C

Catch_0x16

Hello all,

Like most people, I've gone to turn on my central heating after 6 months of it being off and, surprise surprise, it doesn't work. I'm trying to work out what is wrong with it myself, I enjoy the challenge and the learning process; if all fails, I can call a plumber.

I have an Ideal Classic FF250 gas boiler on the ground floor, and a total of 14 radiators in the house, spread across three floors. The central heating pump is a Wilo Gold 60, in the airing cupboard next to the hot water tank.

Initially, I noticed that the gas boiler was not alight when it should've been. I took it apart and saw that the 1A fuse on the circuit board was blown. I replaced this fuse with a spare I had laying around and the boiler started working again. I also ordered a new circuit board and replaced that the following day. The boiler ignites and appears to sound, look and feel normal.

Still however, no hot radiators.

I then opened the radiator valves on all radiators, as well as bleeding all radiators. I noticed a large amount of air bleeding out two of the radiators in a room I recently decorated (I had removed them from the wall to paint behind). These were the only air bubbles I encountered. I have since gone around and re-bled the radiators and can confirm it is only water coming out.

Still however, no hot radiators.

The circulation pump in the airing cupboard appears to be coming on. It is silent and still when the heating is off. When I turn the heating on it vibrates gently and makes an un-alarming humming sound. The pipes above and below it, however, are stone cold.

At this point, I'm out of ideas. Can anyone please help?

Thanks!
 

Reply to Please help me work out why my radiators aren't heating in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
172
Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I have changed the 3 port actuator Honeywell head however this doesn’t seem to have solved the issue, does this mean that the programmer is faulty? Or is...
Replies
8
Views
350
Hi, I have a Worcester 28i junior boiler that has started to lose pressure, only when using the central heating. When using hot water I have no issue, however, when running the heating the pressure drops. Im looking for some ideas on what could be causing this. I have no sign of pipe leaks...
Replies
6
Views
227
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
391
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
518
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock