Have a recently installed Vitodens 100-W, within the last week, & hot water has been intermittent at best. I'm seeing F.373 - 50 & F. 345 - 50 fault codes. Install follow- up has been unhelpful. I,m also seeing standby temps reach 195 F (91 C) which sounds dangerously high.
 
These are all temperature related, so I would check the flow and return valves are open fully under the boiler, or any other restrictions - eg a filter valve valves. Failing that, then there could be an issue with how it’s been installed such as a blockage, pump failure (yes new ones can fail), another circulation issue.
 

Reply to Vitidens 100 W - new unit, no hot water in the DIY Plumbing Forum area at PlumbersForums.net

Similar plumbing topics

Hi bit of a weird issue, I installed a grohe bathroom tap successfully 2 months ago bought from screwfix. Last week the right hand hot tap makes a squeak noise as I turn it on or off, left tap is 100% perfect and noiseless. This grohe tap is like one unit, so no screw notch or way I can remove...
Replies
7
Views
300
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
159
Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
263
Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
2
Views
166
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
375