Hi.

hopefully someone can help me here.

I have a recently had a new gas central heating system consisting of 7 rads and a Worchester 36cdi compact located in the lofty controlled by the wave thermostat.

I used to have electric storage rads and the electric controlled heating with were on tanks.
after install i have a drop in hot water pressure. if the cold is on then the hot drops and even running the bath takes forever.

any ideas?
i want to make sure i have all my facts straight before speaking to the plumber who installed as he did come arounf measureing pressure and said it was about average on the set up up i requested.
the main in pressure was 3 bar and the flow was 14l/m with the hot being 10l/m.
thanks for your help in advance
 
You need to call back the installer to check water flow your about 3Ltr per min short on hot water delivery,
 
He checked flow when I was present.
Everything is open.
I have 15mm that enter house that run in the loft but then goes to 22mm. Would it help to increase to 22mm from 15mm pipe.
The flow seems fairly quick on top taps on sinks but very poor on bath.
 
All your outlets are 15mm to the hots but on your bath i presume its still old 22mm probably delievers the same litres per minute just seems slower.
 
The flow on your boiler will be preset. Im not 100% familiar with your boiler but id say 12litres per minute. Thus cant be adjusted.
As for the 22mm to the bath. Ideally it should be 15mm from a combi...you may find you have to draw off alot more water before it becomes hot.
 
Tbh it's sounds like there's not much wrong. Your water main is giving 14lpm. Your getting a little less once the flow has been restricted by your pipe work and boiler. If you open the cold then it is sharing the 14lpm with your boiler, probably have less restriction than your boiler it gets more of the share.
 
So if I am getting 14lpm and it enters the boiler at 14lpm why isn't it coming out at 14 or even 13lpm.
Sure it shouldn't drop 4lpm.
 
1. Your boiler will provide 13 lpm at a 40 degree temperature rise, plus or minus 15%. If you're unlucky, and its minus 15%, the maximum hot flow rate will be about 11 lpm. Also, the Compact ERP version has a flow restrictor to limit the flow necessary to ensure that 40 degree, which may also reduce the flow rate.

2. The hot (and cold) flow rate at the bath outlet will be lower than an open pipe immediately after the boiler, as it has to navigate the pipework and fittings / bends. Friction in the system will reduce the rate of flow.

3. With a tank system, the hot and cold flow rates are largely independent as both come from large stores of water, usually (in the case of a bath) via 22mm pipes. With a combi, the cold comes off the mains via 15mm pipe, and the hot also comes off the mains via the boiler, again with (usually) 15mm pipe.

4. It would help to know what the cold mains flow rate is at the point of entry to your property. This would give you the maximum possible flow rate for both hot and cold. Measuring separately at the bath taps doesn't give you a full picture.
 
New posts
Status
Not open for further replies.

Reply to New Central heating but problems, Please help in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, I have a Worcester 28i junior boiler that has started to lose pressure, only when using the central heating. When using hot water I have no...
Replies
6
Views
269
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold...
Replies
2
Views
221
Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I...
Replies
8
Views
397
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up...
Replies
2
Views
283
PSxxxxxx
P
Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two...
Replies
2
Views
220
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock