Messages
1
Can anyone tell me if the greenstar 24i circulating pump modulates? i have been looking at param 2.1c which references settings 0 to 4, i know the factory default setting is 4 (constant high pressure) which to me implies that it would not modulate on this setting, does it need to be setting 0 to modulate?. My reason for asking is firstly that the pump sounds like it is labouring when just hot water is on (the boiler is located less than 2 metres away from the hot water cylinder) and when the radiator TRV valves start closing down however there is a bypass on the circuit, and secondly i suspect there would also be a small energy increase on setting 4. I would appreciate a professionals thoughts as a homeowner i contacted worcester bosch but felt they were unable to answer my question satisfactorily, i suppose i would not have the same technical access as the professional installers do.
 
Last edited:
How old is the boiler ?
 
Setting 4 is a quite modest setting for a 7M pump.
It is a 3M constant head which should suit most systems, it will modulate its speed only to maintain that constant head.
If you have a system with very large flow and return piping of say 28mm or even more modest 22mm then setting 3 at 2.5M might be fine, I wouldn't recommend much lower setting.

Setting 0 is apparently PP (proportional pressure) mode but they are showing the full speed curve, normal PP mode has a range where you might select say 4.6M (like mine) this means that the pump will modulate to maintain a flow rate of say 0 to 22LPM between pump pressures of 2.3M and 4.6M. So
at this setting the pump will run at ~ 3.5M to give say 12LPM, like mine and as TRVs are closing in will further reduce the speed and pressure.
The pump certainly won't be labouring at any of settings.
You can just change to setting to 0 and see how it performs, this mode might be PP Auto Adapt where the pump will automatically give the correct flow/pressure for any condition but I have yet to see any one that really works as advertised.



1642945089425.png
 
You want the lowest of ranges 1-4 that gives satisfactory performance. For a traditional two-pipe system fitted with TRVs you probably want range 2 or 3.

The best setting should haven been selected by the installer. That said, a lot of installers seem to just leave the pump set on 4. The setting is in the installer's settings, which the end-user shouldn't really play with so be careful when experimenting.
 
Last edited:

Reply to Worcester Bosch Greenstar 24i Pump Speed in the Gas Engineers Forum area at PlumbersForums.net

Similar plumbing topics

I have an ideal vogue max S18 boiler and I’m considering fitting auto balancing TRVs, my question relates to the boilers pump. I see a boiler pump menu for either 70% or 100%, so, is the pump set at either one of two fixed speed percentages or does the pump actually vary speed, (modulate)...
Replies
1
Views
143
Hi All I have a leak coming from within my Mira Elite QT shower. It seems to be flowing from behind the switching Control. Any ideas what could be causing this leak. Already Changed the Pump Elbow as one of the clips had popped which was causing a second small leak, Any idea? Is it time to buy...
Replies
0
Views
232
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
323
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
232
I was stupid enough not to check the position of the pipes under the tiles when installing a toilet and drilled right through the center of a 16 mm copper water pipe. I exposed the pipe by removing a ~30cm section of the plastic sleeve and a ~10 cm section of the pipe around the hole. Several...
Replies
0
Views
187
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock