Hello All

I am gas safe and G3 registered since 3 years. So still very new to this industry and I have tons to learn.
I specialise in service and maintenance, unvented hot water installations are very popular here in Wiltshire. We have water pressure 3,5-4 or more bar mains pressure over here and hard water is also present.
I have had now, 2 systems which are same make range Tribune, kingspan about 14years old, which I service.
Both systems had initially when I came to them, expansion vessels full to the brim and resulting the 6bar PRV to fail.
Those parts I replaced to pressurised to 3bar to balance the 3bar pressure relief valve.

Now, I face some odd pipe work resistance, resulting in noise/vibration around expansion vessel area.
I checked the filters and they were clear, no debris...both properties have had block salt water softeners installed.

Noise is worst once the cylinder was heated to full temperature 55-58degrees and occurs on most outlets.
Open the taps/shower again and the vibration lessens or not audible.
I guess the water is at its biggest volume after heating, therefore more pressure?

After I replaced the 3bar pressure relief valve/multi control with direct replacement, problem still occurs.

I am grateful for anyone happy to teach me on this subject, as I clearly need it.
I have spoken to the manufacturers technical support and their advice, I have tried...
Changing orientation of expansion vessel, horizontal etc.

What am I missing?

Many thanks
 
I presume you mean a 3 bar pressure reducing valve and not a "3 bar pressure relief valve"
This thread may be worth reading as someone with a similar set up as yours including water softener cured his problem by re locating the PRV to as near the stopcock as possible.

 
I presume you mean a 3 bar pressure reducing valve and not a "3 bar pressure relief valve"
This thread may be worth reading as someone with a similar set up as yours including water softener cured his problem by re locating the PRV to as near the stopcock as possible.

Hello John

yes, that’s right pressure reducing valve. Thank you for your input, I’ll that.

many thanks
 

Reply to Unvented hot water noise in the USA area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold...
Replies
2
Views
192
Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two...
Replies
2
Views
194
Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer...
Replies
4
Views
280
Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I...
Replies
8
Views
366
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
418
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock