Discuss Underfloor Heating Unexplained Temperature Drop in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Status
Not open for further replies.
Turn boiler stat up until u/floor flow pipe gives enough heat to manifold (try 70)
Is u/floor completly full of water without any air present and all valves on mani open (flows and returns)
Then find out why flow is loosing heat from boiler to mani (ceiling void open to elements or draughts, no lagging ?)
I assume new build, so maybe not fully finished


Tried turning the stat up. Makes no difference apart from the Rad circuit getting toasty :vanish:

All mani valves are open / off and there is no obvious signs of air... but the issue is the manifold flow bar cooling down. I cant fathom this part out.

Its a refurb, changing from vented to unvented with new pipework so all ceilings are down.
 
Restriction or air in flow (or return)to mani from boiler, as said above shut rad circuit 2 port and try
If that don't work, I would disconnect flow and returns from primaries and mani and try hosing through both
 
Start again. Finish wiring it & commission it properly. Put valves on to auto. Get a plumber in is the best advice
 
Thanks guys. Next step is to isolate the UFH circuit as you've said and try.

Will post the update here.

Have also got the tech guys from the manifold supplier (well known) on the case.
 
You haven't finished installing it yet! I bet it hasn't been balanced either. Flow rates for each loop need to be set. You will get heat going through to the ufh when you have manually opened the 2 port. Am I missing something or is this a wind up?
 
IMG_20160120_162202397_HDR.jpg

Here you go. Just to confirm that the white nuts on the bottom rail are all open. I just fixed them in place so I didnt lose them.

And I closed all the flow meters down except the last loop nearest the bypass valve just to see if we could get the heat across the manifold when the pump was running.
 
Last edited:
Pump is running directly on the mains atm just so we could test system. The flow cools down and the return goes cold when the pump goes on.

Yes I have flow meters. When the pump goes on the little discs drop inside the vials

So if the flow meters indicate you have water movement through u/floor, problem with restriction in dedicated flow/return
Your central heating pump should supply hot water to the manifold, then the pump on the mani does the rest
If your mani pump is moving the u/floor water around then its a supply problem I would have thought
Not seeing first hand so guessing really
 
Status
Not open for further replies.

Reply to Underfloor Heating Unexplained Temperature Drop in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I'm attending a wet underfloor heating system, it's an old one ..No flow meters, just adjustable valves on the returns with conventional...
Replies
3
Views
541
G
HI folks, is it possible/feasible/reasonable to insatll an ufh manifold and system (for a 17m2 room) from a disused CH 15mm flow and return? I...
Replies
2
Views
568
Good afternoon, I am experiencing a pressure issue with my heating system and was hoping to receive additional insight as to what the problem...
Replies
9
Views
401
As part of deep house renovation, planning to install wet ufh on the ground floor, and radiators on upper floor. Two bathrooms will have both...
Replies
0
Views
644
Hi All, Looking for a bit of advice on the best way to pipe this. - 24kW Worcester regular boiler in kitchen, approx. 9 years old - unvented...
Replies
16
Views
1K
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock