Discuss Underfloor heating, radiators and Nest in the Central Heating Forum area at PlumbersForums.net

Messages
3
I currently have a radiator central heating system, controlled by a Nest with OpenTherm (combi boiler, no zones/valves). I'm now getting an extension built which will be one big room from the new structure and the existing kitchen and dining room. I'd like to install underfloor heating in this new room. As I understand it, the done thing in this scenario is to move the existing radiator circuit onto a zone valve, then have a separate thermostat and zone to control the underfloor heating. However, I quite like the Nest/OpenTherm that puts out a continuous low level of heat through the radiators, and I think I'd have to get rid of it and go back to On/Off relay control of the boiler if I did that? Or, since my existing radiator system is running all the time at 30-40C anyway, can I just run the underfloor heating off that with a pump and blend valve?

Second question is, for the underfloor heating it seems you can either bury it in the screed or have an overlay system. It seems like it's standard to do under the screed for new build and overlay for renovations. I'm going to dig up the kitchen floor, so I can do either. The screed systems take a long time to respond though, compared to the overlay systems, which seems like a significant advantage to overlay to me? What's the downside? Just price?
 
If you want to continue using opentherm or any other modulating controls, or low temperature systems then some form of hydronic separation will be needed as the lower your flow temperature gets the UFH will pull more flow rates, which can starve the rads when both are in use.
Alternatively if its reverted to simple on off controls then this wouldn't be needed and could be zoned, obviously that's a step back though.
System needs a bit of thought. With regards to screeds or underlay I cant really comment but others with experience will be along shortly.
 
I will leave it to others to comment re controls. The underfloor itself get it properly designed we are polypipe registered installer's but all the manufacturers will do you a proper design/layout.
As for type we only install overlay as a first reserve last resort basis, really fast response is not required on underfloor its not how you operate it!.
The much larger heat sink of a screed system for my money is always preferable.
 
Thanks for the replies.

Shouldn't the scenario you suggest just result in the thermostat modulating the boiler higher? Isn't it basically the same as a TRV opening/closing? I suppose since the blend valve keeps the floor at constant temperature, roughly the same amount of heat would come out of it whatever the thermostat did, so the nest would be just controlling the radiators, so I would need some kind of thermostatic control of the ufh.

What's the actual benefit of a 'larger heat sink' as you put it? More even floor temperature?
 
Underfloor heating should be controlled with back set temperatures typically no more than 4 C below desired room temperature. I have both screed and overlay systems in my own property when up to temperature the screed system runs far less typically only been on less than 5 hrs a day maintaining 22C with a backset of 19C for 7 hrs overnight.
You should also consider type of screed pumped systems work well also polymer modified screeds.
 

Reply to Underfloor heating, radiators and Nest in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
2
Views
209
P
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
143
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
482
Copper pipes, I think its fair to say, is not what it used to be, the copper is getting thin while the cost is going up. Meanwhile, plastic Pushfit seems to be getting better and better, cost and convenience was always better, but now the quality is to, have we reached a stage where plastic will...
Replies
2
Views
259
Hello all, I'm would like to extend an existing outside tap to another point in the garden. I'm about to pour a concrete patio and was hoping to run the water line underneath. There are existing drain (and who knows what) pipes running along the same wall so I'm nervous about digging too far...
Replies
6
Views
237
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock