With nothing to do today I thought I would do a spring clean on my Grant Vortex 26-36KW model so turned off power, removed door, and then removed baffles gave them a scrub , hoovered out chamber BUT got a phone call while I was messing. After phone call noticed smell of kerosene, looked on floor and the valve was leaking!! I don't know whether I banged it by accident. Anyway put boiler back to together, twisted that little screw on top of valve, fired up boiler all good heated HW for about 30 mins. Put a piece of paper under valve checked it now and its dry. But why did it leak in the first place?

Also I keep hearing about " A fire safety valve, should be fitted" but last time I was quoted €70.0 so declined but if this valve is now getting iffy should I replace it with a fire safety valve? What exactly is a fire safety valve and is it easy to fit? Tank is almost empty but it will soon be topped up for winter so would like everything shipshape.

Here is a pic of valve and I did twist it anti clockwise and that seemed to do the trick. I take this valve is just a stop valve.
 

Attachments

  • IMG_1263.jpg
    IMG_1263.jpg
    208.7 KB · Views: 12
The valve you have is a fusible head Firevalve, but doesn’t meet oil safety regulations. They also tend to leak due to O rings gland inside them.
The valve head has a small threaded ‘nut’ soldered with low temperature melting solder and the valve is under a spring release pressure, so in theory a fire supposedly would melt the outer head off allowing valve to snap off.
No use in reality and needs a remote firevalve with sensor probe at boiler - a Tedington KBB valve for example.
You need an experienced oil engineer to do proper service - boiler and burner cleaned, nozzle and oil hoses replaced, oil filters cleaned/replaced, entire install, flue, oil tank inspected and an oil pump pressure gauge and analyser used to set up the combustion accurately. Worth every penny to pay a local decent engineer if you can find one
 

Reply to This Oil Valve on floor near boiler started leaking? in the UK Plumbing Forum | Plumbing Advice area at PlumbersForums.net

Similar plumbing topics

I have had a look at previous posts and think I know the answer to this but just before I make it worse could I just check what you think about...
Replies
7
Views
239
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up...
Replies
2
Views
250
PSxxxxxx
P
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold...
Replies
2
Views
182
I was stupid enough not to check the position of the pipes under the tiles when installing a toilet and drilled right through the center of a 16...
Replies
0
Views
221
We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the...
Replies
5
Views
307
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock