I was just pondering about my new system design, which will be fitted at the beginning of 2018.

Is it possible to run an unvented cylinder with a vented system boiler? Just wondering as it has to be far less hassle/least likely to leak than a pressurised CH set up?

I already have an unvented system in place so guess it would be a case of removing the large tank feeding the vented cylinder

Feel free to poke holes in my theory :)
 
If you are asking if you can use an existing open vented boiler to heat a new unvented cylinder?
The answer is yes. As long as it is fully pumped and not Gravity.
 
Sorry I should have been more clear

New system or conventional boiler - new unvented cylinder. Can I keep a header tank in place so as not to have to pressurise the CH circuits. My thinking is that it will be much more serviceable and better for the longevity of the joints in the longer term....
 
As above you don't have to seal the system, you can go old school and use an f and e tank
 
Thanks Shaun - Is this a wise option from a plumbers perspective. It will take less work to keep it like this - I'm just wondering if i am missing out on any benefits of pressurised?
 
If done correctly eg no pumping over and correct feed placement

There both the same, just don't want it sucking in air as this speeds up corrosion
 
My current set up isn't set up properly at all given the time it takes to eradicate air in the system (cylinder, pump and diverter valve in airing cupboard, boiler downstairs in kitchen a room away). However, working on the assumption my pump will be mounted on or near the unvented cylinder (all to be fitted in attached garage)... then my plumber should be able to reroute it, to make it more 'free'. I have also bought a Spirotech deaerator which should help?
 
My current set up isn't set up properly at all given the time it takes to eradicate air in the system (cylinder, pump and diverter valve in airing cupboard, boiler downstairs in kitchen a room away). However, working on the assumption my pump will be mounted on or near the unvented cylinder (all to be fitted in attached garage). then my plumber should be able to reroute it, to make it more 'free'. I have also bought a Spirotech deaerator which should help?

Best to get Plumbing sorted rather than fit Spiro.
Use it now you bought it but there is no substitute for the system working correctly.
If Plumber is re-piping system to move pump, it shouldn't be a problem after he/she's been.

What output is current Boiler?
 
I've re-piped everything, so all he will need to do is decommission the current set up and fit the new set up in place, in the garage. The only question mark is around ease and effectiveness of the tank feed into upstairs pipework...I'll have a chat with him when we meet to determine the final components (not sure if he will go down the system or regular boiler route).

Current boiler is 1986 - not an option to keep and in entirely the wrong place :) with an eye watering score of 63/100 for efficiency :eek::D
 
I've re-piped everything, so all he will need to do is decommission the current set up and fit the new set up in place, in the garage. The only question mark is around ease and effectiveness of the tank feed into upstairs pipework...I'll have a chat with him when we meet to determine the final components (not sure if he will go down the system or regular boiler route).

Current boiler is 1986 - not an option to keep and in entirely the wrong place :) with an eye watering score of 63/100 for efficiency :eek::D

Where did you get 63/100 from?
 
Status
Not open for further replies.

Reply to Types of systems available in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, I was hoping to replace an old system boiler with a Vaillant Ecotec Exclusive 627 system boiler, thats the one with the diverter valve so no...
Replies
1
Views
188
Hi, I am replacing our 11 year old boiler (due to H.Ex. leak) with a new one. This is in a "sealed" system with red expansion vessel in airig...
Replies
3
Views
546
Hi, I need a small water heater for a bathroom sink tap. I was going to have an unvented undercounter unvented cylinder installed by a plumber...
Replies
4
Views
573
Hi all, grateful for your expertise on the following. DIYer, not pro. Rural property in France Single storey. Septic tank. Late 80s construction...
Replies
1
Views
227
A
Previously had a WB Greenstar R28 HE System boiler with 4 pipes and vented (gravity fed) cylinder. No valves or pumps outside of the boiler...
Replies
1
Views
903
Deleted member 120897
D
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock