Had no heating in the kitchen so added a rad to the existing system. To my surprise it worked, the bad news is the rad in the hall is luke warm now. I'm told the system needs balancing. How do i do this?
 
Try googling it mate. Quite straight forward, the hall rad is now being starved of heat. Just a case of adjusting all rads on the lockshield valve.
 
Before you balance all system,just close lock shield on the kitchen rad and open 1/4 to 1/2 a turn,that may be enough to correct hall rad
 
Status
Not open for further replies.

Reply to tepid radiator in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is...
Replies
5
Views
535
Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two...
Replies
2
Views
191
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold...
Replies
2
Views
190
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up...
Replies
2
Views
261
PSxxxxxx
P
I have had a look at previous posts and think I know the answer to this but just before I make it worse could I just check what you think about...
Replies
7
Views
246
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock