Hi guys. Is there any reason you can’t can’t downsize the hot water draw off from 22mm to 15mm straight away? Other than the flow rate being affected would there be any other concerns?
Cheers
 
Flow rate and potentially a bit of noise are the only issues I can think of.
But considering the unvented was probably out in to ensure a good flow rate I’d check what the customers future plans are / eg if multiple showers then you should stick to 22.
 
Also depends on incoming mains pressure.
No point in smaller diameter pipe with low mains pressure.

We have high pressure over here - reduced at water meter to 500kPa.
Generally most houses have a 1/2 inch hot water pipe.
 
Not needed. There should always be a shut off as part of the inlet control set.
Also by shutting off the cold this gives you a good idea of the state of the expansion vessel or the air bubble- by way of how long the hot runs before it stops. This function is lost if you shut off the hot on its way out.
 
Just for clarification. These cylinders have been fitted to spec on a job with lever valves on the hot draw off. I questioned it because it seemed daft when you can just isolate the cold. Also there’s a risk of implosion when draining down if somebody doesn’t know what they’re doing. I’ve been advised to label the valves to ensure they are left open when draining.
 
So why fit them?
It’s best not to let a customer tell you how to do your job - even if they think they know better.
State what you intend to do and if necessary explain why, if you they still insist you do something you’re not happy with - that is the time to explain they need to find someone else to do it.
 
I fit lever valves to the hot on all my unvented installs. If you wanted to isolate the hot and not the balanced cold you would be stuffed

You will only get implosion if you try to drain the cylinder with the hot lever valve off, but this is no different than having the hot taps shut anyway. Realistically someone who's G3 should be working on the cylinders and they should know the procedure for draining an unvented cylinder. I'm not a big fan of making things easier for DIY when we pay lots of money to have our qualifications.

As far as I see it there is no problem with immediately reducing the hot to 15mm.
 
Actually it would fill at the same rate but because of the smaller diameter the velocity would increase.
You misunderstand. Smaller pipe means less cold water sitting in the pipe, which has to be drawn off before hot arrives.

Smaller pipe also increases the frictional losses, so it’s not exactly the same rate.

There are also velocity regs to adhere too.
 
You misunderstand. Smaller pipe means less cold water sitting in the pipe, which has to be drawn off before hot arrives.

Smaller pipe also increases the frictional losses, so it’s not exactly the same rate.

There are also velocity regs to adhere too.
No I haven't mate, It would take the same time to fill a bath. A larger diameter would flow at a lower rate whilst the smaller diameter with a smaller area flows faster.
 
So why fit them?
It’s best not to let a customer tell you how to do your job - even if they think they know better.
State what you intend to do and if necessary explain why, if you they still insist you do something you’re not happy with - that is the time to explain they need to find someone else to do it.
Alright mate. I haven’t fit these cylinders and it’s not the customer who’s saying anything. It’s an apartment block with a load of cylinders going in. Builder would like to be able to isolate the hot if need be. I personally would just rely on the cold mains iso above the combi valve.
There’s no issue having a valve on the hot as long as whoever works on the systems knows to leave the valve open when draining down.
 

Reply to Unvented cylinder install query?? in the UK Plumbing Forum | Plumbing Advice area at PlumbersForums.net

Similar plumbing topics

Hi, My current hot water system needs to be replaced. Anyone got any suggestions or can recommend any plumbers around Derrimut area that won't rip me off? An office guy recommended me to apply for government rebates and get it installed through timetosave.com.au. How reliable is this...
Replies
6
Views
314
Hi, Later this year I am going away for a 2 week holiday and as the weather will be warm there is no need for the heating to be on and arguably no need for me to needlessly heat hot water. My intention was to turn the boiler off along with the mains water when going away. Now, I have heard...
Replies
1
Views
107
Hi all, I'm installing a concrete patio out back. By the wall under the kitchen sink I have an existing P-Trap gully for the grey water from the sink, dishwasher, washing machine etc. When I pour the concrete there won't be any chance to dig it up anymore. From my own research I get the...
Replies
0
Views
139
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
283
Hi bit of a weird issue, I installed a grohe bathroom tap successfully 2 months ago bought from screwfix. Last week the right hand hot tap makes a squeak noise as I turn it on or off, left tap is 100% perfect and noiseless. This grohe tap is like one unit, so no screw notch or way I can remove...
Replies
7
Views
275
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock