I guess this is going to be an airlock problem but I have tried to deal with it and I am getting nowhere.

I have two rads at the end of the heating run and they get cold when others around the house are hot. Even though we live in a bungalow we do have a loft conversion with two rads upstairs. It is a pressurised system, oil boiler.

If I run water from the bleed valve on the end rad until it comes through hot it will remain hot for about a week but then stop running hot until I run some water out again and so it continues. I have tried running water out past the point when it runs hot to see if any air comes out but nothing.

If this is air, how do I get it out of the system?

Thanks, Daniel.
 
Turn off all the radiators in the bungalow except one of the ones in the attic. Open both the valve and the lockshield on that radiator to their fully open position. If you can, set the pump to its highest setting then do so and turn on the heating.

If the radiator gets hot, bleed it, then open up the second radiator in the attic in the same way (including bleeding) and progressively work around the bungalow. Thereafter balance the system

If the radiator does not get hot, you possibly have a vent valve in the attic above the level of the attic radiators that needs venting - see KOP posting above - try to trace the pipework to find it - often in loft conversions, the vents have been boxed in in the area between the eaves and the internal partition and can be a but of a puzzle to find. Start by looking in the area above where the pipework breaks through the ceiling.

It that fails get back to us
 
Are there any air vents on the high points in the loft? Kop
Yes there is a bleed vent in the loft near the hot water tank. I do check it regularly and there is often air in there although a tiny amount.


Is the system balanced?
Sorry, I don't understand how to tell about that.


Turn off all the radiators in the bungalow except one of the ones in the attic. Open both the valve and the lockshield on that radiator to their fully open position. If you can, set the pump to its highest setting then do so and turn on the heating.

If the radiator gets hot, bleed it, then open up the second radiator in the attic in the same way (including bleeding) and progressively work around the bungalow. Thereafter balance the system

If the radiator does not get hot, you possibly have a vent valve in the attic above the level of the attic radiators that needs venting - see KOP posting above - try to trace the pipework to find it - often in loft conversions, the vents have been boxed in in the area between the eaves and the internal partition and can be a but of a puzzle to find. Start by looking in the area above where the pipework breaks through the ceiling.

It that fails get back to us

I'll give that a go.
 
Wanted to come back here to say the problem has been fixed. I was a balancing problem after all so thanks to SimonG for pointing that out.

I confess I had no idea how or what balancing a heating system was all about but I googled it and watched a YouTube video.

This evening all rads are boiling hot, the best performance we have had for years so thank you very much for the input.

Daniel.
 

Reply to Rads going cold after about a week of being hot in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
115
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
316
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
1
Views
113
Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
2
Views
97
Hi bit of a weird issue, I installed a grohe bathroom tap successfully 2 months ago bought from screwfix. Last week the right hand hot tap makes a squeak noise as I turn it on or off, left tap is 100% perfect and noiseless. This grohe tap is like one unit, so no screw notch or way I can remove...
Replies
1
Views
80
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock