Evening all. I have been to change a pump on a vailliant ecotec plus 824 as water was not circulating and the boiler kept cutting out. Also when I opened the pump vent it sprayed straight into my face so couldn't check to see if it was turning.

Any way, changed the pump and it started ok but had the same problem. Then it just started giving me the f64 fault. Random at 1st but now continuously.

Hmmm
 
Have you got the vaillant app?
It give solutions to fault codes
I will look it up in a mo
 
I didn't know there was one. Got the manual, says flow NCT short or faulty pcb. Not sure why changing the pump would cause any issues
 
IMG_2284.PNG
 
Did you get things wet when you changed the pump?
Why did you change the pump? was it faulty?
 
No, I always keep a towel over the pcb and have my wet vac at hand. And I always check before I turn on to see if any water did get in.

Yeah, changed the pump as the bearings were goosed. I could not ooennthe bleed button on it as water was gushing out.
 
So looks like I will be changing the pcb this morning. Will put in reconditioned one. Maybe also take flow sensor and harness but I doubt it will be a short circuit there.

Can I get some reassurance?

Cheers fellas
 
Check the thermistors with your meter and check through the wiring harnesses too. I would be looking for a short circuit. If you cannot find one, the Board sounds favourite in my mind but it is Saturday Morning and I'm on tick over
 
Update guys. Changed the plate on this and all is working well now. I got there in the end.

Cheers for the advice.
 
Status
Not open for further replies.

Reply to Vailliant 824 f64 fault in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi there, thanks for your time to look at this record long post!! I work on the operational management side or a small building contracting firm...
Replies
9
Views
1K
H
Hi there, thanks for your time to look at this record long post!! I work on the operational management side or a small building contracting firm...
Replies
0
Views
657
HRP123
H
    • Like
Hi all, We recently purchased a house and nothing seems to work correctly here, I've spent weeks rectifying issues. Plumbing, electrical...
Replies
47
Views
5K
Hello All I've been having fun with my old vented, Y-Plan central heating system, since I finally got it up and running again yesterday, having...
Replies
17
Views
4K
Hello All and thanks Lou i did write a reply but it would not let me send it? i am not sure what I am meant to write and I do not want to come...
Replies
1
Views
847
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock