floor. It has 100l capacity inbuilt cylinder which is delivered on mains...
Replies
0
Views
345
Max Hill
M
My daughter bought her first home and was hoping to convert to gas but its not available in the area, so thinking a boiler upgrade is the better...
Replies
8
Views
424
Hi, I am replacing our 11 year old boiler (due to H.Ex. leak) with a new one. This is in a "sealed" system with red expansion vessel in airig...
Replies
3
Views
524
I have a 40 year old floor standing Glow Worm 45-60 boiler (open vent )which is in a cupboard in the centre of the house. Its an old workhouse...
Replies
2
Views
333
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock