Hi Lads/lasses just wanted some advice on unvented cylinder inspection. I just took on what seems to be a contract for a block of flats all with direct heating via immersion. The way they have been installed seems a bit off as there is no check valve on the supply to the cylinder. It goes,
Stop tap
Double Check valve
PRV
then tee's off to the cylinder feed and cold water supply for the rest of the apartment.
When draining i noticed if i opened up a cold tap downstairs and opened the TPRV hot water came out the cold tap.
I explained to the customer what's going on and she said she has noticed she has to draw off a bit of hot water out the cold tap before filling a glass of water and thought it was normal.
The cylinders haver been installed in 2004 was the water regs different then? as they didn't require a DCV?
Can i carry out a cylinder safety inspection in this current state?
I have only been doing unvented for around 6 months now so I'm still getting to grips with the certs. I have a picture but my phone won't upload as of yet.
 
Hi Lads/lasses just wanted some advice on unvented cylinder inspection. I just took on what seems to be a contract for a block of flats all with direct heating via immersion. The way they have been installed seems a bit off as there is no check valve on the supply to the cylinder. It goes,
Stop tap
Double Check valve
PRV
then tee's off to the cylinder feed and cold water supply for the rest of the apartment.
When draining i noticed if i opened up a cold tap downstairs and opened the TPRV hot water came out the cold tap.
I explained to the customer what's going on and she said she has noticed she has to draw off a bit of hot water out the cold tap before filling a glass of water and thought it was normal.
The cylinders haver been installed in 2004 was the water regs different then? as they didn't require a DCV?
Can i carry out a cylinder safety inspection in this current state?
I have only been doing unvented for around 6 months now so I'm still getting to grips with the certs. I have a picture but my phone won't upload as of yet.
You cannot put a valve between cylinder and one of the pressure releif valves, and yes the way it is configured the water will syphon down cold if the supply to cylinderis isolated and you open TPRV.
 
Cheers Ricky. Its an Albion stainless steel no fitting instructions and none on the web to be found. So as it breaches water regs because its allowing hot water to mix with potable water, legionella and all that i guess i cannot sign off the inspection report. I just wanted to know if the regs changed from 2004 till now because it looks like 250 apartments are piped up wrong?
 
You can see the gate valve at the bottom of the cylinder feed a pipe goes through the floor. this is the cold feed to the kitchen and bathroom
 

Attachments

  • Resized_20210304_163659.jpg
    Resized_20210304_163659.jpg
    155 KB · Views: 35
So when expansion is taking place it expands into the cold and then into the expansion relief valve as the expansion vessel was flat as a pancake and has not had a service since it was installed.
 
Ok i got hold of kingspan that bought Albion cylinders so thanks Scott D for the hint. They have been plumbed up incorrectly as they should have a on return valve protecting the cold feed to the apartment even back in 2004. I ow have the pleasure of changing around 200+ cylinders ;)
 
I would think it’s acceptable as it’s not really different than installing the inlet block on the cold water mains and having the cylinder upstairs in the airing cupboard

you might have a check valve passing on a tap or shower ?
 
Yes there is a expansion vessel fitted its not doing much though,
Whats happening is as the cylinder heats up the expansion is taking place down the cold main to the kitchen tap as there is no non return valve!
 
Why are you proposing changing the cylinders rather than just adding a non- return valve?
Sorry just to clarify, Im not changing the cylinders, just the pipework, although they have been neglected since 2004! My original question was would this issue need to be rectified before a safety inspection is signed off as im not sure if its water regs or unvented related.
 
The top of the cylinder is normally the hot water outlet, it seems a strange place for a E.vessel if you are referring to this, if it is screwed to the cylinder top where is the HW drawn off?.
Sorry i couldn't flip the image but yes the expansion sits on the top which is incredible unstable when trying to re charge it.
 

Attachments

  • Screenshot 2021-03-05 at 22.58.45.png
    Screenshot 2021-03-05 at 22.58.45.png
    406.2 KB · Views: 9
The attached gives some idea of pipework which may be of some little use even though for a different type.
 

Attachments

  • Albion Ultrasteel Unvented Direct Universal Cylinder Installation (1).pdf
    1.3 MB · Views: 12
The attached gives some idea of pipework which may be of some little use even though for a different type.
Cheers John G, this is the ultrasteel which is what kingspan and albion manufactured when they merged. Same rules apply the non return valve after the cold connection to protect it by ensuring expansion takes place in the vessel and not in the cold water supply to taps. Thanks all i have enough evidence to justify my work on all the cylinders.Shame they wasn't fitted properly ut then again thats where half my work comes from.
 
Interesting way of installing the cylinder,
Have they sent you the orignal fitting instructions?
Why would you put the pressure gauge before the pressure reducing valve, it doesn't tell you anything helpful, ie is the pressure reducing valve shutting off at correct pressure.
Most cylinders have multiblock inlet valves, where you take the cold supply from, did some plumber fit what he thought was correct?
As Scott asked where is the expansion tank connected, I have always installed the expansion vessel on the inlet, again its to do with Legionella etc you don't want that amount of possible stagnant water on the outlet where it can get warmed up.
 
Interesting way of installing the cylinder,
Have they sent you the orignal fitting instructions?
Why would you put the pressure gauge before the pressure reducing valve, it doesn't tell you anything helpful, ie is the pressure reducing valve shutting off at correct pressure.
Most cylinders have multiblock inlet valves, where you take the cold supply from, did some plumber fit what he thought was correct?
As Scott asked where is the expansion tank connected, I have always installed the expansion vessel on the inlet, again its to do with Legionella etc you don't want that amount of possible stagnant water on the outlet where it can get warmed up.
Yeah thats it, its to great having the expansion vessel o the to of the cylinder but it is subject to legionella killing temperatures. I guess thats why they have changed the design now on the ultra steels and started making valve blocks so people cannot finesse there way through an install. I have the manufacturers instructions and it has to been installed properly. As you mentioned why would the pressure gauge be before the PRV this is telling you your supply pressure to the house but not the cylinder, maybe worth moving this swell if i want to get fussy.
 

Reply to Unvented cylinder inspection in the USA area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
113
Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
2
Views
94
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
316
Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
221
I have had a look at previous posts and think I know the answer to this but just before I make it worse could I just check what you think about this one. Granddaughter just moved house and this valve decided to leak when it was closed. When open its fine. Normally I have repacked the gland on...
Replies
7
Views
179
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock