-Small flat with a kitchen and one bathroom.
-Vokera Unica 32 BHE boiler.
Problem: Kitchen tap has low HW pressure and sporadic hot temp
  • It's sporadic so sometimes water comes out piping hot, other times the boiler won't fire
  • Diverter motor and valve checked and ok
  • Bathroom sink tea and bath has HW whenever tap opens.
  • Kitchen tap is one metre from boiler, bathroom is three metres from the boiler.
  • Doesn't seem to matter if CH is firing or not. CH works absolutely fine.
  • adding: Changed kitchen tap, worked fine for 15mins then back to sporadic running cold

I am thinking about changing the Plate Heat Exchanger.
But when it does fire the temp is excellent. Bathroom HW flow and temp are good though.
The bathroom HW does not point to the Plate HE.

So pretty confused here, any thoughts appreciated.
 
Last edited:
Change the kitchen tap but have a look at the flexis if it has them kinked ?
 
If you open the bathroom hot sink tap while kitchen hot tap has low flow/temp is the bathroom tap flow/temp ok and does the kitchen tap still have low flow but hot water?.
 
As suggested, maybe flexi kinked/damaged so swap hot/cold if cold flow was ok.
I'd be unlucky to have had a kink on old tap and new one but it is possible... Will check that...

So maybe not the plate HE? Shower is running hot so if it was the plate HE, I'd have consistently low flow, low temps... Is this right?

If so, then pipework as you guys say... Maybe the ballofix under the kitchen tap? Do they ever go wrong? I've never had one go wrong, anyone else?

I'm wondering about debris ? Like just before the ballofix. Suppose I could whip it off and check.. But the boiler has several filters for the HW...
 
Last edited:
ok good and makes sense ShaunCorbs ..

Trying to pinpoint and understand the connection between low flow and low temp:

one thing I noticed today after the new tap went on - I was checking HW on, off, swing the mixer H to C and back and it was behaving well for about 15 mins as mentioned above.
Then I as I was watching it the flow rate dropped noticeably. Then it started running cold.

Would low flow rate be low enough not to fire the boiler?
This would explain lack of HW. It runs cold. not warm.
 
Yes low flow = boiler not making hot water as it’s not sensing demand
 

Reply to Weird HW problem in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

Hi bit of a weird issue, I installed a grohe bathroom tap successfully 2 months ago bought from screwfix. Last week the right hand hot tap makes a squeak noise as I turn it on or off, left tap is 100% perfect and noiseless. This grohe tap is like one unit, so no screw notch or way I can remove...
Replies
7
Views
260
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
363
Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
253
Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
2
Views
156
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
280
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock